Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

E133 Error Potterton Titanium 24

View the thread, titled "E133 Error Potterton Titanium 24" which is posted in Gas Engineers Forum on UK Plumbers Forums.

abc_plumb

Gas Engineer
Hiya fellow gas engineer.
Need some help on this boiler fault.

Went out to this E133 Error on a Potterton Titanium 24 (GC: 47-393-39)

I checked the inlet standing pressure which was at 25mb. Boiler attempts to fire and the pressure drops by 1mb but the gas valve doesn't open. Checked the black gas lead to the gas valve and I was getting
230v between pins (3L) & E
230v between pins (3L) & (4N)
230v between pins (3L) & (1N)

Checked the gas valve coil and resistance was all good.
Checked X3 on the pcb between 1&2 and getting 230v.
I suspected a sticked gas valve so went there today to replace it with a new one and it's the same fault.

I was told that the pcb was replaced for a reconditioned one 5 weeks ago.

I'm leaning towards the pcb but I'm getting the correct voltage at the black plug end that fits into gas valve???

Would appreciate some help on this please.
 
Hi Shaun

Are you saying I should've tested the gas valve but turning the boiler gas isolation off then tried the firing sequence. From 25mb is should've dropped to 1 or 2mb?
Handy tip for next time.

I did remove the 3/4" nut above the gas valve and I know the gas was not getting through the g/valve.
I'm positive the gas is not getting through, just can't understand why?
 
Hi Shaun

Are you saying I should've tested the gas valve but turning the boiler gas isolation off then tried the firing sequence. From 25mb is should've dropped to 1 or 2mb?
Handy tip for next time.

I did remove the 3/4" nut above the gas valve and I know the gas was not getting through the g/valve.
I'm positive the gas is not getting through, just can't understand why?

Yes proves if the gas valve is opening

If you have power eg 240v on the pins and no drop gas valve (eg with supply isolated)
 
I've put a brand new gas valve yesterday and I'm getting the same fault. I'm thinking the gas plug is not making the contact with the pins to transfer the 230v to the gas valve.

Feel like my clutching at straws, but can't get my head around this one!
 
I've put a brand new gas valve yesterday and I'm getting the same fault. I'm thinking the gas plug is not making the contact with the pins to transfer the 230v to the gas valve.

Feel like my clutching at straws, but can't get my head around this one!

Lift the plug slightly so you can check at the terminals
 
Lifted it, wobbled it, squeezed it..... done it all, but nothing.

I mean you can test with a multi meter on the gas valve pins to see if the connection is ok just a thought as well did you remove the bung on the new gas valve they sometimes put them in to save any rubbish going in them while in the box
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "E133 Error Potterton Titanium 24" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
abc_plumb,
Last reply from
ShaunCorbs,
Replies
9
Views
1,164
Back
Top