Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Very high 75,000kw gas consumption - advice?

View the thread, titled "Very high 75,000kw gas consumption - advice?" which is posted in Gas Engineers Forum on UK Plumbers Forums.

Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm. This question is for my own house setup.



We are really fortunate to have a large house, about 5,000sqft in total over 3 floors. It was built around 15 years ago by a reputable company with cavity walls and insulation plus timber double glazing etc. The heat loss is not bad from experience - so aside from peak winter - we can normally hold temperatures of 20 degrees around the house.



The house came with a little known I think 20kw Geminox boiler in the garage and 2 x unvented 200l cylinders from new in the loft. The original boiler kept breaking down plus would prioritise hot water over central heating and then be unable to cope with peak heating loads. However we had to work around the original pipework and circuits plus have not change the cyliners etc.



Around 10 years ago I replaced it with a new Worcester Bosch 40 CDI system boiler (specified by the plumber who does some work for us). Gas was something like 2.5p per kwh and for many years I did not worry about high gas consumption.



Now with gas prices so high it has come to my attention of how high our gas consumption is - it was up to 90,000kwh per annum and recently I've managed to get this down to 75,000kwh but this is still too high.



I've been studying the system and learning from online resources and Youtube videos so sorry for my basic understanding!



This is what I have currently:



Boiler set to flow 65 degrees - connected to Grundfos Alpha pump to vertical low loss header. I experimented increasing flow temperature but see below, I cannot get it to go much higher.



Two x 2 channel Honeywell programmer / timer clocks connected via a relay along with pumps below - so CH, cylinders, UF and towel rails each have a circuit.



From the low loss header we have:



1. Central heating circuit for first and second floors connected to max 12 radiators on two different zones (so 8 and 4 radiators) - controlled by a Nest thermostat and with a Grundfos Alpha pump and zone valve. My calculations suggest this should on peak load be 13-14kwh gas consumption but usually it will be around 8-9kwh.



2. Hot water cylinders x 2, each with a zone valve and connected with a Grundfos Alpha pump plus one zone valve for the circuit. These are connected with a secondary hot water brass circulator pump which is on most of the day (otherwise we lose a lot of water to get hot water). Based on my family usage and the circulator, I'd expect this to use about 30-40kwh of gas per day.



3. Underfloor heating circuit - connected with Grundfos UPS2 25-40/60 130 - zone valve for circuit and then going to two separate manifolds for the downstairs ground floor - each underfloor heated room is zone with actuator heads and room thermostats. The plumber put a JG blending valve from the low loss header flow and u/f return to ensure this circuit does not reach more than 45/50 degrees. The max demand with all circuits open I am guessing is around 19-20kwh but typically lets say 30-40% of that so maybe 8-9kwh.



4. Towel rails - with Grundfos Alpha and simply controlled on and one by the timer clock (use about 4 hours per day to heat bathrooms) - 5 towel rails - this should be 6kwh when open.



I can chart the central heating usage via the Nest app - so in peak winter to achieve around 20 degrees in the house - the circuit is open 8/9 hours. This reduces to 2/3 hours as the weather is above 7/8 degrees.



I cannot control or chart the underfloor usage. Two things I have noticed - throughout the course of the day, one of the underfloor heated rooms will be calling for heat maybe 0.5 degrees - and therefore the underfloor circuit can be on for quite a few hours a day even though it could only be one zone calling for heat. I'm experimenting overriding this with a timer function (so UF can only be on max 15 hours a day lets say). I am also trying to buy some programmable 2 wire battery room thermostats from Heatmiser.



The towel rails I can control using the timer clock.



I cannot tell how much gas the cylinders are actually using or how often the circuit is calling for heat. But if it is getting a max input flow temperature of around 50 degrees (see below) and the tanks are at 55 degrees, I wonder if this is an issue.



Another problem I wonder - using an infrared thermometer when all circuits are on - I feel like all the pump bodies on all circuits are showing a temperature of around 50 degrees (which is what the underfloor blending valve is set at) rather than 60-65 degrees which is the boiler flow. These pumps are within a couple of meters pipework from the boiler and the pipes are insulated plus in the garage, so this level of heat dropoff is confusing. I have copper pipe thermometers on the returns and they show max 40 degrees. It just got me thinking about whether it is possible the blending valve for the UF heating circuit is possibly causing the manifold to not output the true flow temperature of the boiler? So basically I am never getting 60+ degree to any circuit, but actually getting 45/50 degrees.



I've also been playing with all the pump settings to see if I notice any particular issues... but it is hard to decide the optimal CP or PP or set pressure settings for each pump. I think the CH and towel rails should be on set pressure I or II and the CH on CP (even though there are TRVs, they shouldn't be kicking in). The UF seems to work fine on setting 1 or 2.



