Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

g60rge

Gas Engineer
Feb 21, 2012
94
15
8
hi, im working towards my acs and have a query,

if im checking safety devices on a gas hob/cooker,

letby/tightness

lid shut off

check controls are working and not letting by or stiff/loose

check stability device/hose connections etc

i check the fsd by lighting the oven and watching it light on low flame, once the phial has heated up it allows the main burner to light (30 secs). Shut the gas off, wait for the click (time it) turn back on, should start off on low flame again.

check the flame returns to bypass after temp is satisfied

check the seals with a sheet of paper

now ive found nothing in my notes to suggest checking ffd shut off on hobs and cookers and doing the tightness test to ensure gas isnt being passed to the burners which worries me.

thinking about it, if the gas supply was interrupted and then reinstated, but the ffd shut the gas off, how is the appliance reset? as ive never seen one with a reset button. if they dont, then what happens?

thanks in advance
 
"i check the fsd by lighting the oven and watching it light on low flame, once the phial has heated up it allows the main burner to light (30 secs). Shut the gas off, wait for the click (time it) turn back on, should start off on low flame again."

there will be no click on an oven vapor pressure fsd, after your 30 sec you just turn gas off and wait 90 sec max then relight, it should then light on low flame
 
i did realise that but the college will probably have old appliances in there.

any advice what i should do in my acs exams if the mi's dont say if it has one or not?
 
to check cooker lids light the cooker burners and lower the lid, gas should turn off
 
"i check the fsd by lighting the oven and watching it light on low flame, once the phial has heated up it allows the main burner to light (30 secs). Shut the gas off, wait for the click (time it) turn back on, should start off on low flame again."

there will be no click on an oven vapor pressure fsd, after your 30 sec you just turn gas off and wait 90 sec max then relight, it should then light on low flame

ahh i see, thats all i need to check then, other than the other stuff i mentioned, thats good.

how about the hob? all i remeber doing at college and with the engineer i was with on my portfolio (whom i dont like bugging too often which is why im here) is check the controls are working correctly and the flame looks good.
 
ahh i see, thats all i need to check then, other than the other stuff i mentioned, thats good.

how about the hob? all i remeber doing at college and with the engineer i was with on my portfolio (whom i dont like bugging too often which is why im here) is check the controls are working correctly and the flame looks good.

if it doesnt have a lid or fsd's on the hob the yes
 
if it doesnt have a lid or fsd's on the hob the yes

thats great, this website really is proving helpfull..

last q
if the mi's dont mention the fsd, or on the tools there are no mi's, what would be the sign that the hob has an fsd?
 
thats great, this website really is proving helpfull..

last q
if the mi's dont mention the fsd, or on the tools there are no mi's, what would be the sign that the hob has an fsd?
each burner will have it pointing into flame, you will see them
 
there will be thermo-couple, do not confuse it with ignitor.
You can light one of the burners and blow it. FSD should shut the gas within 60 sec max.
You can put your hand on the cooker and feel when FSD does work
 
Last edited by a moderator:
there will be thermo-couple, do not confuse it with ignitor.
You can light one of the burners and blow it. FSD should shut the gas within 60 sec max

Allowing gas to escape In to amtosphere. That's not very good lol

I know what you mean thou. Should just wait for allowed time and turn back on. No gas. Pass!
 
hang on,

flame is lit on hob
i cut off the gas
after 60 secs it click shut
i turn gas back on and do a tightness test to check it has shut off and not passing gas to the burner - it passes
gas control is still on
how does it then go back to normal ie gas is allowed back in - is it when the control has returned to the off position?
 
Last edited:
  • Like
Reactions: 1 person
hang on,

flame is lit on hob
i cut off the gas
after 60 secs it click shut
i turn gas back on and do a tightness test to check it has shut off and not passing gas to the burner - it passes
gas control is still on
how does it then go back to normal ie gas is allowed back in - is it when the control has returned to the off position?[/QUOTE]
no just press down on control knob and relight burner,doesnt matter what position , flame touches t/couple again and stays lit
 
Just to change the subject because this thread is so fresh and im doing my acs too,
When purging existing pipework say after a service or something do you have to work out a purge volume to purge it or can you just purge 0.01 m3 of gas through. I understand that you have to work out purge volumes to check its within your limits.
 
