Hello all

I’m looking for some clarification as to what electric works plumbers / heating engineer can undertake. It seems to be a grey are with part p defined scope etc which I believe has gone? And that part p is just a building Reg and not a qualification. So in light of my confusion some help is wanted.


so what can a plumber / heating engineer do. I mean with no electrical quals or part p.

I don’t just mean that they have the skill to do it but they have the legal right to do it. Aren’t breaking any buildings regs etc

can a gas safe heating engineer wire a new boiler into an existing fused spur even in a kitchen . ?


Can a plumber replace like for like electric shower

can a plumber replace a heating system component such as a zone valve, pump, thermostat - including wiring it into wiring centre

can they fit a new room stat as part of a new boiler

I very much believe in doing things correctly and doing the best I can.
 
I was certified working from fused spur and wiring full system, changing anything on the sysyem can’t remember if this was due to BG electrical training also taking nvm level 3 when we started gasforce
 
I completed my essential electrics and our electrical manager has no problem me changing like for like stuff, adding wireless stats (from the boiler supply), etc.
 
If you are changing the fixed wiring then you need to be competent to install, test, certify etc

If you are changing like for like then crack on BUT if in the shower example the manufacturers instructions say the circuit needs RCD protection and there isn't any, you need to get this resolved ............
 
If you are changing the fixed wiring then you need to be competent to install, test, certify etc

If you are changing like for like then crack on BUT if in the shower example the manufacturers instructions say the circuit needs RCD protection and there isn't any, you need to get this resolved .

Thank you very much for this. What is the definition of fixed wiring?

do you mean the wiring up to for example the fused spur or the cabling up to the shower.
Does an appliance such as a shower, a shower pump, a boiler , a central heating control System that are all hard wiring count as fixed wiring?

does it count as changing the fixed wiring or the circuit when you swap like for like
[automerge]1605170638[/automerge]
I completed my essential electrics and our electrical manager has no problem me changing like for like stuff, adding wireless stats (from the boiler supply), etc.

Thank you for your reply. What course did you do for electrics
 
Thank you very much for this. What is the definition of fixed wiring?

Thank you for your reply. What course did you do for electrics

To me the definition of fixed wiring, is it’s a fixed part if the circuit, eg socket outlets, lighting. Non fixed is something that can usually be moved by means of flex cable, eg a boiler, zone valves, etc.

My course was called essential electrics, ran by citb, however I’m led to believe this one (citb) is no longer available.
 
To me the definition of fixed wiring, is it’s a fixed part if the circuit, eg socket outlets, lighting. Non fixed is something that can usually be moved by means of flex cable, eg a boiler, zone valves, etc.

My course was called essential electrics, ran by citb, however I’m led to believe this one (citb) is no longer available.

great. Thank you for taking the time to reply. So is a shower fixed or non fixed. ?
 
This might be one for @Murdoch or any other person with more knowledge, but I’d say the wiring to the pull cord is fixed, possibly even the wiring to the shower, but if you’re doing a like for like, eg same kw rating but have to move the wire slightly, I’d say it’s ok.
 
Anything after the fused spur I'm happy to change/wire. S plan, y plan etc. Experience has found not a lot of electricians are actually comfortable when it comes to heating controls.
Showers like for like after a look at the fuse board to confirm rcd. If I'm not happy or unsure then its bring in the electrician time.
Even when I'm doing a bathroom you need yours eyes open for the lighting. Lots of lights in bathrooms dont meet the regs. I simply say to the customer that they need to get them sorted.
 
great. Thank you for taking the time to reply. So is a shower fixed or non fixed. ?

A shower is fixed when the supply cable runs in the fabric of the building, same as for any other circuit really.

If something is plugged in its not fixed

Fused spurs can get complicated .........

The other thing to watch out for with showers is higher wattage, cable size etc ..........
 
A shower is fixed when the supply cable runs in the fabric of the building, same as for any other circuit really.

If something is plugged in its not fixed

Fused spurs can get complicated ...

The other thing to watch out for with showers is higher wattage, cable size etc .

Thank you murdoch. So can plumbers replace an electric shower? can they wire into a fused spur?
 
so a fused spur that has the wiring before the spur that is in trunking or wall mounted is okay to wire into but if it’s in the wall it’s not?
Some of the confusion here may be because the word 'spur' can refer to several different things. I'd use it to mean a branch circuit tee'd off a main circuit. It's also often used to refer to what I'd call a fused connection unit (FCU). FCU's come in several types, one of which is a flex ('pigtail') outlet that are often used to supply things like immersion heaters or boilers*.

My reading of @Murdoch is that in his opinion it's okay for you to connect flex into an existing FCU flex outlet but from there back to the consumer unit will be 'fixed wiring', which requires additional qualifications to work on. Where the FCU is being used as an isolator, not a flex outlet, it's a job for an electrician.

(*) There's a school of thought that holds that boilers should be connected via a 13A plug and socket so that a heating engineer can visually verify isolation before working on the boiler.
 
Last edited:
thank you for your replies by fused spur I mean the white box that things like boilers , shower pumps , immersion heaters are wired into
[automerge]1605252947[/automerge]
thank you for your replies by fused spur I mean the white box that things like boilers , shower pumps , immersion heaters are wired into.

mu understanding is that these are called fcu’s
 
Last edited:
So for me to be clear In my head lol Can a plumber Wire into an fcu (which I understand to be a fused connection unit at the end Of a spur or even on its own circuit from consumer unit) - a shower pump, a boiler, an immersion heater for a hot water cylinder. and also a zone valve and pump wired via the wiring centre. I’m envisaging the common situation face by plumbers whereby one is broken and needs replacing like for like.

