Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Vaillant boiler taking ages to get to target temperature

View the thread, titled "Vaillant boiler taking ages to get to target temperature" which is posted in Boiler Advice Forum on UK Plumbers Forums.

Thanks for clearing that up, makes sense and adds up.

Well, all we know for sure is that the installed radiator output (T50) is 33.5kw, whether this is actually required at something like -10C or so is unknown except a heat loss was carried out, even if 24kw only is required and the rads are oversized, good, if weather compensation was installed which would give maximum boiler efficiency and even without it, you can manually set the boiler target temperature.
Rads are definitely oversized, the reason was to run a lower flow temp but that hasn’t happened yet….i have family members who really feel the cold (old age). No weather compensation fitted, just running hive units but have been thinking of upgrading controls but not sure which to go for. I’ve seen either Vaillant which seems expensive and can not work out exactly what I require or the other option was nest using open therm module
 
Did you ever actually measure the secondary flow temperature?, if the secondary pump which looks like a UPS3 is on PP2? setting then that can result in a very low actual head which may not have been sufficient for some rads.
 
Did you ever actually measure the secondary flow temperature?, if the secondary pump which looks like a UPS3 is on PP2? setting then that can result in a very low actual head which may not have been sufficient for some rads.
I did at some point but can not remember the value unfortunately. Yes you are correct about the pump model and setting, I took that from the manual that it was recommended to be on PP2 but that was just for 2-pipe system. What would be the ideal setting from your experience?
 
I did at some point but can not remember the value unfortunately. Yes you are correct about the pump model and setting, I took that from the manual that it was recommended to be on PP2 but that was just for 2-pipe system. What would be the ideal setting wfrom your experience?
I've never even seen a LLH but think I have a fair idea of how they work, if you need the secondary flowtemp to be the same as the primary (boiler) flowtemp then the secondary flowrate has to equal to or less than the primary flowrate so a constant pressure or constant curve (speed) may be more appropriate but there's no point in overthinking it, the temperature gauge will give the best advise IMO.
 
I've never even seen a LLH but think I have a fair idea of how they work, if you need the secondary flowtemp to be the same as the primary (boiler) flowtemp then the secondary flowrate has to equal to or less than the primary flowrate so a constant pressure or constant curve (speed) may be more appropriate but there's no point in overthinking it, the temperature gauge will give the best advise IMO.
Thanks John, much appreciated. Once I’ve fitted the LLH and get temp reading I’ll post back
 
You do realise that extra 15 degrees is wasted energy/ warming the return up so not required

Does the boiler pump manage the load eg heats all of the rads etc ?
 
You do realise that extra 15 degrees is wasted energy/ warming the return up so not required

Does the boiler pump manage the load eg heats all of the rads etc ?
Is 60degC the ideal flow temp?

I need to check all rads when just on boiler pump, I had checked earlier downstairs and a few in the 1st floor but not all of them and not the loft rads
 
Well ideally your return needs to be below 50 for condensing boilers to be happy and with sensor mad vaillants this is a must also with your split as it won’t reach max burn / temps unless the split and temp rise is within spec (split is the difference between flow and return ideally 20dc)
 
Well ideally your return needs to be below 50 for condensing boilers to be happy and with sensor mad vaillants this is a must also with your split as it won’t reach max burn / temps unless the split and temp rise is within spec (split is the difference between flow and return ideally 20dc)
Thanks. I’ve turned down flow to 65dC and will see how that goes.

Do you have any thoughts on replacing hive controls with one that can modulate the boiler better and set different flow temps for hw/ch?
 
Thanks. I’ve turned down flow to 65dC and will see how that goes.

Do you have any thoughts on replacing hive controls with one that can modulate the boiler better and set different flow temps for hw/ch?

There brilliant and priority hot water and wc heating but you will have cooler rads then stock temp etc
 
There brilliant and priority hot water and wc heating but you will have cooler rads then stock temp etc
Thanks. Vaillant controls are a bit of a mine field, not sure exactly what I would need? Vr66 wiring centre, weather comp sensor, not sure of which thermostats for both floors and then how to incorporate a vr10 sensor for dhw temp.

Hw priority would be great, can set flow at higher temp for quicker recharge
 
Last edited:
Thanks. Vaillant controls are a bit of a mine field, not sure exactly what I would need? Vr66 wiring centre, weather comp sensor, not sure of which thermostats for both floors and then how to incorporate a vr10 sensor for dhw temp.

Hw priority would be great, can set flow at higher temp for quicker recharge
Are you thinking of not re installing the LLH?.
How are the rads performing now at 65C??, if the return is like the previous 47C then you will be getting reasonable condensing and you may be able to further reduce the target temp. Are you still just running one zone at the time with d.00 set to 20kw or both with d.00 set to 30kw or whatever?.
 
Are you thinking of not re installing the LLH?.
How are the rads performing now at 65C??, if the return is like the previous 47C then you will be getting reasonable condensing and you may be able to further reduce the target temp. Are you still just running one zone at the time with d.00 set to 20kw or both with d.00 set to 30kw or whatever?.
I’m thinking of leaving it for a bit as it is and see how it goes. Rads seem to be performing fine at 65c, don’t want to reduce anymore as cylinder heat up times will need to be increased hence the thought of changing controls for hw priority on a higher flow temp. Still running d.0 at 20kw and single zone at a time
 
Given how much is being being built on the assumption, I'd want to check (using a stopwatch) and the gas meter, that the power the boiler claims to be delivering to the system matches the amount of gas being consumed.
 