The boiler is not cycling a lot because I put a wireless thermometer on the return to alert me when the return is above 45 degrees, and this happens rarely. The good thing is it is probably condensing all the time. However I would expect the return to rise higher when only one or two circuits are one (but it rarely does).



So a couple of novice ideas of the problem - maybe someone experienced could guide me :



1. The blending valve of the UF heating circuit is somehow affecting the low loss header to restrict the flow to 45/50 degrees all circuits i.e. UF temperature, instead of sending lets say 60+ degrees to CH, cylinders and towel rails and 45-50 degrees to UF?



2. The boiler modulation of this older boiler means it can do a minimum of 9kw output. If only one or two rooms are calling for UF heat for example, it means for many hours of the day the boiler is doing 9kw because it cannot modulate lower? So I should replace it with a more modern boiler that can modulate down to 3kwh lets say?



3. The boiler is not modulating the flow temperature well enough so it is works at max capacity too often? Recently I have range rated the boiler down to 60% to see what happens... at peak times it means the boiler is working flat out (can tell from my home hub gas consumption it is using 22kwh of gas per hour)... and so far the home is heating up ok... but this means it is going to take more hours to heat up the house (I'm experimenting so don't know the answer yet) so the net result may still be high gas consumption (i.e. more hours at lower output).



Any suggestions, ideas or thoughts would be much appreciated. I would have thought a house of this size and build should ideally not be consuming more than 30,000-40,000kw of gas per annum but maybe I am wrong.
 
Hope you have found and fixed the problem ….
have you a smart meter, that reads gas usage every half hour.
does the Hive give you costs per hour. Think I have seen some graphs on friends system.

when first fired up in the morning there will be high use for a few hours while system heats up.then each half hour there will be less needed as housr is topped up. Then nothing overnight if off.
Could you have a leak somewhere in the hot water pipework?

when my daughter moved in to her house there was no hot water. The boiler fired frequently just to supply hot water leaking out of a pipe, even though there was no central heating needed.
 
Hope you have found and fixed the problem ….
have you a smart meter, that reads gas usage every half hour.
does the Hive give you costs per hour. Think I have seen some graphs on friends system.

when first fired up in the morning there will be high use for a few hours while system heats up.then each half hour there will be less needed as housr is topped up. Then nothing overnight if off.
Could you have a leak somewhere in the hot water pipework?

when my daughter moved in to her house there was no hot water. The boiler fired frequently just to supply hot water leaking out of a pipe, even though there was no central heating needed.
Yep I am using the smart meter to chart the gas usage and check how it is firing. The only thing I cannot monitor is how the hot water demand is turning on and off throughout the day. Thanks
 
Ah! I see it’s a new post. Suppose the heating is using 60000 kwhr a year over winter months. That’s 333 kWh a day. You say that you boiler firing continuously using 22 kwh. Every hour … that’s 15 hours on time daily, which sounds about what you are using. Rads not getting to max temp. can you turn off all the rads and see how the boiler responds?

as it’s a big house have you a continuously pumped hot water loop? I Read you post again and I see you do.

You are using crazy amounts of energy. In a relatively well insulated house. Look at the EPC … that might give anticipated energy use. It cant be going to heat the air in the house, so unfortunately it looks as if you must have a leaking hot water pipe going to one of the taps. It must be Underfloor as was my daughters. We never found the leak as it would mean floor excavation. We were able to re route pipes As an easier solution.

A quick way of seeing if you do have a leak. Try turning off the main cold water stop tap coming into the house. if there is a hot water leak it should depressurise the hot water loop and stop most of the leak. The heat from the boiler will then go to the rads and the temperature will rise. Try turning up the thermostat. You should see a big increase in room temperature rather than it struggling all of the time.

good luck. This could be an insurance job?

I am talking from experience, I have installed heating systems in my own homes. But I am self taught and don’t have qualifications.

let us know how you get on.


. This could be an insurance job?
 
I always start with the simple things. You've probably checked these already but just in case ...

I've come across cases where when an imperial meter (1unit = 100 cu ft) has been converted to a smart meter (1unit = 1 cu metre) but the billing system has not been updated to reflect the change. This results in a billed consumption rate that is about 2.7 times higher than it should be. Take a look at your bill and make sure the one unit (1m^3) is being converted to ca 11 kW hr, which is correct, not ca 32 kW hr, which is wrong but would explain the discrepancy you are looking for.

Next, I'd compare the summer and winter bills to get a handle on how much of the consumption is down to the DHW system. Unless they are extremely well-insulated, and they often aren't, secondary circulation loops can waste a lot of heat while they are running.

A relatively common explanation for mysteriously high gas consumption is a hot water leak that is pouring money (in the form of hot water) down the drain or into the ground 24/7. Power showers and teenagers are another expensive combination.

30,000–40,000 kW hr per year for the house you describe seems about right to me. New builds had to include quite reasonable insulation in 2008.
 
I always start with the simple things. You've probably checked these already but just in case ...

