When I moved into my bungalow 10 years ago the central heating was a nightmare. Hot water cylinder on the ground floor and presumably lack of general use of zone valves back in 1971 when the system was installed meant that 2 pumps had been installed. Firing of the boiler was controlled by a 4 pole contactor which was wired incorrectly so hoy water and heating functions were mixed and confused.
I was unable to persuade any local heating engineer to even come and look at it so I set to myself. I sorted the contactor wiring so that the right pump ran according to whether the call was for heat or hot water but a common return meant there was still some crossover between the systems. I sorted this by moving the cylinder from the bathroom into the roof space closer to the kitchen and fitted zone valves on the two systems. Functionally the system now worked properly. Some radiators already had TRV's fitted and I added them to radiators which did not have them, leaving one in the Hall where the Thermostat was located as manual .

We still had problems getting the system right in terms of room temperatures so I installed a Honeywell Sundial Programmer Thermostat but it didn't really solve the problem.

I'm still very technical so decided to look at Smart TRV's. We probably won't be here for years to come so I looked at a fairly low cost approach , ignoring Hive, Nest and others. I bought unbranded Valve heads which actually work quite well and are extremely quiet in operation. I thought that as it is possible to know when the set temperature has been reached in each room then it seems logical to turn the boiler off when no heat is required by any radiator and turn it on again when any radiator calls for heat - First question - Is this a valid assumption?

My problem is that the valves I have bought seem to have a mind of their own and partially open or close as the room temperature approaches the set temperature either rising or falling rather than opening when the temperature is below the set temperature and closing when the temperature. I'm pretty sure that this is the way a standard TRV would operate and the Smart TRV has no other variable user input other than the Set temperature. It is not able to account for other possible sources of heat in the room and therefore shouldn't make that assumption. Second question - is this a correct summary.

The real issue is `illustrated by an actual happening 2 days ago. The Lounge was set at 22° and the recorded room temperature 22.5° The valve was showing as open at 50%. My external control logic assumes anything less than 51% open is in fact closed and will turn the boiler off if no other valves are open. So the boiler and central heating pump were both off. I decided I wanted a shower. The Shower room was set at 15° and the actual temperature was 19° so the valve opening was 0%. I set the temperature to 22° and the valve opened to 100%, the boiler fired, the pump ran shower warmed up nicely but the Lounge radiator got a new heat hit because it was 50% open. The lounge suddenly became uncomfortably warm as the large radiator dissipated that heat.

Final question for now if you aren't totally bored - Is it reasonable to go back to the valve manufacturer (I'm led to believe that my supplier can do this) and request a modification to the software in the valve and suggest as it stands, it is not fit for purpose?

My boiler by the way is an Oil fired Boulter Classic which I believe to be the original installed in 1971
 
I thought that as it is possible to know when the set temperature has been reached in each room then it seems logical to turn the boiler off when no heat is required by any radiator and turn it on again when any radiator calls for heat - First question - Is this a valid assumption?
Not really, because boilers have a minimum output power.

My problem is that the valves I have bought seem to have a mind of their own and partially open or close as the room temperature approaches the set temperature either rising or falling rather than opening when the temperature is below the set temperature and closing when the temperature. I'm pretty sure that this is the way a standard TRV would operate and the Smart TRV has no other variable user input other than the Set temperature. It is not able to account for other possible sources of heat in the room and therefore shouldn't make that assumption. Second question - is this a correct summary.
Not really. Broadly speaking, traditional TRVs use the expansion and contraction of a working substance (for example melting wax) to throttle the flow, i.e. 'proportional (P)' type control over a band of a few degrees between fully open and fully closed. Smart TRVs can employ more sophisticated control strategies and these vary between makers and models. What you have described could either be a form of 'proportional+differential (PD)' control or possibly a heuristic method that treats rising and falling temperatures differently perhaps as a way of introducing hysteresis to prevent 'hunting'.

The real issue is `illustrated by an actual happening 2 days ago. The Lounge was set at 22° and the recorded room temperature 22.5° The valve was showing as open at 50%. My external control logic assumes anything less than 51% open is in fact closed and will turn the boiler off if no other valves are open.
I can't see that working. The controller needs to shut down the boiler when the emitter system is dissipating less than the boiler's minimum output.

Final question for now if you aren't totally bored - Is it reasonable to go back to the valve manufacturer (I'm led to believe that my supplier can do this) and request a modification to the software in the valve and suggest as it stands, it is not fit for purpose?
There's no law against trying. Whether you are successful or not will probably depend on how many of the modified valves you want. Don't expect to get an answer unless you're placing an order for a very large number.