Re install LLH.

Move second filter from primary flow to secondary return in to LLH.

Set secondary pump to constant. You want LLH flow in/out to be the same to prevent return water mixing. Can roughly check with temp probes on all LLH connections.

Set boiler to auto, not limited.

Get a vaillant LLH sensor (ntc) and attach to LLH and boiler.

Set to 65c, ensure return is low enough to condensate.

Forget about it and spend your energy somewhere else 🙂.
 
With respect to the Header, from the photos posted, that will probably have a high parasitic flow. I would have expected to see a Header with an oversized primary flow and oversized secondary return.

The term often used is Low Loss Header, the configuration posted gives hydraulic separation, but it is unlikely to be low loss
 
Re install LLH.

Move second filter from primary flow to secondary return in to LLH.

Set secondary pump to constant. You want LLH flow in/out to be the same to prevent return water mixing. Can roughly check with temp probes on all LLH connections.

Set boiler to auto, not limited.

Get a vaillant LLH sensor (ntc) and attach to LLH and boiler.

Set to 65c, ensure return is low enough to condensate.

Forget about it and spend your energy somewhere else 🙂.
Hi

There is no filter on the primary flow, it’s a deaerator - spirotec rv2

For the pump speed do you mean constant speed or pressure?

The LLH sensor, is that the vr10 and does it need to go on primary flow on secondary flow?

Also would moving down to a 24kw boiler be ok?

Thanks in advance
 
Last edited:
With respect to the Header, from the photos posted, that will probably have a high parasitic flow. I would have expected to see a Header with an oversized primary flow and oversized secondary return.

The term often used is Low Loss Header, the configuration posted gives hydraulic separation, but it is unlikely to be low loss
Hi there

The primary and secondary flow & returns are all 28mm up the point where they branch off to the 3 zone valves down to 22mm
 
Hi

There is no filter on the primary flow, it’s a deaerator - spirotec rv2

For the pump speed do you mean constant speed or pressure?

The LLH sensor, is that the vr10 and does it need to go on primary flow on secondary flow?

Also would moving down to a 24kw boiler be ok?

Thanks in advance
NO LLH now?
Can you set d.00 to auto, and put both zones in service until fully heated up, say 30/40 minutes and with the boiler target temp at 75C, then note the flow/return temps, d.40&d.41., that will give useful info, IMO.
 
NO LLH now?
Can you set d.00 to auto, and put both zones in service until fully heated up, say 30/40 minutes and with the boiler target temp at 75C, then note the flow/return temps, d.40&d.41., that will give useful info, IMO.
Hi john

Haven’t got around to refitting LLH yet, but I’ll set to auto and report back temps

I may wait and get rgi to do it as I need to swap boiler out. The reason for the 624 was I’ve got access to a 3yr old one from a friend who’s removed it for a combi
 
I may wait and get rgi to do it as I need to swap boiler out. The reason for the 624 was I’ve got access to a 3yr old one from a friend who’s removed it for a combi
Don't assume, without checking, that a Gas Registered engineer will be willing to install a second-hand customer-supplied combi.
 
Hi john

Haven’t got around to refitting LLH yet, but I’ll set to auto and report back temps

I may wait and get rgi to do it as I need to swap boiler out. The reason for the 624 was I’ve got access to a 3yr old one from a friend who’s removed it for a combi
Can you just do those tests now with no LLH connected, you don't require a RGI, just change d.00 to auto, set target temp to 75c and open the two CH zone valves and then check d.40&d.41 say 15/20 minutes after the target temperature has been met.
 
Can you just do those tests now with no LLH connected, you don't require a RGI, just change d.00 to auto, set target temp to 75c and open the two CH zone valves and then check d.40&d.41 say 15/20 minutes after the target temperature has been met.
Right d.40 is 75 and d.41 is 55

All rads hot apart from loft which saw temps high as 50c flow. Not sure if this is due to height or them being old rads on 8/10mm

The rgi was referred to for changing boiler and getting him to add LLH back in
 
Don't assume, without checking, that a Gas Registered engineer will be willing to install a second-hand customer-supplied combi.
Don't assume, without checking, that a Gas Registered engineer will be willing to install a second-hand customer-supplied combi

Don't assume, without checking, that a Gas Registered engineer will be willing to install a second-hand customer-supplied comb

Don't assume, without checking, that a Gas Registered engineer will be willing to install a second-hand customer-supplied combi.
Hi

Totally agree, it would be the rgi who decommissioned it and they are happy to install. He said if he didn’t decommission it, wouldn’t install it
 
Right d.40 is 75 and d.41 is 55
All rads hot apart from loft which saw temps high as 50c flow. Not sure if this is due to height or them being old rads on 8/10mm

The rgi was referred to for changing boiler and getting him to add LLH back in
At 75C/55C you are getting 29.3kw rad output or 89.2% of your 33.5kw T50 rating, if you were to run at a flow temperature of 65C then you will get a return temperature of 49.4C with 22.81kw rad output or 68.1% of your 33.5kw T50 rating, so a 24kw boiler may be ok especially as you probably won't be running two zones together for very long periods.
 

Official Sponsors of Plumbers Talk