Old(ish) Grundfos proportional pressure control circulator

View the thread, titled "Old(ish) Grundfos proportional pressure control circulator" which is posted in Central Heating Forum on UK Plumbers Forums.

I'm trying to set up a Honeywell DU145 ABV with an ALPHA 15-60 130 (Model number 59526443) and work out the speed setting. The pump has one variable dial (no C1/2/3 ect).

Grundfos support have no info on the pump as its from circa 2001, so unable to help. Its running 5 rads in a small 2 bed flat with only one TRV turned down (the rest fully open).


Any advice would be welcome
 
Are you trying to set the bypass? Or the pump ?
Both ideally.

The pump is currently set on the max setting, and the ABV on number 2. However, the previous owner admitted to playing around with it. So I though it best to start from the beginning. I dont know why the ABV is there has the loo rad has no TRV, just 2 open lock valves unless the ABV is for the hot water?? Its an S Plan system.
 
S plan system?

Try turning the pump down to half and see if it heats up
S plan: two separate valves. one for heating and the other for water.

I've tried that a week ago, and it was slightly better than full on. The rads warm up more equally on half. I imagine the next step would be to slow it down another 1/4 or keep where it is?
 
Exactly keep notching it down until something stops and notch it up one
Excellent.

Any tips for the ABV setup, or turn the bleeding thing off lol I did have the pump curves that I could have used with the boiler flow to set the ABV, but its difficult with a variable control with no markings to find where the curve is.
 
S plan: two separate valves. one for heating and the other for water.

I've tried that a week ago, and it was slightly better than full on. The rads warm up more equally on half. I imagine the next step would be to slow it down another 1/4 or keep where it is?
I doubt if the pump, with just one control is a proportional pressure (PP) controlled pump, its more than likely a variable speed pump where each pump head is determined by the speed setting, as the pump flow increases the head falls just like the old 3 speed pumps or it may be, even if unlikely, a constant pressure (PP) pump where the pump head remaind constant as the flow increases. Its hard to imagine it giving less head/flow at full setting than say at 1/2 setting, its more than likely a 5M or 6M pump at full speed so a ABV setting of 0.2, 2m, at full speed would/should have resulted in massive bypassing, so do as suggested in post # 10, then maybe shut all rads except the loo rad and open the ABV until it just gets warm the reclose it 1/4 turn or so. Or as you say if loo rad is always on maybe just shut it fully?
 
The following is the only info I have on the pump:

Grundfos ALPHA 15 60 130 (Model number 59526443) Integrated proportional pressure control
GRUNDFOS ALPHA pumps feature automatic control of differential pressure through adjustment of pump performance to actual heat requirement without the need for connection of external components.


With the heating or hot water on, there is always somewhere for the water to be pumped, the issue on S Plan is when both the two port valves shut and the pump overrun is on. Without the ABV open there is no where for the heated water to go.

I'm not sure of the boilers minimum flow as they wont tell me and its not in the manual, so unsure of the pump speed /ABV relationship using the flow / curve charts. Therefore, If I set the pump speed to low, will it cause issues with the boiler. Also, will a lower speed in a PPC pump result in low pressure preventing the ABV to open.

To be honest, the debates I've read about the relationship between 'S Plan / ABV / Modulating Pumps' is on par with my PhD thesis !!!!
 
Last edited:
If the pump is proportional pressure control only then a ABV will only work in the following way.
If you have set your pump (like mine) to a 4.6m PP setting, this means that the pump will circulate ~ 20LPM (1.2m3/hr) at 4.6m and 0 LPM at 2.3M, in other words when you shut off all zone vales then the pump pressure falls to 2.3M.
So you run your boiler to the loo rad only , and slowly open the ABV to just start passing water (maybe then shut it in a touch), when the zone valve closes then the pump head will be 2.3M or very slightly higher at say a required flow of 6.5LPM, 390 LPH) through the ABV at a ~ setting index of 0.23, you open either your HW or CH zone valves and the pump head can rise up to 4M (mine rises to 3.5M with 10 rads), so ay 3.5M, the ABV will now pass ~ 10.8LPM, 650LPH, so useless, in this (PP) case you can just install a gate valve or throttling orifice to give you that 6.5LPM (which should be quite adequate for any boiler on overrun) it will the rise to a max of 8.0LPM at 3.5M which may be acceptable at the expense of a higher boiler return and a bit of efficiency loss.
The above obviously is by passing at all times.
You can do your own interpolating below, mine might be a bit out.


