R

redmist

hi there all wonder if you can help me, i am in the process of having a log burner plumbed into the hot water side of economy 7 heating this will be taking place in a months time my question is i have bought an indirect hot water tank and would like to put this in place and plumb it into the existing pipe work now except the flow and return to the boiler just cap the fittings off to use at a later date would this damage the coil inside the tank.and yes im having a heatas approved engineer to install the fire but not the wet side looking forward to your response many thanks in advance
Dean
 
Dean, I would get him to do the lot. Solid fuel is a mare if done badly . Solid fuel works on gravity circ. your indirect cylinder may not even be suitable. Is it 28mm coil?
 
Last edited by a moderator:
Agree ^^^. A cylinder has to have a coil that specifically suits Gravity for solid fuel, - many do not.
Also, the unused coil does not need capped off.
Let an expert do it.
 
thanks guys yes the coil is 28mm the cylinder was purchased for gravity feed this boiler is only going to heat the hot water and a heat leak rad not central heating but i am not a plumber guys just a good diy,r thanks very much for the replys though
 
I would use either a dunsley neutraliser or equivalent as I've done a couple of these systems and your doing the worst of the work anyway as the burner although can be pumped it must be piped to work on gravity incase of power cuts. Also the feed tank in loft that fills the cylinder and vents the burner must have a copper ball valve and fibreglass tank .to cope with high temperatures . If your running 28 to cylinder then the other pipework can be 22mm from boiler to neutraliser. It's a brilliant cost effective system once fully installed .
 
Status
Not open for further replies.

Reply to vented indirect hot water tank in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

First post as I can not figure this one out. I have a hot water boiler heating system, gas fired, with an HTP SuperStor indirect hot water tank...
Replies
2
Views
413
Hi, I have a rayburn 212 that I have plumbed into a vented hot water tank as far as I am aware I do not have to vent the rayburn as the tank is...
Replies
3
Views
548
Hi, I am reinstating an indirect hot water tank and have 2 cold water feeds coming into it from the same supply. One of the feeds has a float...
Replies
5
Views
917
Hi, I have two indirect water cylinders (Gledhill) connected to a gas boiler (Vaillant). The system is setup/programmed so that the tanks heat up...
Replies
4
Views
890
Hi, I have a hot water cylinder which feeds 3 outlets (kitchen sink, basin in bathroom & bathtap) which has never had very good pressure (probably...
Replies
14
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock