D

Danv44444

Hi Guys,

I went to service a Worcester Greenstar 37cdi combi boiler for a customer today and I checked the inlet pressure on the boiler whilst running in chimney sweep mode. The Inlet pressure was only 15mb and I checked the mi's and it says the boiler should'nt be commissioned if the pressure is less that 18mb. The boiler seems to be working fine and the anaylser readings are ok but I have capped of the gas supply to the boiler for now as im not sure how to catergorise it? Is it At Risk? Are the in any danger if they continue to use it? There is a 22mm gas supply to the boiler probably about 16m with bends etc included.The property is empty at the moment and the customer wants to let it out. Any ideas guys, is the only answer to install 28mm gas pipe?

Thanks Guys
 
They'll work down to just below 14 I think but it's NTCS if it's working ok I believe.

They need a lot of gas, try to get as much upgraded to 28mm from the meter as possible.

Any other appliances between meter and the boiler?
 
If it is not affecting the operation of the boiler i.e fga reading ok, gas rate ok then it is NCS. Make sure it isnt affecting any other appliances like a hob without a fsd or a gas fire.
 
  • Like
Reactions: 2 people
Thanks very much for your responses guys. The trouble is the gas supply comes straight off the meter and goes in side the wall somewhere? The also have a decorative gas fire in the front room. I tried running that full rate and the boiler full rate and it still works fine.
I was wondering if it was safe to use because it might not burn correctly? but the fga says its all ok and its a room sealed appliance. I am reasonable new to gas work and I just wasnt sure so i am just wondering if you guys have come across this before.
 
If its ok at full rate with the fire on max then just make a NTCS note on the certificate.

Especially as your FGA is saying the same, input rating just to go belt and braces but it's not in common when people upgrade boilers with little regard for a good job.
 
with the two appliances working at full rate did you check the burner pressure at the fire?
as already asked what was the working pressure at the meter?
if that was low you need to call out national grid
 
Reference TB 115 & GIUSP.

If low IP is not affecting gas rate and FGA readings then as mentioned it only NCS.
 
I havent checked the pressures at the meter or the fire but i will when I go back to re connect the boiler. If the are both ok and I do a ncs ticket will that be ok?
 