How can high pressure steam be produced when the tap is open

bit of water left in the pipework (clutching at straws here 🙂 ), but the main issue is you could fairly easily cause damage when there no need to if you dont use the boiler, why risk it??
 
but you just hit the nail on the head there, mains is off as the tap is leaking so its not at mains pressure, so water can boil at 100 deg c and lack of water can let it boil, produce steam which can be quite high pressure which can also damage the o rings and cause leaks. Hence why all low water content boiler have overrun to cool the hex to prevent hot spots etc cooking them. So the only one spouting rubbish is milsy
the ch side is still full of water and will dissipate the latent heat in the hex
 
would any of the leave it its ok, who have a ferrolli like this at home, pop out and set it up to see what happens in this situ and let us know pse
 
its safe to leave the heating running even with no mains feed it will only fier for heating and the water flow keeps the hex at normal temps and pump will over run to dissipate het when boiler goes of
 
There is no way that the boiler firing up for heating is going to cause any damage to the heat exchanger because the DHW side is empty The pump will run and this will take the heat out of the boiler. Yes there is still going to be water in the DHW side but at zero pressure it will not build up so drastically that it is going to cause damage to the heat ex. As for the OH stat it will also cut the boiler out on the DHW side of things as well as the heating it is a safety feature that will shut the boiler off when heat exchanger gets to a set temperature. It will not do any thing to the potentiometer as every OH stat I have ever come across in the 14 years I have worked in this trade work the same they go from closed to open circuit.

I have left many peoples heating running in the past whilst I have had the water off changing taps etc and surprise surprise I have never killed anybodys heat exchanger. I would suggest Lame plumber that you do not comment on things you are 100% sure of as in this case you are definately sprouting rubbish.
 
we can all have an opinion, but there's no need to be rude, after all forums are for discussion and everyone has had different experience of boilers and problems and because of issues I have had, esp with a ferrolli in the past I offered my opinion such that the bloke posting a query could make a choice. Like I said, I've experienced a ferrolli doing just this when I failed to bleed a pump thro recently, it only wrecked a couple of o rings but when chris from ferrolli turned up, he was decent enough to point out loads of his work involves repairing boilers where the hex is boiled and o rings blown and flow valves melted, and with that damage pcbs etc knackered. This is being done regularly on new installs so there is the potential to do the same with this boiler if your luck runs out so why risk it. So as you tried to say, you shouldnt comment on things you are not 100% sure of, but in this case I'm 98% sure so I think I can offer an opinion without being told I'm sprouting, sorry spouting a lot of rubbish. If you want to comment, please feel free, its an open forum but dont get arsy as its not really needed. After all the guy only wants an opinion to make his choice! be it yours or mine or someone elses
 
There is no way that the boiler firing up for heating is going to cause any damage to the heat exchanger because the DHW side is empty The pump will run and this will take the heat out of the boiler. Yes there is still going to be water in the DHW side but at zero pressure it will not build up so drastically that it is going to cause damage to the heat ex. As for the OH stat it will also cut the boiler out on the DHW side of things as well as the heating it is a safety feature that will shut the boiler off when heat exchanger gets to a set temperature. It will not do any thing to the potentiometer as every OH stat I have ever come across in the 14 years I have worked in this trade work the same they go from closed to open circuit.

I have left many peoples heating running in the past whilst I have had the water off changing taps etc and surprise surprise I have never killed anybodys heat exchanger. I would suggest Lame plumber that you do not comment on things you are 100% sure of as in this case you are definately sprouting rubbish.
sorry but your wrong,end of argument,as said this boiler has a twin pass heat exchanger,there is a risk that remnants of water left in the domestic side can cause issues if the ch is used,now who has the balls to argue differently with me about boiler design??? i am not taking anyones side but this is FACT
 