1668187755861.png
 
Last edited:
You could install this normally open 2 port valve as a bypass wired in parallel with the two zone valves which will close when either of the zone valves is signalled to open?.

Honeywell Home V4043B1257 22mm Normally Open 2 Port Motorised Zone Valve​

 
@John.g

I have no point of reference on the pump speed control to accurately set the PP, apart from a ‘dot’ in the middle. Equally, no idea what the minimum boiler flow is to obtain the ABV setting from the curve. However, I like the idea of adding a normally open 2 port valve. That would address the specific issue of both ports are closed and pump overrun on.

Another thought I had was to start the system cold while manually closing both ports to mimic pump overrun, then adjust the ABV until I feel heat on the return.

However, this may all be a moot point as when the heat is satisfied, the boiler and pump switch off, ergo there is no pump overrun. I find this strange has its an S Plan system with an old oil-fired boiler. I’m going to look further into this to establish how the system is configured.
 
"Another thought I had was to start the system cold while manually closing both ports to mimic pump overrun, then adjust the ABV until I feel heat on the return."

That's basically how you do it, it doesn't matter though what the PP setpoint is which you set to satisfy your heating load first, the fact is that the by pass volume will increase when the zone valves open because the pump head increases, this is the opposite to the nomal constant curve ( or the old 3 speed pumps) where the maximum pump head is with the zone valves closed and it then falls with increasing flow so the ABV closes almost as soon as the zone vales open.

Its very normal not to have pump overrun with a oil fired boiler (mine doesn't) as the zone valves open. OF boiler's HX acts as a buffer since it holds 25 to 30 litres of water, which will soak up the residual combustion chamber heat, the hi temp o/limit stat opens at 110/113C which is a long way from the 55C/75C boiler stat SP. I have measured my temp at a max of 90/95C after shutdown with a boiler SP of 70C.
You might also notice how the burner can take up to 5 minutes or so to refire after cycling off, that's because its using up the stored heat in the Hx until the temperature in the top falls to boiler SP-8to10C.
 
"Another thought I had was to start the system cold while manually closing both ports to mimic pump overrun, then adjust the ABV until I feel heat on the return."

That's basically how you do it, it doesn't matter though what the PP setpoint is which you set to satisfy your heating load first, the fact is that the by pass volume will increase when the zone valves open because the pump head increases, this is the opposite to the nomal constant curve ( or the old 3 speed pumps) where the maximum pump head is with the zone valves closed and it then falls with increasing flow so the ABV closes almost as soon as the zone vales open.

Its very normal not to have pump overrun with a oil fired boiler (mine doesn't) as the zone valves open. OF boiler's HX acts as a buffer since it holds 25 to 30 litres of water, which will soak up the residual combustion chamber heat, the hi temp o/limit stat opens at 110/113C which is a long way from the 55C/75C boiler stat SP. I have measured my temp at a max of 90/95C after shutdown with a boiler SP of 70C.
You might also notice how the burner can take up to 5 minutes or so to refire after cycling off, that's because its using up the stored heat in the Hx until the temperature in the top falls to boiler SP-8to10C.


@John.g

I managed to find a basic wiring diagram of the boiler (attached image). It does not look to facilitate a pump overrun. The permanent live appears to supply the boiler with power to enable the frost thermostat.

Thus, my whole thread is no longer valid as I would only require it when both ports were closed. During the call for heat I have one rad fully open that acts as a bypass.

This has saved me some hassle. Regardless, its been an interesting exercise and I have learnt a lot.

Thank you all 😊
 

Attachments

  • ws.png
    ws.png
    18.6 KB · Views: 41

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Old(ish) Grundfos proportional pressure control circulator" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Coddey,
Last reply from
Coddey,
Replies
17
Views
2,819
Back