I've come across cases where when an imperial meter (1unit = 100 cu ft) has been converted to a smart meter (1unit = 1 cu metre) but the billing system has not been updated to reflect the change. This results in a billed consumption rate that is about 2.7 times higher than it should be. Take a look at your bill and make sure the one unit (1m^3) is being converted to ca 11 kW hr, which is correct, not ca 32 kW hr, which is wrong but would explain the discrepancy you are looking for.

Next, I'd compare the summer and winter bills to get a handle on how much of the consumption is down to the DHW system. Unless they are extremely well-insulated, and they often aren't, secondary circulation loops can waste a lot of heat while they are running.

A relatively common explanation for mysteriously high gas consumption is a hot water leak that is pouring money (in the form of hot water) down the drain or into the ground 24/7. Power showers and teenagers are another expensive combination.

30,000–40,000 kW hr per year for the house you describe seems about right to me. New builds had to include quite reasonable insulation in 2008.
Thanks for taking the time to put down your thoughts and ideas.

Yes unfortunately the billing is correct! I have checked that and also had the gas meters changed.

I am in the process of monitoring how the usage is changing with the weather.

I'm also trying to work out how I can monitor how often the hot water is calling for heat. Right now I have two ways... I've hooked up a Ring camera positioned on the boiler and manually have to keep an eye on when the hot water cylinders call for heat from the boiler and for how long... this is not a very efficient way though!

I've also bought wireless temperature sensors which I can wrap on the copper pipe, to send me an email alert everything the pipe temperature changes in the hot water loop from the rest temperature (e.g. every time the hot water pipe goes up from 20 degrees to above 40 degrees). In this way I can see how many hours of the day the hot water is waking the boiler up.

I've calculated based on usage / showers / secondary hot water, what my usage should in theory be, and I can then compare how often the boiler is turning on for heating hot water tanks... and somewhat back of the envelope work out whether more gas is being consumed for hot water than expected.
 
Ah! I see it’s a new post. Suppose the heating is using 60000 kwhr a year over winter months. That’s 333 kWh a day. You say that you boiler firing continuously using 22 kwh. Every hour … that’s 15 hours on time daily, which sounds about what you are using. Rads not getting to max temp. can you turn off all the rads and see how the boiler responds?

as it’s a big house have you a continuously pumped hot water loop? I Read you post again and I see you do.

You are using crazy amounts of energy. In a relatively well insulated house. Look at the EPC … that might give anticipated energy use. It cant be going to heat the air in the house, so unfortunately it looks as if you must have a leaking hot water pipe going to one of the taps. It must be Underfloor as was my daughters. We never found the leak as it would mean floor excavation. We were able to re route pipes As an easier solution.

A quick way of seeing if you do have a leak. Try turning off the main cold water stop tap coming into the house. if there is a hot water leak it should depressurise the hot water loop and stop most of the leak. The heat from the boiler will then go to the rads and the temperature will rise. Try turning up the thermostat. You should see a big increase in room temperature rather than it struggling all of the time.

good luck. This could be an insurance job?

I am talking from experience, I have installed heating systems in my own homes. But I am self taught and don’t have qualifications.

let us know how you get on.


. This could be an insurance job?
Thanks for putting down your thoughts.... yes it is madness that I am consuming between 300-400kw a day in peak winter months. I simply cannot understand it.

I will try and see how the boiler responds to changes in the radiator demand - i.e. if only a few of the radiators are calling for heat - does the boiler modulate down from 22kwh usage to lets say the minimum 9kwh. I can do the same with the underfloor heating.

Based on your advice I am trying to monitor how often the cylinders are calling for heat, see my post below. This will give me an indication of whether there could be a leak somewhere, although my instinct (or hope!) is that there isn't.

Thanks again!
 
The Viessmann Vitodens 200W has the sort of modulation (19:1) you require and also has a Legionella cycle so you don't have to continually heat the HW cylinders to 60/65 degC, just set to once a week and the rest of the time say 50 degC. Properly set up and with weather comp should also see a decrease in your gas consumption.

Give Andrew Millward (Watford) a call as he's nearby, he's expert setting up the 200W especially with UFH.

 
Last edited:
I forgot to say, the secondary circulation pump can really leech your hot water resource especially as it's on all the time. I'd investigate some external controls like PIR sensors, pipe stat, or having it on a timer.
 
I forgot to say, the secondary circulation pump can really leech your hot water resource especially as it's on all the time. I'd investigate some external controls like PIR sensors, pipe stat, or having it on a timer.
I have connected the secondary pump to a wifi controlled timer and this has helped to control usage and drawdown based on when its needed. Also have added a solar diverter which is helping to top up the tanks on sunny (not enough!) days. Thanks
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Very high 75,000kw gas consumption - advice?" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
HRP123,
Last reply from
HRP123,
Replies
9
Views
2,246
Back