I thought it was thrashed out re the ABV positioning and the consensus was that it is installed correctly, my only slight unease concerns the vertical "return" pipe, this has a motorized valve attached which I would have thought is a bit unusual as they are normally installed on the flow.
I will just repeat what I said in some other post above, with the boiler firing normally and up to temperature, open (anticlockwise) the ABV fully to index 0.1, if the pipes on both sides of this don't get "red" hot in less than say 1 to 2 minutes then you have a problem. Just re close (clockwise) the ABV fully to index 0.5 after the test.
Just tried this. The pipe on the return side doesnt get red hot just slightly hot when fully open. I have waited a good few minutes.
 
Not sure where the heating return connects sorry

Thanks, if the pipes on either side of the AAV are/were cold, the HW MV closed. With boiler on to CH, if you opened up the AAV fully do the pipes then get hot on both sides of it within a minute or less?. if they do then the AAV is operating/installed correctly, if they don't the there is something wrong.
I appreciate the question was asked a few times but not sure of your reply.

Edit: Just saw your other posts, thanks.
 
Thanks, if the pipes on either side of the AAV are/were cold, the HW MV closed. With boiler on to CH, if you opened up the AAV fully do the pipes then get hot on both sides of it within a minute or less?. if they do then the AAV is operating/installed correctly, if they don't the there is something wrong.
I appreciate the question was asked a few times but not sure of your reply.

Edit: Just saw your other posts, thanks.
Just done it. The small return pipe is only slightly warm. Nowhere near as hot as the flow pipe.
 
Just tried this. The pipe on the return side doesnt get red hot just slightly hot when fully open. I have waited a good few minutes.

There is definitely something amiss then, if the boiler and system contents are up to near normal running temperature of say 60 to 70C then both sides of the AAV should get equally very hot in a very short time when opened fully as you are effectively short circuiting the flow&return pipework.
 
There is definitely something amiss then, if the boiler and system contents are up to near normal running temperature of say 60 to 70C then both sides of the AAV should get equally very hot in a very short time when opened fully as you are effectively short circuiting the flow&return pipework.
The radiators had been fully on for only 10 mins. My boiler is set at 65. Maybe I didn't leave it long enough?
 
Perhaps, but you did say that the return is cool in comparison to the flow, try again after say 20 minutes, and let us know the result.
 
Perhaps, but you did say that the return is cool in comparison to the flow, try again after say 20 minutes, and let us know the result.
Thanks. So do I have to turn all rads fully on our can i just do it to 1 to make the boiler fire up and stay on? Bit of a pain having to keep going round them all
 
Hi. Another question. This isn't my cylinder but I have one of the little white cylinders too. But mine is at floor level. What is it?

7C4BD9AB-C2D0-4454-9AC8-3A35AB622002.png
 
Just 1 will do, just make sure the boiler is firing, thats all, or if you go to the boiler now and feel the Flow (top) pipe it should be quite hot, once it is just open up the AAV and both sides of it should get very hot as well in a very short time.

The "white cylinder" is a expansion vessel.
 
Just 1 will do, just make sure the boiler is firing, thats all, or if you go to the boiler now and feel the Flow (top) pipe it should be quite hot, once it is just open up the AAV and both sides of it should get very hot as well in a very short time.

The "white cylinder" is a expansion vessel.
Thanks. Just ran it with 1 on for literally a few seconds and it got red hot straight away. Wonder why it didn't do that earlier.
 
Both sides of the AAV got red hot??

OK' it looks as if it did, now can you set the AAV (temporarily) to index setting of 0.2 with boiler on, then stop the boiler and see if you are still getting that whooshing sound from the rad.
 
Last edited:
Both sides of the AAV got red hot??

OK' it looks as if it did, now can you set the AAV (temporarily) to index setting of 0.2 with boiler on, then stop the boiler and see if you are still getting that whooshing sound from the rad.
Thanks. Yes red hot. It only makes the crackling sound now and again. I can't make it do it so will have to test over a few days. Just for info when the boiler fired up the water loudly gushed around all the pipework for about 30 seconds or so.
 
Hi. Sorry for the late replies I did not get notifications. The boiler is downstairs under the stairs directly below the airing cupboard. The pump is in the boiler I don't have one seperatesl as far as I know
From what I’m gathering from your info the flow is on the right hand of the pic and the zone valve is on the return. If this is the case then B has to go to the boiler for it to work the way it’s been piped.
 
  • Optimistic
Reactions: Tigermad
Thanks. Yes red hot. It only makes the crackling sound now and again. I can't make it do it so will have to test over a few days. Just for info when the boiler fired up the water loudly gushed around all the pipework for about 30 seconds or so.
Gushing sound; sounds like air in the system.
 
Gushing sound; sounds like air in the system.
There's nothing coming out of the rads when I bleed apart the from the towel rail that needs bleeding every week or so because the toprails don't get as warm. Lots of air comes out when I do that which is strange for a sealed system. Been doing it for over a year.
 
There's nothing coming out of the rads when I bleed apart the from the towel rail that needs bleeding every week or so because the toprails don't get as warm. Lots of air comes out when I do that which is strange for a sealed system. Been doing it for over a year.
If the towel rail constantly needs bleeding and nothing else does then it could be an issue with the towel rail which is quite common
 
  • Informative
Reactions: John.g
Is there a AAV (automatic air vent) or a number of them in your system, if there is just check if the little cap on the air nozzle(s) on top of the AAV is open or shut, some prefer just to open these occasionally just to check for any air once all the air has been expelled after a drain down/refill of the system.

What pump/model have you got and what setting is it on?.
 
Is there a AAV (automatic air vent) or a number of them in your system, if there is just check if the little cap on the air nozzle(s) on top of the AAV is open or shut, some prefer just to open these occasionally just to check for any air once all the air has been expelled after a drain down/refill of the system.

What pump/model have you got and what setting is it on?.
Hi. No aavs on system. The only pump I have is inside the boiler as far as I know. Is that right for an unvented system?
 
That's correct (gas boiler) and you can't access it (not GSR) , post #57 above suggests that it could be a issue with the towel rail.

I meant to ask you this before, why did you decide to fit a ABV??, was it because the boiler manufacturers require it or some other reason.
 