there will be thermo-couple, do not confuse it with ignitor.
You can light one of the burners and blow it. FSD should shut the gas within 60 sec max.
You can put your hand on the cooker and feel when FSD does work

ah i see the fsd in a hob is a thermoelectric valve
 
  • Like
Reactions: 1 person
hang on,

flame is lit on hob
i cut off the gas
after 60 secs it click shut
i turn gas back on and do a tightness test to check it has shut off and not passing gas to the burner - it passes
gas control is still on
how does it then go back to normal ie gas is allowed back in - is it when the control has returned to the off position?[/QUOTE]
no just press down on control knob and relight burner,doesnt matter what position , flame touches t/couple again and stays lit

just like on the fire place.

im so happy right now thanks every1
 
  • Like
Reactions: 1 person
Just to change the subject because this thread is so fresh and im doing my acs too,
When purging existing pipework say after a service or something do you have to work out a purge volume to purge it or can you just purge 0.01 m3 of gas through. I understand that you have to work out purge volumes to check its within your limits.

if the gas pipe has been opened, i would do a purge calculation and follow the correct procedure to remove explosive mixtures!
 
if the gas pipe has been opened, i would do a purge calculation and follow the correct procedure to remove explosive mixtures!

But what if you cant see the pipe work and you dont know how many fittings or how much 22mm pipe runs though the ceiling? Are you only doing purge volume caculations to check if you are allowed to purge it with out igniting. I am confused. Alot of the time you can see the pipework and you cant go ripping floor boards up.
 
Just to change the subject because this thread is so fresh and im doing my acs too,
When purging existing pipework say after a service or something do you have to work out a purge volume to purge it or can you just purge 0.01 m3 of gas through. I understand that you have to work out purge volumes to check its within your limits.
You have to purge installation if you had pipework open. If you did work on the boiler with isolation valve closed than no need to purge.
 
You have to purge installation if you had pipework open. If you did work on the boiler with isolation valve closed than no need to purge.
Yeah sorry mate i know this but what if for instance i have cut the pipe work and have to purge but cant see the pipe work to get the IV.
 
well if installation is up to 28mm it would be 0.01m3

So why do you need to work out a purge volume ?
I mean cant you just purge 0.01m3 through everytime if the pipe work is not greater that 28mm. Dont forget im doing my acs soon and need explanation.
 
So why do you need to work out a purge volume ?
I mean cant you just purge 0.01m3 through everytime if the pipe work is not greater that 28mm. Dont forget im doing my acs soon and need explanation.
Correct. The standard purge volume for a G4/U6 meter with 28mm pipe is 0.01m³ as Syty states.
Only if bigger meter or greater than 28mm pipe does this change.
 
  • Like
Reactions: 1 person
Just to change the subject because this thread is so fresh and im doing my acs too,
When purging existing pipework say after a service or something do you have to work out a purge volume to purge it or can you just purge 0.01 m3 of gas through. I understand that you have to work out purge volumes to check its within your limits.

check your notes and get your head round this you seem to be mixing a couple of things up
depending on meter and/or pipe size you only need to purge 0.01m3, if above 28mm or U16 meter there is a calculation to do, but a purge calculation isnt done to see if it is within limints of your work scope, the calculation is to work out how much gas to purge and whether you purge to air with no ignition or constant ignition
the calculation to decide whether you cvan work on it is IV (Installation Volume) and if over 0.035m3 isnt domestic
 
if the gas pipe has been opened, i would do a purge calculation and follow the correct procedure to remove explosive mixtures!


i wouldnt do a purge calculation until i had done a visual inspection to see what meter and pipes were fitted, as you dont need to calculate every install
 
But what if you cant see the pipe work and you dont know how many fittings or how much 22mm pipe runs though the ceiling? Are you only doing purge volume caculations to check if you are allowed to purge it with out igniting. I am confused. Alot of the time you can see the pipework and you cant go ripping floor boards up.

