Pressure testing 63mm gas pipe

View the thread, titled "Pressure testing 63mm gas pipe" which is posted in Gas Engineers Forum on UK Plumbers Forums.

One of these yellow tags

Screenshot_20181219-121823_WhatsApp.jpg


Screenshot_20181219-121823_WhatsApp.jpg
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar


Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.

Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.

Thank you all
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
 
So went to pressure test this job but the pipe was not installed to regs. They had run yellow mdpe into the building which if I remember correctly is a no.

I do know the gas board do this though when replacing the mains to the meter inside the house with mdpe by pushing it up the old pipe.
Any pics?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Pressure testing 63mm gas pipe" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
mutley racers,
Last reply from
mutley racers,
Replies
95
Views
2,616
Back
Top