we can all have an opinion, but there's no need to be rude, after all forums are for discussion and everyone has had different experience of boilers and problems and because of issues I have had, esp with a ferrolli in the past I offered my opinion such that the bloke posting a query could make a choice. Like I said, I've experienced a ferrolli doing just this when I failed to bleed a pump thro recently, it only wrecked a couple of o rings but when chris from ferrolli turned up, he was decent enough to point out loads of his work involves repairing boilers where the hex is boiled and o rings blown and flow valves melted, and with that damage pcbs etc knackered. This is being done regularly on new installs so there is the potential to do the same with this boiler if your luck runs out so why risk it. So as you tried to say, you shouldnt comment on things you are not 100% sure of, but in this case I'm 98% sure so I think I can offer an opinion without being told I'm sprouting, sorry spouting a lot of rubbish. If you want to comment, please feel free, its an open forum but dont get arsy as its not really needed. After all the guy only wants an opinion to make his choice! be it yours or mine or someone elses
nothing to do with the dhw side then ??
 
sorry but your wrong,end of argument,as said this boiler has a twin pass heat exchanger,there is a risk that remnants of water left in the domestic side can cause issues if the ch is used,now who has the balls to argue differently with me about boiler design??? i am not taking anyones side but this is FACT
how and why ?
 
Ok, so whats the difference between this and the heat exchanger on the DHW side being full as you would find in normal operating circumstances? So for example, the heating has been on all night and no one has run the tap. Late at night the tap is run. The water in the DHW side does not get anywhere near boiling point otherwise it would be lethal as it comes out the tap (the volume of water contained within the heat exchanger all night)

The reason is because the heating side is dissapating the heat, which is exactly the reason why the heat exchangers are joined. If there were 2 completely seperate heat exchangers being primarily and directly heated by the burner then this would occur. Remember this is a heat exchanger and its primary purpose id to be able to transfer heat efficiently. Having a twin pass means the 2 act like a big heat sink to one another.

The reason (in my opinion) lame plumber, you had said problem is because you had no flow in either DHW or heating, therefore no way of dissipating that heat, the boiler cannot react quick enough to shut down so the static water boils (or as near as)
 
Last edited:
how and why ?
the domestic circuit runs through but not in direct contact with the primary circuit(ch) the hex is a direct heat design,as apposed to the plate heat set up that is a indirect heat design,take a polystyrene cup,put a tiny amount of water in it and place your gas lamp on full and torch the bottom,you then get some idea of what your doing to a twin pass heat exchanger when running it in heating mode with no water in the secondary (dhw) circuit only in this cup the water quickly evaporates and the cup melts,in a boiler the small amount of water turns to steam melting o rings,the plastic gubbins of the flow switch,and very quickly the copper tubes within the heat exchanger
 
the domestic circuit runs through but not in direct contact with the primary circuit(ch) the hex is a direct heat design,as apposed to the plate heat set up that is a indirect heat design,take a polystyrene cup,put a tiny amount of water in it and place your gas lamp on full and torch the bottom,you then get some idea of what your doing to a twin pass heat exchanger when running it in heating mode with no water in the secondary (dhw) circuit only in this cup the water quickly evaporates and the cup melts,in a boiler the small amount of water turns to steam melting o rings,the plastic gubbins of the flow switch,and very quickly the copper tubes within the heat exchanger
Still don't understand the above ?

Long & short of it is - do we think that a boiler manufacturer (even Ferroli) would design a combi boiler that if the mains water supply was interrupted due to say, water board turning off or a burst pipe, when the heating was on & it would cause damage or failure of heat exchanger ? I don't think so ! I can just see the claims rolling in now, Although not an every day occurrence common enough for the industry to hear about it.
 
Lets get this straight, has anyone checked the MI's? I have. This boiler does not have a seperate plate heat exchanger. Its heat exchangers HTG + DHW are both located above an atmospheric burner. So when it calls for HTG it also heats the DHW side regardless of DHW demand. So if the DHW side become empty through evaporation because the water is turned off then the consequences could cause damage.

Agree with everyone if it had a seperate plate heat exchanger heated from the main HTG heat exchanger through a diverter valve. Which is the normal for all your Vaillants, Worchesters ect, but not for an old ferrolli Modena.