Can this be done without being qualified electrically?

is it notifiable or minor works etc such that an electrician is required each time you want to swap a heating system component.
 
My understanding is that 'installing fixed electrical equipment is within the scope of Part P, even if the final connection is by a standard 13A plug and socket, but is notifiable only if it involves work set out in regulation 12(6A).' (ADJ, p.7)

I used to think that this heating control wiring needed to be carried out by a competent person or be notified under the building regulations. I have since been advised (on this forum) that this isn't what is meant by control wiring (which is, or used to be, notifiable).

In practice, I would rather do the work and then ask an electrician to check and formally sign the work off as most electricians understand electrical safety but not heating controls. This relies on a good working relationship with an electrician, however. It is worth noting that it is would be a small minority of electricians that would go to the effort of testing and recording the replacement of, say, a lamp pendant, provided the light goes on and off with the switch.

I suspect the technical answer is that while a lot of those works )even a directly like-for-like replacement of an electric shower) may not technically require to be notified, they still need to comply with the building regulations. As we are plumbers and do not have a comprehensive understanding of BS7671 (The IEE regs), nor do we have the specialist calibrated equipment with which to test any work we may carry out, then technically we would be unable to ensure that our non-notifiable work is 'inspected, tested and certificated in accordance with BS 7671' (ADJ, p. 10).
 
Can this be done without being qualified electrically?
Here's my opinion for what it's worth.

A plumber with literally 'no electrical quals or part p.' should not be doing any work involving electricity in a customer's home until they have passed a recognised 'basic electricity for plumbers' course. This will teach you things like isolation, proving isolation, visual inspection, simple electrical tests using a multimeter, preparing and making straightforward connections, etc. It will also make it clear what you are and are not qualified to do. If you tell the instructor what sort of work you want to do they'll be able to say whether you're covered or which additional course(s) you need to take.

This is largely for your own protection. You do not want to injure yourself (hence the 'isolation') and you don't want to be the totally unqualified plumber who is being accused by a customer of incompetent electrical work.

Firstly, make a list of what you want to be able to do and contact your local college to see what they have on offer in the way of suitable courses. Secondly, try to develop a good working relationship with an electrician who can help you out with small jobs if necessary.
 
Last edited:
As we are throwing in opinions. Mine would be the fact that if the wiring is powering something that is already in place then an Heating engineer can wire up any part of the heating system he wishes as long as he holds the correct qualifications for that appliance. If however, he was taking out storage heaters and and immersion heater and putting a combi in the kitchen and a new spur is needed then a sparks should be doing the works. Or an engineer with electrical qualms.
 
Where are these electricity for plumbers or basic electricity for plumbers courses? any recomendations
Here's an example of the sort of thing I had in mind:
I'd always start with a local / regional further education college as their courses are usually good quality and good value. If you're going to spend a significant amount on a course do your research and make sure you understand what you are getting and who will be teaching assessing and accrediting it before signing up.
 
Last edited:
While I agree with the opinions being ventured in this thread, I'm not sure whether they answer the question, which was, I think, "technically and legally what should we do?"

Reason I say this is that someone with an Intermediate Amateur Radio Licence is allowed to build his or her own radio (mains powered electrical), having (usually) studied the RSGB material. But then this person is not considered to be electrically qualified. The irony is that while I have been assessed as competent to wire a so-called "13A" (technically a BS1363) plug and build my own amateur radio as far as the RSGB is concerned, I'm not qualified to do so in other fields, even though it's exactly the same plug!

Why is this relevant? It's relevant because the C&G NVQ2 course contains an electrical element.. We are taught how to carry out very basic tasks such as junction boxes and FCUs and the safety aspect at a basic level and then told this isn't a qualification. Why, then, are we being taught this, if it doesn't make us competent? Well, because C&G knows you'll probably end up doing this sort of thing anyway and they'd rather you had at least a basic level of electrical education (my assessor's answer).

Similary, the BPEC course gives you a level of knowledge that then still doesn't make you a competent person. Not that I don't think it's a good idea, though useless to plumbers who lack the ACS CCN CEN gas certificates (pre-requisites). 'It has been designed with plumbing and heating engineers in mind and is limited to work that will NOT involve working on fixed installation of the property and addresses the following scope of work.' So you still wouldn't be legally allowed to do anything except repair the boiler, I take it?
 
Does competent mean having a certificate?

If a third party looks at/tests an installation and all is done to regulations and in a neat/tidy way then they would have to come to the conclusion that it was done competently.

This assessment of the work could not determine who it had been done by...

So does it matter if this was carried out by an electrician, brain surgeon, footballer or trained monkey?
 
Does competent mean having a certificate?

If a third party looks at/tests an installation and all is done to regulations and in a neat/tidy way then they would have to come to the conclusion that it was done competently.

This assessment of the work could not determine who it had been done by...

So does it matter if this was carried out by an electrician, brain surgeon, footballer or trained monkey?
Yes, it means a certificate. Hence some of the shoddy electrical work I see was carried out by 'competent' persons.
 
Does competent mean having a certificate?

If a third party looks at/tests an installation and all is done to regulations and in a neat/tidy way then they would have to come to the conclusion that it was done competently.

This assessment of the work could not determine who it had been done by...

So does it matter if this was carried out by an electrician, brain surgeon, footballer or trained monkey?

Not just this.

No decent sparks sign off 3rd parties work - why would you?

What I come across is plumbers adding spurs to spurs, disconnecting the main equipotential bonding, and replacing showers without RCD's or a higher rating with insufficient cable size and / or breakers
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "What electric works can plumbers undertake" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
midsman,
Last reply from
Harvest Fields,
Replies
50
Views
9,823
Back
Top