The conventional way to set up a domestic heating system is to balance the radiators with all TRVs fully open so that the house can be maintained at the correct temperature by the system thermostat, normally in a hallway, which turns the boiler on and off. The TRVs are there to trim out variable external influences such as solar gain reducing the heat required in south facing rooms on sunny days. If you want to use TRVs to make every room an independently controllable zone you really need a buffer tank to act as a thermal reservoir that removes the 'minimum output power' constraint. People who install 'smart home heating controls' often overlook this point and the system performs below par as a result.
 
Last edited:
Thanks for that quick reply Chuck

I did think I should try and provide a little more detail about the boiler itself because I haven't really looked at it for a long time.

It is in fact a Boulter Classic 70/90 commissioned in 2001.


Not really, because boilers have a minimum output power.

The only external electrical connection is a 3 core 240V supply cable and the only internal control is a knob without any real markings on it which is presumably to set the actual primary circuit temperature and to set the output power within the range.

Surely it is better to turn the boiler off when none of the rooms being heated require heat than to control this from a central thermostat.







Not really. Broadly speaking, traditional TRVs use the expansion and contraction of a working substance (for example melting wax) to throttle the flow, i.e. 'proportional (P)' type control over a band of a few degr ees between fully open and fully closed. Smart TRVs can employ more sophisticated control strategies and these vary between makers and models. What you have described could either be a form of 'proportional+differential (PD)' control or possibly a heuristic method that treats rising and falling temperatures differently perhaps as a way of introducing hysteresis to prevent 'hunting'.



I can't see that working. The controller needs to shut down the boiler when the emitter system is dissipating less than the boiler's minimum output.

The valveheads I have bought do have very poor documentation but they do have one parameter that can be set which is defined as Control Type of Valve and the options of either PID or ON/OFF. I have set these to ON/OFF . I would expect the valves to operate in the way you describe with the PID option selected but would also expect them to be open or closed when the ON/OFF otion is selected - Does that seem unreasonable. As I said, the documentation is bad and doesn't define what the effect of choosing between the option actually does.
 
The valveheads I have bought do have very poor documentation but they do have one parameter that can be set which is defined as Control Type of Valve and the options of either PID or ON/OFF. I have set these to ON/OFF . I would expect the valves to operate in the way you describe with the PID option selected but would also expect them to be open or closed when the ON/OFF otion is selected - Does that seem unreasonable.
Firstly, ON/OFF control requires hysteresis, i.e. ON a little below setpoint and OFF a little above setpoint, to avoid instability sometimes known as 'hunting'. Secondly, you don't really want TRV's to snap closed instaneously because that will result in a sudden rise in the return temperature, which when it arrives back at the boiler may cause lock-outs or other issues.

Obviously, the details of what will actually happen are specific to each system and boiler. I don't recall (if I ever knew) how your boiler would behave and I haven't tried to look it up.
 
I have no prior knowledge of your boiler. If it be old enough to work on a semi-gravity system and if it has a large internal heat exchanger you may find it would run quite happily without any minimum flow. Some old boilers eg the Housewarmer range, with no flow at all but a call for heat from the thermostat, would just warm up to set temperature and then stop firing until they started to cool down.
 
I have no prior knowledge of your boiler. If it be old enough to work on a semi-gravity system and if it has a large internal heat exchanger you may find it would run quite happily without any minimum flow. Some old boilers eg the Housewarmer range, with no flow at all but a call for heat from the thermostat, would just warm up to set temperature and then stop firing until they started to cool down.
Hi Ric

Yes this is no measly wall mounted affair. The hunk of cast iron above the top of the burner is about 40cmx40cmx37cm and there is no other way to control it other than to switch the mains on and off
 
Controlled by a thermostat in a pocket on the heat exchanger itself as opposed to clipped onto the flow pipe leaving the lump? No pump over-run or overheat cut-out? If I'm guessing correctly then I would also guess the effect of being switched off suddenly will be a heat surge and possibly near-boiling inside the boiler and then everything settles and that's only if you're running the boiler at 80d egrees int he first place.
Even if I'm wrong and the boiler installtion instructions require a minimu flow or over-run this can normally be achieved by an ABV or a radiator with the TRV removed such that it is permanently on.
Your smart trv system does sound a bit weird in fairness to you.
 
Controlled by a thermostat in a pocket on the heat exchanger itself as opposed to clipped onto the flow pipe leaving the lump?

Yes

No pump over-run or overheat cut-out?

There is a red reset button on the front of the burner. But other than the thermostat that is it
If I'm guessing correctly then I would also guess the effect of being switched off suddenly will be a heat surge and possibly near-boiling inside the boiler and then everything settles and that's only if you're running the boiler at 80d egrees int he first place.