you never need to know how many fittings are on an install to work out purge volume, its down to meter and/or pipe size, if you cant see all the pipework you need to work on a best endeavour, say 28mm pipe disappears under the floor and 8m away 22mm pipe appears up as you dont know where it drops down simply take it as 28mm all the way, the reality is it wont make much difference, remember we are nearly talking about IV and PV in the same thread, max IV for domestic ticket is 0.035m3 (approx 90m x 22mm pipe with an E6 meter, so you will never go over in a domestic as you wont get any gas out of the pipe if the appliance is 90m away from the meter, if there is any 35mm pipe or a U16 meter you need to work out IV before you start, (o.035m3 max for domestic) if you can work on it you need to work out PV so you need PV of the meter and then calculate pipe lengths (again if you cant see all the pipe or where it reduces assume larger size) once you add up all the pipe volumes, add 10% for fittings (thats why you dont need to know how many there are) then multiply answer by 1.5 lastly add PV of meter, if under 0.02m3 purge to vented area, if over 0.02m3 you need to light it as soon as you start purging
 
  • Like
Reactions: 1 person
So, on a U6 meter, you have to purge times the badge capacity which is 0.355 and this has to be burned. Do you just use a lighter at the hob? As you are not able to use electricity?
 
So when you guys say turn the gas off and wait for the click, do you mean just turn the gas off on the tap? Not like on the isolation valve like any other appliance? Am sure you wouldnt disconnect it from the bayonet fitting. Or would you?
 
ok, I have looked in my Viper and gas book and it says that for a U6 meter with 28mm pipe, you purge 0.01m3. And you do not need to light it. Which on the dial, is just between increment 3 and 4. But, if on my acs assessment, i lit the gas at the cooker, would it be allowed? As, it is recommended to in both my viper and Corgi to light. If so, what do i use to light it? A lighter or bit of paper?

Thanks for all the help guys
 
you never need to know how many fittings are on an install to work out purge volume, its down to meter and/or pipe size, if you cant see all the pipework you need to work on a best endeavour, say 28mm pipe disappears under the floor and 8m away 22mm pipe appears up as you dont know where it drops down simply take it as 28mm all the way, the reality is it wont make much difference, remember we are nearly talking about IV and PV in the same thread, max IV for domestic ticket is 0.035m3 (approx 90m x 22mm pipe with an E6 meter, so you will never go over in a domestic as you wont get any gas out of the pipe if the appliance is 90m away from the meter, if there is any 35mm pipe or a U16 meter you need to work out IV before you start, (o.035m3 max for domestic) if you can work on it you need to work out PV so you need PV of the meter and then calculate pipe lengths (again if you cant see all the pipe or where it reduces assume larger size) once you add up all the pipe volumes, add 10% for fittings (thats why you dont need to know how many there are) then multiply answer by 1.5 lastly add PV of meter, if under 0.02m3 purge to vented area, if over 0.02m3 you need to light it as soon as you start purging

Thanks pal thats cleared it up for me.
 
out of all the things in gas /acs ect this is the one thing that scares me the most just carnt get my head round the amount of gas that comes out by doing it by the book ive done it that way and it took ages to clear an was scared incase anyone came in and switched something on or the fridge fired up or the fone went ect as you carnt turn everything off in a house especaily a freezer full of frozen food, had this discusion on here loads of times, i understand why they do it but dont agree with it, if you smell the slightest amount of gas wen in a house transco tell you to turn the gas off and open all doors windows etc so why is it ok to let that amount of gas into a room i still use my sniffer on my anton till it goes to high to purge i no thats not the "correct"way but just carnt do it the other way
 
out of all the things in gas /acs ect this is the one thing that scares me the most just carnt get my head round the amount of gas that comes out by doing it by the book ive done it that way and it took ages to clear an was scared incase anyone came in and switched something on or the fridge fired up or the fone went ect as you carnt turn everything off in a house especaily a freezer full of frozen food, had this discusion on here loads of times, i understand why they do it but dont agree with it, if you smell the slightest amount of gas wen in a house transco tell you to turn the gas off and open all doors windows etc so why is it ok to let that amount of gas into a room i still use my sniffer on my anton till it goes to high to purge i no thats not the "correct"way but just carnt do it the other way

why are you scared? you are purging to ventilated area and the gas cant explode till it is between 5-15% volume, you are only purging 0.01m3 gas so if 0.01m3 is 5-15% of the room volume and likely to explode what size will the room be? and that would also mean you had shut the window to stop the gas escaping, on a hob or cooker, 20-30 secs will purge the correct volume it just isnt going to be a problem,
 
out of all the things in gas /acs ect this is the one thing that scares me the most just carnt get my head round the amount of gas that comes out by doing it by the book ive done it that way and it took ages to clear an was scared incase anyone came in and switched something on or the fridge fired up or the fone went ect as you carnt turn everything off in a house especaily a freezer full of frozen food, had this discusion on here loads of times, i understand why they do it but dont agree with it, if you smell the slightest amount of gas wen in a house transco tell you to turn the gas off and open all doors windows etc so why is it ok to let that amount of gas into a room i still use my sniffer on my anton till it goes to high to purge i no thats not the "correct"way but just carnt do it the other way