Also agree that the overheat would probably protect it. but would not rely on it as thats your last line of safety device.
 
Last edited:
I am with Dancing. Lets think what can happen:
This boiler would be designed in a way that the water in the HW heatex pipe could get overheated (significantly past 90odd degC) at any situation. The user would open the HW tap, the pressure would drop, the water in the heatex would turn in milliseconds into steam at the usual expansion rate. Lets say the tap is just near the boiler.
1st: the customer could loose his hearing because of gases leaving at above 1bar.
2nd: the customer can suffer severe steam burns.
3rd: the boiler internals might not cope with the rapid pressure increase and the customer gets hit by boiler(parts).

Next thought: How much water is in the HW heatex and how long would that take to superheat at 30kW input. Lets say there would be demand for half an hour. We assume the HW would be functional but not in use. What temperatures do you expect?

I would say this boiler is safe to use without HW. If not then you have to expect it to be unsafe with HW working too.
 
Last edited by a moderator:
Lets get this straight, has anyone checked the MI's? I have. This boiler does not have a seperate plate heat exchanger. Its heat exchangers HTG + DHW are both located above an atmospheric burner. So when it calls for HTG it also heats the DHW side regardless of DHW demand. So if the DHW side become empty through evaporation because the water is turned off then the consequences could cause damage.

Agree with everyone if it had a seperate plate heat exchanger heated from the main HTG heat exchanger through a diverter valve. Which is the normal for all your Vaillants, Worchesters ect, but not for an old ferrolli Modena.

Also agree that the overheat would probably protect it. but would not rely on it as thats your last line of safety device.
i have and here they are for your perusal

http://www.ferroli.co.uk/wp-content/uploads/brochures/archives/Ferroli F30 B Manual.pdf
 

I have the mi's already and have checked it out, as I said in my previous post.

Anyway its only a problem if the DHW side dries up. so as long as there is water in it no problem.

If this faulty tap is below the boiler do you think it will dry out. So waters off tap is on, even if its above the boiler, what if they turn on the kitchen ho****er tap which is likely to be below the boiler. It will drain the heat exchanger just above the gas burner which is happly burning away because the heatings turned on.
 
I have the mi's already and have checked it out, as I said in my previous post.

Anyway its only a problem if the DHW side dries up. so as long as there is water in it no problem.

If this faulty tap is below the boiler do you think it will dry out. So waters off tap is on, even if its above the boiler, what if they turn on the kitchen ho****er tap which is likely to be below the boiler. It will drain the heat exchanger just above the gas burner which is happly burning away because the heatings turned on.

I had thought it is understood that the HW pipe has to be designed in a way that it does not reach temperatures above boiling point under any circumstances?
 
If you take a close look at the hydraulic circuit it becomes evident that the DHW heat exchanger is (wet) on the primary circuit and therefore, as long as the pump is working (and it will when CH is working) it won't reach any temperature above the flow temperature, consequently nothing will melt or overheating. When there is a demand for DHW the electronics after evaluating the flow sensor signal will stop the pump and the full power of the boiler will heat up the primary cooled down by the secondary with running cold water.
conclusion: from the design of it Dancinplumba is 100% correct.
 
The frost protection will not work if the electricity and/or gas supply to the unit are cut off.
To avoid damage caused by freezing during long shutdowns in winter, it is advisable to drain allwater from the boiler, the tap water and the system water; or drain off just the tap water andadd a suitable antifreeze to the heating system, as prescribed in chap. 2.3.

Above is from page 6 (1.4), now even Ferroli would not put it in print if there was any chance of it recking their boilers now would they.




 
I love it when Chris joins in as he seems to find these little one liners from nowhere that supply a definitive answer in hard format.

Right, so now that ones put to bed, what else can we argue about....?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Is a combi boiler safe with NO mains cold water? (Urgent)" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Lycanfox,
Last reply from
Reg Man,
Replies
89
Views
63,733
Back
Top