Got a brand new 25mm hdpe incoming main with pressure of 2/2.5 bar. Need to check flow rate but doesn’t look great at kitchen sink. The main connects to stopcock and is run in 28mm directly to cylinder which is located on 2nd floor of a town house. Hot and colds are run out in 22mm. It serves a shower and basin on the same floor, a main bathroom on 1st floor and WC on ground floor. Shower runs ok on top floor but when opening bath on 1st floor it pretty much stops. Any ideas on problems? Mains has been flushed and combination valve checked for debris etc.

Jim
 
Sounds as if its a supply issue this is becoming a common problem especially in 3 storey town house's there's such a demand on the water supply that the pressure is a lot less in the main you need a constant 3 bar and 20+ litres a minute flow firstly check your stopcock is fully open and any supply valves, water pressure and flow is decreased the higher the water has to travel multiple outlets running will result in poor performance if no faults are found , it may result in you needing a accumulator or a booster pump to achieve a satisfactory performance. Regards kop
 
Always measure main before recommending unvented or mains reliant systems. 3bar and 20litres/min a good minimum guide. Design outlets and pipework to cope with simultaneous demand.
 
Pressure at incoming main is 2 Bar with a flow rate of 7 litres per min.

28mm main runs to top floor of a townhouse so 2nd floor. Goes through combination valve at cylinder which is completely clear of debris and is working. Balanced cold then runs down to ground flooring 22mm, teeing off for top floor bathroom, teeing off for 1st floor bathroom and ending up at utility on ground floor

flow at utility sink on balanced cold is 11 litres per min

flow at 1st floor bath tap is 22 litres per min

flow top floor shower is 11 litres per min

As people have said you would expect 3 Bar and 20 litres per min on incoming main. Obviously inconsistency in readings between main and balanced flow rates. Would this be down to cylinder location and pressure flow rates at main or can anyone suggest an issue with how pipe work is run internally?
 
Maybe there's a PRV installed upstream of the PG because if not and both the taps where the flows were taken are similarly sized then it would require nearly 20 bar to increase the flow rate from 7 to 22 LPM. If one is 1/2" and the other 3/4" then if 2 bar is the dynamic pressure in both cases one might expect ~ 15 LPM from the bath tap?.
 
Last edited:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Problems running multiple outlets with unvented system in new build" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
jimmy84,
Last reply from
John.g,
Replies
10
Views
3,105
Back
Top