If you 'carnt' be doing the purging by the book and if you 'carnt'
be doing it the "correct" way I would wonder if you are competent
to be doing gas work at all.

Are you registered with Gas Safe Register as a GSR installer?
 
why are you scared? you are purging to ventilated area and the gas cant explode till it is between 5-15% volume, you are only purging 0.01m3 gas so if 0.01m3 is 5-15% of the room volume and likely to explode what size will the room be? and that would also mean you had shut the window to stop the gas escaping, on a hob or cooker, 20-30 secs will purge the correct volume it just isnt going to be a problem,

get all that kirkgas mate dont disagree and dont no why, it just does, 20 or 30 secs i do that anyway no loads of gas safe people and dont no anyone who purges by the book all say the same as me
 
If you 'carnt' be doing the purging by the book and if you 'carnt'
be doing it the "correct" way I would wonder if you are competent
to be doing gas work at all.

Are you registered with Gas Safe Register as a GSR installer?

whats with the big writing,am not even going to reply to this read my post properly
 
get all that kirkgas mate dont disagree and dont no why, it just does, 20 or 30 secs i do that anyway no loads of gas safe people and dont no anyone who purges by the book all say the same as me


i take your point its all about being comfortable with what you do, BUT if you dont purge the correct volume and an old cooker with no FSD's goes out due to an airlock then the unburnt gas fires back through when nobody is in the kitchen, to me is far more dangerous than purging 0.01m3 with the window open, TBH i have never ever considered it anything other than safe to do, when you consider some of the things we do at work anyway!!!!!!!!!!!!!!!!!!!!!!!!!!!
who has seen the supplier snatching an ecv and his mate catching the gas from the open end into a black bin bag then taking it outside, haha superb, "you're no in college noo wee man"
or the guy moving the meter from inside to outside cutting the live supply and plugging with denso till he is ready to snatch on the transitional fitting to connect the new plastic supply, the only H&S they use is the guy outside the track having a spare hacksaw ready to chuck into to him if the blade on the first one breaks, and the guy with the spare hacksaw is usually smoking a ***
 
  • Like
Reactions: 1 person
i take your point its all about being comfortable with what you do, BUT if you dont purge the correct volume and an old cooker with no FSD's goes out due to an airlock then the unburnt gas fires back through when nobody is in the kitchen, to me is far more dangerous than purging 0.01m3 with the window open, TBH i have never ever considered it anything other than safe to do, when you consider some of the things we do at work anyway!!!!!!!!!!!!!!!!!!!!!!!!!!!
who has seen the supplier snatching an ecv and his mate catching the gas from the open end into a black bin bag then taking it outside, haha superb, "you're no in college noo wee man"
or the guy moving the meter from inside to outside cutting the live supply and plugging with denso till he is ready to snatch on the transitional fitting to connect the new plastic supply, the only H&S they use is the guy outside the track having a spare hacksaw ready to chuck into to him if the blade on the first one breaks, and the guy with the spare hacksaw is usually smoking a ***

yep mate youre the instructor so to speak so your right and dont disagree with anything you have said or put and ive done it loads of times by 10 times the badge volume on the meter i ye no what i mean ,i do lol but all i was sayin is i use my gas leak sniffer on my anton till it goes to high beeping and high on the scale and then light and stay there for 10 mins and keep checkin it usually leave it on for 5 mins so i dont ever have a situation were it could go out as youve discribed cos i dont walk away till its been on a while
 
If the hose connection leak is on a threaded supply connection, consider turning off the water and dismantle the leaking joint. You must also check the olive for damage and that should help you tackle leaks with hose connections.
 
These fsds on each burner are thermocouples just like you see on fires and boilers and work the same way,heat up to allow gas on ,cool down to shut gas off.
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.