Thanks for that, am I right in thinking those figures may relate to
25mm inlet
80mm pump vane?
If so yes that would make sense as old units are 15mm inlet and 60mm vanes
Could you freeze one side and adjust the pipe/ pump valve sages draining down ?
Is the boiler firing or not with that temp of 89.5C?.Upstairs has been running on its own tonight for a couple hours. 2 double rads hot and bathroom tall single hot.
On time = 1.5 mins. Off time= 4 mins 45 secs.
Return temp 43c
View attachment 67200
View attachment 67201
Again on the small upstairs zone I can get all rads warm. But when I balance first 2 correctly the rest fall off cold even with valves fully open.
It's on the larger downstairs circuit that the return temp never rises above 25c even after hours of running.
Is the boiler firing or not with that temp of 89.5C?
I think the max boiler setpoint temp on that boiler is 75C or maybe just 80C max?. Can you ensure that the pump is pumping away from the boiler and what is the power showing there, it looks like 13W? What is the boiler stat set to? there is a 28mm? copper elbow under the boiler stat, is that the vent?.
Thanks, that very high temp of 89C might cause the pump to cavitate and cause circulation problems, might try a SP of ~ 70C for tomorrow and see what the pump power is. Can you see what that power reading was above, looks like 13W to me.
OK thanks again, can see tomorrow what the 70C does, if anything, you will soon know as the boiler dT will decrease if the pump is circulating more.
Presume boiler only ran continuously for 20 minutes or so and then started cycling??.
The impeller on JCs old (alpha/wilo) looks as if it has been in contact with something metallic as it seems a bit chewed up.
What pump setting? and what are boiler flow/return temps as flow rate can be calculated from this.
While its running, pop up to the attic and look for any movement in the F&E tank, hold a "glass" of water with the vent immersed in it and see if any water is being drawn in, also, later, get someone to stop/start the boiler/pump and watch for any pump over or tank surging when the pump starts or stops. IMO 6M on that capacity pump would be more than adequate and 5M would probably fit the bill as well as its so big that it will run like a constant pressure pump on any one of those settings.
What is the Boiler SP.
I have a theory here of what was happening.
The pump was always undersized. However with the old boiler it was just about functional and balancing still wasn't right but "good enough"
New condensing boiler definitely made it lie down dead pressure wise. I believe the new boiler is harder to pump water through the jacket. Maybe due to heat exchanger etc.
Additionally, when the water flow was well down the new boiler was getting up to temp too fast and too high. Also cavitating the pump for good measure. There were times I could hear the boiler boiling the water.
Is the hunter stove in use at times for CH,?
Probably working on gravity circulation as well / helping hand now around 60 won’t work as much so more strain on an undersized pump so I guess your happy now ?