Mitsubishi Ecodan 2011 8.5kw

Hy Guys, I have just installed a second hand ecodan, all seemed to be going well until i noticed that the flow temp doesn't increase much, infact 2 degrees in 40 mins, then the pump shut off with a over temperature warning on the gas side.

I have it piped up to a 300l grant solar cylinder (Indirect).

On first glance I thought it was no circulation but I defiantly have circulation, spent hours making sure.

Inside the ecodan, the gas to the plate exchange pipe gets red hot, the return at the bottom stays cold.

I am using a ftc2. it configured for dhw only at the moment. I have a 5kw ecodan that works perfectly on the same setup.

Any advice would be greatly appreciated.

Thanks in advance

Paul.
 
The solar coil doesn’t have enough surface area you need a min of around 3m2 also have you used 28mm piping and a buffer ?
 
The solar coil doesn’t have enough surface area you need a min of around 3m2 also have you used 28mm piping and a buffer ?
The solar coil doesn’t have enough surface area you need a min of around 3m2 also have you used 28mm piping and a buffer ?
No buffer, I am going to use one eventually but just wanted to test the heat pump as I have 15 days left on my buyer protection. I used 22mm Pipe.
 
No buffer, I am going to use one eventually but just wanted to test the heat pump as I have 15 days left on my buyer protection. I used 22mm Pipe.
It should show a little heat though right? it goes from 17 to 20 degrees after about 45 mins you can hardly tell from feeling the pipe that there is any kind of heat coming from the heat pump.
 
But if the pipework is restricting the heat pump it just won’t heat / only heat up it’s self and cycle a heat pump needs 4 times the amount of flow than a normal boiler does, can you rig it up temp into a container to see if it flows and runs etc ?
 
But if the pipework is restricting the heat pump it just won’t heat / only heat up it’s self and cycle a heat pump needs 4 times the amount of flow than a normal boiler does, can you rig it up temp into a container to see if it flows and runs etc ?
ok, i see. but the 5kw ecodan I have heats up right away. just the 8.5 that doesn't.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Heatpump Hot on Gas Side But Cold On Wet Side?" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
paul_jefferson,
Last reply from
paul_jefferson,
Replies
13
Views
1,467
Back
Top