Surely what I am doing is no different from what the wall Thermostat in the hall would do? I'm also treating a valve opening of 50% as being closed so all the radiators could be at 50% when the boiler was turned off but at least one would be. The boiler doesn't turn back on until at least one radiator is more than 50% open.


Even if I'm wrong and the boiler installtion instructions require a minimu flow or over-run this can normally be achieved by an ABV or a radiator with the TRV removed such that it is permanently on.

The very first radiator in the system which sits just above the pump has its lockshield turned down low and its TRV set at 35° . It heats the airing cupboard and acts as a by-pass.

It may sound odd because I agree it may be very non standard but I already appear to have more accurate control of my room temperatures and my boiler-on time is very short at the moment. We do supplement the central heating with a log-burner during the colder months and how the system reacts when that is brought into play will be the crux.
 
Last edited:
Not sure I'm making my point clear. What I meant was I can't really understand the logic of your fancy system (which I take it you would have designed rather differently). It doesn't really seem very well designed unless it has a way of learning the heating characteristics of the house and tweaking how it controls the valves. A bathroom 4°C below setpoint not calling for heat sounds frankly crazy.

I created a completely 'dumb' version of what you have many years ago using a number of zone valves and room thermostats that simply turned the boiler and pump on and distributed the heat to the rooms requiring heat. It was arguably inefficient in that it would run a 0.6kW radiator off a 13kW output boiler (which was cycling madly) rather than waiting for a few rooms to need heat and heat them simultaneously, but because the boiler was similar to yours it coped with the situation. I still think it used less gas than heating the whole house needlessly. It would still technically overheat as the radiators would be red-hot when the valved shut, but because the radiators were not oversized, this was a very minor symptom. Point is, a 'smart' system should be superior!

Chuck commented that your observation I thought that as it is possible to know when the set temperature has been reached in each room then it seems logical to turn the boiler off when no heat is required by any radiator and turn it on again when any radiator calls for heat - First question - Is this a valid assumption? was not necessarily valid as a boiler has a minimum output and I agree with him, as logic is now probably to prevent a modern boiler cycling by keeping above its minimum output and thus run the radiators on tickover and allow the boiler to do the same rather than overheat the rooms slightly, allow them to cool slightly and then repeat. As yours cannot control the flame except on/off, the boiler will have to cycle to keep to the required output. but it should still work. All I can assume is that the TRVs are assuming that the radiators are only large enough to keep the room warm and so will not overheat by providing a pretty decent flow at just below the set temperature. Which obviously won't be the case in the early heating season when your radiators will have excess capacity.
 
Last edited:
As Chuck mentioned before, the simplest way to control individual rooms via TRVs is by using a buffer tank and a smart pump. Then you don't need any room thermostats or zone valves, and you can get rid of the bypass (maybe the tank would fit there?), and program each TRV for whatever temperature schedule you want in each room.
 
A bathroom 4°C below setpoint not calling for heat sounds frankly crazy.
I'm sorry Ric I think you may have misread that - The Actual Temperature in the Bathroom was 19 with the Set Temperature at 15 not the reverse. I just wanted it a little warmer.

There are a number of factors that have made me follow this route. I'm 73 years old and will probably only be in this house for another few years, certainly not long enough for there to be any payback on a boiler replacement and probably not even by installing new and better sized and distributed radiators. The rooms in this bungalow are very large as are the windows. The Lounge , main bedroom and hallway all have SSW facing windows. The Lounge is about 25 sq metres with a single radiator and even the hallway where the wall thermostat is located is close on 14 sq metres with a half glazed door with side panels about 2.5 metres wide, so quite susceptible to temperature change from the late afternoon/early evening sun or from opening the external doors at either end. It certainly isn't the best place to have a thermostat to control the overall house temperature but that is where it is. I have tried a Honeywell Sundial thermostat but it wasn't hugely successful.

With weather as it is at the moment, dull one moment and blazing sunshine the next I'm already seeing the benefits in terms of comfort. To be able to tweak the set temperature on the radiator whilst sitting in my chair is already worth the relatively small amount I have spent. Also when I come to leave the property, an hours work in fitting the old valveheads back and 5 minutes disconnecting and reconfiguring the remote boiler switch and, the system will be back to a operable "standard" dumb state.

If I find that what I have done does not work effectively I merely have to re-program the hall thermostat, turn the boiler programmer back to Auto and disable the piece of software that switches the boiler on or off right now but at the same time I can still keep the individual room programmes in the valves but know that the hall thermostat will control the maximum temperature at any moment in time.

