Hi guys,

I have a set up with rads upstairs and UFH downstairs. I have installed the manifold for the UFH along with 2x Honeywell 2port values, one near the manifold and the other on the radiator side. I will be using Nest 3rd gen thermostats to control both the upstairs radiators and downstairs UFH zones - 1 thermostat upstairs and 3 thermostats downstairs.

I am just getting my head around the wiring for the complete system and have put together a quick diagram to show where im at with things. Note that I have not yet shown the wiring of the actuators and heatlinks (for the nests) into the UFH wiring center (Danfoss FH-WC). Before I proceed with this I would like to check with you kind folks that what I am proposing so far wiring wise makes sense?

There are 4 questions/points on the attachment that I am unsure about, and of course if there is anything else which is wrong it would be great to know.

Thank you very much for any help provided :)

Parts/materials:

Danfoss FH-WC wiring center
Honeywell Home 2 port valve
Nest 3rd gen thermostat
Worcester 36CDI combi boiler

Alex
 

Attachments

  • UFH wiring.pdf
    19.3 MB · Views: 20
1 correct link the lives

2
Brown your switch / call
Blue neutral
Green / yellow earth
Orange switch live
Grey perm live link to lives

3 answered above

Lr on your Worcester combi is your switch
 
1 correct link the lives

2
Brown your switch / call
Blue neutral
Green / yellow earth
Orange switch live
Grey perm live link to lives

3 answered above

Lr on your Worcester combi is your switch
Really do appreciate the quick response Shaun, thank you

I have made the amendments and attached again with the 2port valves connected to LR and perm live.
With the 2 port valve rad side the wiring does not make complete sense to me - the pdf will explain this better.

Does all the wiring so far look correct Shaun?
 

Attachments

  • UFH wiring3.pdf
    21 MB · Views: 7
1 needs to go into sl orange goes to the boiler / pump etc also you can’t have multi feeds need to feed it all off one fused spur
 
Yeah the grey/brown being the wrong way is stupid, it still catches me out and have fitted loads of them.

Wiring diagram as per manual below. If you're using programmable room stats then ignore the programmer wiring and go straight to the stats. If you're using 2 separate programmers or twin channel then wire them between terminal 4 of the wiring center and the stats (or the equivalent using a new terminal in the box)

Whats the plug 4a fused in the top left?

I'll try and do my own drawing as I'm a little lost with yours (just the way my brain works)

What you're proposing to do only a small percentage of plumbers would normally do and a lot of electricians would say they can't do it because they don't understand it.
1689000145057.png
 
Yeah the grey/brown being the wrong way is stupid, it still catches me out and have fitted loads of them.

Wiring diagram as per manual below. If you're using programmable room stats then ignore the programmer wiring and go straight to the stats. If you're using 2 separate programmers or twin channel then wire them between terminal 4 of the wiring center and the stats (or the equivalent using a new terminal in the box)

Whats the plug 4a fused in the top left?

I'll try and do my own drawing as I'm a little lost with yours (just the way my brain works)

What you're proposing to do only a small percentage of plumbers would normally do and a lot of electricians would say they can't do it because they don't understand it.
View attachment 84000
Cheers Fowler! Glad i'm not alone with the confusion. I am only an apprentice electrician so it is a bit of a learning curve.

If its possible to do a drawing that would be amazing - Unless I have cracked it with the last version.
Its tricky but love to learn new stuff :)
 
IMG_1383.jpeg

Not gone into details about how each control is wired but thats where the wires go between each.

The supply can go to the wiring center or the boiler depending on where it is. If it goes to the wiring center then the 230v out from the boiler can be made redundant.

I’ve done the diagram on how i would do it with an airing cupboard upstairs hence the wiring center would be there and why the ufh zone valve is wired off the ufh wiring center which would be next to it. Saving you just running a 5 core between the wiring center and ufh center. I’ve also forgotten the actuator wiring but thats straight forward. Anything written as LNE is all taken from 1,2,3 on the wiring center unless shown

Obviously duplicate zone 1 for the 3 zones, stats, actuators

Remember to remove the link from the boiler when using external controls
 
Last edited:
View attachment 84004
Not gone into details about how each control is wired but thats where the wires go between each.

