jase158

Been to 2 radiator jobs this week and both were Vaillant boilers, both customers requested that boiler was filled to 1.8/ 1.9 bar.

one of the boilers come up with F75 code until I put pressure up.

Any ideas why Vaillant boilers are 1.8 bar when other boilers are 1 bar please?
 
i remembre some one saying here is that they have a problem with pressure sensor , and if pressure drops below 1.5bar F75 comees up
 
Pressure should be set to 1 bar as normal, I don't know where you got 1.5 from

Customer asked you to fill to 1.5?

Just checked manual. 1 - 2 bar

I would have thought, unless you were struggling to get up to top rads, 1 bar would be preferable to allow for more expansion.

Still could be wrong
 
Last edited by a moderator:
As far as I am aware, most of the vaillants I have worked on anyway, are no different to the norm and I normally go the the usual 1.5 bar. Round about middle of grey area on dial.
If you are getting the F75 fault when just bellow the 1.5 bar the pressure sensor is faulty.

The sensors are very sensitive to dirt and have replaced a few on newish boilers.

Would recommend a magnafilter or the like on any new vaillants.
 
As far as I am aware, most of the vaillants I have worked on anyway, are no different to the norm and I normally go the the usual 1.5 bar. Round about middle of grey area on dial.
If you are getting the F75 fault when just bellow the 1.5 bar the pressure sensor is faulty.

The sensors are very sensitive to dirt and have replaced a few on newish boilers.

Would recommend a magnafilter or the like on any new vaillants.
its a common fault due to the position of the switch on the pipework esp in boilers fitted in lofts .
change the switch and i would recommend changing to solid copper pipes as the rubber sections have proved to be places for dirt to build up and can split.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Vaillant boilers" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
jase158,
Last reply from
glenno1,
Replies
8
Views
3,184
Back
Top