I did find this website when I was researching Short Cycling - Boiler Short Cycling - http://www.home-heating-systems-and-solutions.com/boiler-short-cycling.html and was interested to read this
Screenshot 2021-10-12 212900.png


solution. Which is effectively what I'm doing except I have 10 Thermostats
 
As Chuck mentioned before, the simplest way to control individual rooms via TRVs is by using a buffer tank and a smart pump. Then you don't need any room thermostats or zone valves, and you can get rid of the bypass (maybe the tank would fit there?), and program each TRV for whatever temperature schedule you want in each room.

Firstly I only have 2 zone valves which isolate the central heating and hot water circuits from one another. The only room Thermostat that I have is now set to 35°c 24 hours a day so it is constantly on and the WiFi TRV's control the temperatures in each of the rooms . I don't want to get rid of the radiator which serves as a by-pass (which I probably don't need) because it warms the airing cupboard . I still need to research Smart pumps but there don't seem to be many available at present and I suspect that the big cast iron heat exchanger in my 20 year old very dumb boiler acts as its own buffer. After having the heating switched off for 30 minutes, the radiator in my kitchen became too hot to hold your hand against for any period of time in less than a minute after switching the heating on again.

Thanks for your input.
 
Firstly I only have 2 zone valves which isolate the central heating and hot water circuits from one another. The only room Thermostat that I have is now set to 35°c 24 hours a day so it is constantly on and the WiFi TRV's control the temperatures in each of the rooms . I don't want to get rid of the radiator which serves as a by-pass (which I probably don't need) because it warms the airing cupboard . I still need to research Smart pumps but there don't seem to be many available at present and I suspect that the big cast iron heat exchanger in my 20 year old very dumb boiler acts as its own buffer. After having the heating switched off for 30 minutes, the radiator in my kitchen became too hot to hold your hand against for any period of time in less than a minute after switching the heating on again.

Thanks for your input.
Sorry, I should clarify. By "smart" pump, I didn't mean something fancy with Wifi or remote control features or anything like that, I meant a pump that modulates, so that when the TRVs open, they pump more. They are very common now. You leave the pump on all the time you want heating available, and when the TRVs are all closed, it will throttle down to a few watts. When one or more TRVs open, it will pump faster. You hook that to a buffer tank which provides the supply of hot water, which is always there whether the boiler is on or not. The boiler then heats the tank to a fixed temperature with a simple cylinder stat, so there is no cycling and no bypass required. Ideally, the tank should be large enough that the boiler can run at least 5-10 minutes to satisfy the thermostat differential.

A buffered heating system is the only way I can think of to truly have one zone per TRV, and it avoids the boiler firing all the time when you only need a few kW of heat.

Reading the thread I understand that you are not interested in making substantial changes like that, as it would cost a few hundred pounds. It was more of a comment really.
 
I do hope this two month old thread isn't too stale for me to contribute to, as I sympathise with Tilerdon's approach to his problem. I too have a home-brewed software control system and have found the extra few degrees of control that this gives me often makes it possible to work around issues using just the basic components already present.

I was wondering if Tilerdon might be able to monitor the temperature of the flow leaving the circulating pump and 'gate' the demand on the boiler firing according to the current amount of heat already flowing through the heat exchanger (which evidently has a significant time-constant) and the differences in setpoint and actual room temperatures. This all depends on the level of access the software has to these parameters. It also means controlling the circulating pump independently of the boiler electrical input as it would need to be operational all the while there was any demand (unlike the boiler).
 
The above is very interesting re buffering etc, yet you have systems like evohome that give very tight control of room temperatures and will fire the boiler continuously if any room is > than something like 1/1.5C below its setpoint and when less than this will cycle the boiler with on times as low as 1 min on and 9 min off, 6 cycles/hour, these settings are settable. Still, cycling the boiler very frequently is the main modus operandi.
I also think that even if the total energy demand is > than the boiler min output that it continues in this fashion, surely the system can summate the individual room HR92 controllers and when > the calculated boiler min output would fire it continuously as a large proportion of heating demand is within the (gas) boiler(s) modulation.

I have a 20kw oil fired boiler with 10 rads, 8 with TRVs and a room stat with another TRVd rad in the same (big) room with a non TRVd rad, the roonstat is set to 22C and all the other TRVs set to maintain 20C downstairs and 16/18C upstairs, this results in the boiler running (cycling as a OF boiler must) ) continuously for the 17 hour heating day and gives excellent control, the only very large room facing south can deviate by ~ 1.5/2 C before correction due to the solar effect as the room has a very large window area, because even though a TRV has a very small hysteresis it is relatively slow in response due to lag time in heating/cooling the liquid/wax filled actuator.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Smart TRV's" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Tilerdon,
Last reply from
John.g,
Replies
14
Views
3,186
Back
Top