The supply can go to the wiring center or the boiler depending on where it is. If it goes to the wiring center then the 230v out from the boiler can be made redundant.

I’ve done the diagram on how i would do it with an airing cupboard upstairs hence the wiring center would be there and why the ufh zone valve is wired off the ufh wiring center which would be next to it. Saving you just running a 5 core between the wiring center and ufh center. I’ve also forgotten the actuator wiring but thats straight forward. Anything written as LNE is all taken from 1,2,3 on the wiring center.

Obviously duplicate zone 1 for the 3 zones, stats, actuators

Remember to remove the link from the boiler when using external controls

This has helped me BIG time!!


I had removed that 230V supply from the boiler end as I realised that with my old circuit, if the spur was turned off the circuit was still energised... what a noob!

I have studied how your circuit works and compared to the one I was working on (attached). Fundamentally as far as I can see both work in the same manner. The exceptions I can see is that a seperate spur is currently feeding my circuit and you are using the boiler power, which makes complete sense. (I might make this change!)

My boiler and the 2port rad valve are next to one another in one room and quite some distance away is my manifold, which is next to the pump and 2 port UFH valve. There is a 2.5mm and also a 5 core cable between the two which I can utalise.

My next step is proably to tidy up my circuit and make it as efficent as possible with cables going to each component.

Regarding the link: I have attached a photo of the current boiler wiring, this is currently connected to an old honeywell thermostat which will be replaced with my nest heatlink. I premume the link that needs to be removed is already removed?

Last thing... Might be a stupid question but how does the hot water work?

Thanks so much
 

Attachments

  • UFH wiring5.pdf
    23.4 MB · Views: 8
  • current boiler wiring.jpg
    current boiler wiring.jpg
    163 KB · Views: 10
The link has already been removed because of the external controls already fitted.

The link there is for the hot water which is operated by a flow switch within the boiler, the link stays in unless you have external controls to decide what times the pre-heat function works (pre-heat keeps the water in the heat exchanger hot to reduce time to get hot water to the taps, personally I have mine off because it wakes me up when it comes on.) You could use your nest for this.

It looks like it may be wise to have a wiring center next to the boiler and then take that 5 core across to the UFH.

Its definitely best practice to have one spur feed the lot so the plumber can isolate it safely to carry out work. You can add additional isolators and its common to put an isolator for the entire UFH, I typically see fan isolators for this because its 3 pole for the L/N/SL (terminal 10 in my drawing)

I was also wrong you only need a 3 core between UFH center and main wiring center.


To clarify your drawing;

Spur at the UFH is an isolator?

Personally I wouldn't be wiring straight into the boiler with the oranges, try and put a junction box or better the main wiring center next to the boiler. Try and keep just 1 cable going to the boiler if possible 2 max

Your grey on the UFH 2 port valve wants to be into a permanent live. You currently have the brown from the 2 port connected to the permanent live and going into the pump terminals of the UFH wiring center (basically a link wire) this looks like it should be removed?

2 port valve neutral wants to go to the main neutral not the one on the boiler relay (I think based on other wiring diagrams and presuming the boiler relay is acting as a SL to fire the boiler)
 

Reply to Wiring UFH system help in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi folks, hoping someone can help with a problem that's been perplexing me since just before Christmas..... I have a wet underfloor heating system...
Replies
19
Views
1K
P
Hi, I'm after some advice on converting my current CH system to Wiser smart system. In particular, looking for advice on whether I can use the...
Replies
1
Views
1K
Hello I'm new to the forum and wanted to ask a question after having a good read. House is undergoing a complete renovation and new pipework needs...
Replies
5
Views
928
  • Question
HI, we have replaced 3 manifolds (1 upstairs 2 downstairs) with new Warmup units. The installation manual from Warmup states that to fill the...
Replies
6
Views
820
Hi, I have a combi boiler that supplies hot water to two ufh manifolds. We only have ufh and no radiators. I am trying to find the most efficient...
Replies
1
Views
1K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock