Crikey that’s was some read!!
I teed in a prv to outside on a system where the boiler was located in a cellar below ground, spoke to vaillant who told me to blank off the boiler prv and install remotely then leave a sign on the front of the boiler.
 
I can't see any issue either, it's only like Baxi's remote PRV kit they sell. As long as the PRV is on the system and cannot be isolated from the boiler by the means of isolation valves then I don't see any issues.
 
Crikey that’s was some read!!
I teed in a prv to outside on a system where the boiler was located in a cellar below ground, spoke to vaillant who told me to blank off the boiler prv and install remotely then leave a sign on the front of the boiler.
thanks mate thats good to know
[automerge]1572381238[/automerge]
I can't see any issue either, it's only like Baxi's remote PRV kit they sell. As long as the PRV is on the system and cannot be isolated from the boiler by the means of isolation valves then I don't see any issues.

Cheers mate
 
In answer to the OP, stating the obvious I know, but the boiler is the heat source and should be the perfect point in system for installing a PRV.
On a system or combi boiler the PRV part of the boiler anyhow.
The expansion vessel kits are irrelevant.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Pressure relief valve install" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Leeboyguv,
Last reply from
Best,
Replies
29
Views
3,869
Back
Top