sheff paul

called today to give a second opinion on a recent fit,250 litre unvented hw cylinder,9 rads,most large doubles close to 16 kw output on heating side,all heating on one zone,been heated by a 18 kw sysyem boiler,not the best job.The term undersized boiler comes to mind
 
Paul,

Can you get the customer to clock the gas meter per day, perhaps its a bit late now the outside temperature is going up, but like you say it doesn't stack up, I think the 250 litre Un-vented primary coil is rated more than the boiler alone.
 
Best remedy bar adding a second boiler or putting a bigger one in would be to wire it up as a w plan, get the cylinder to temp then heat the house
 
Paul,

Can you get the customer to clock the gas meter per day, perhaps its a bit late now the outside temperature is going up, but like you say it doesn't stack up, I think the 250 litre Un-vented primary coil is rated more than the boiler alone.

the coil is rated at 19 kw,will work ok in spring,but in winter when hw calls demand the rads will be barely warm,another 3rd rate install cannot be bothered to get involved
 
called today to give a second opinion on a recent fit,250 litre unvented hw cylinder,9 rads,most large doubles close to 16 kw output on heating side,all heating on one zone,been heated by a 18 kw sysyem boiler,not the best job.The term undersized boiler comes to mind


It should be ok. If it hasn't, fit trvs which will reduce the load. Put hot water on 24 hours so it never heats from cold. Make sure loft and cavities are fully insulated. Maybe consider weather compensation if the customer isn't thick!
 
Not a very good install, but could get around it by setting the hot water and heating times separately so they aren't on at the same time.
 
Hang on a second.

If the cylinder is 250 litre and based on a temp rise of 40 deg C, then you should only need the full output of the boiler for just over half an hour to go from stone cold to piping hot. Whilst I agree that the rads will cool down in this time, the air temp should not drop more than a couple of degrees.

And thats assuming the worst possible scenario, of a stone cold cylinder being heated from scratch.

TBH I suspect some other problem here. You may be able to mask it by pumping up the input, but that doesnt make it the right diagnosis.
 
18kw for the whole thing is crap though ray.

Why? We used to allow 8,000 or 10,000 BTUs (BTUs, not KW) for hot water, and everyone was happy.

Sure, if I had a 16kw heating load and an unvented cyl, I would opt for a 24kw boiler. But I don't think it would be miles better than an 18kw. Better, yes. Miles better? Not really...
 
i wasnt getting at ya, we dont know what the usage of the cylinder is. imho that boiler isnt big enough for the maximum output at full load.
 
i wasnt getting at ya, we dont know what the usage of the cylinder is. imho that boiler isnt big enough for the maximum output at full load.

*Whistles*

but the boiler is good enough to do the maximum load of one OR the other.

W plan hot water priority.
 
Set the water to come on an hour before the heating. If that doesn't solve the problem then there are further problems with the install.
 
What temperature is the boiler set too?
It could be as simple as a faulty boiler stat.
Check the flow temp and see if it correlates with the boiler thermostat setting.
You don't need much of a temperature drop for a borderline boiler to really under perform.

Oz Plumber
 
I must have a weird way of looking at things. I suppose during the winter the heatings been next to useless most of the time its run.

if they haven't fitted a lockshield valve to the coil then it will offer next to no resistance, easily more than half the heat will run around that and give unsatisfactory performance to both. By the time the cylinder reaches temp then the heating will be going off.
 
Non issue in my eyes, as said just vary the timings slightly. We have the same at home boiler is currently range rated to 19kW with 15 rads (in 2 zones) and 300l unvented and we have never been cold or had no hot water.
 
they used to say allow 2kw for the hw on vented cylinders do unvented cylinders realy need that much kw .
 
No, the modern unvented cylinders just have much more efficient heat exchangers so they can actually disperse more power into the water quicker. You could charge them with 2kw of heat from the boiler and for similar sized cylinders they would heat up in exactly the same time as an older vented one. Well a bit quicker actually due to better insulation but let's not split hairs!
 
depends on the demand if its used by a few teenagers its gonna rob the heating regardless how long it heats or keeps the heat..i do like to learn and if 20kw can can heat a big house and big cylinder I'll be fitting smaller boilers in future.
 
Our cheap skate new home builders installed a Potterton Promax 15 SL 15KW system boiler onto our system. It has an unvented hot water cylinder with an 18.3KW heat exchanger. There are just under 15KW of radiators in our house.

You can get away with sizing a boiler to suit the heating requirement only in a house like Ray says. The rads will not be heated for the half hour or so a modern unvented cylinder takes to recharge, in practise it will hardly be noticed.

I caveat this with there are just 2 of us in the house and we use showers only most of the time.

Our house is a 5 bedroom detached house. I would say the boiler is undersized and when we change it I will fit a 24KW system boiler but it does the job.
 
Last edited:
There is no requirement to allow both the heating and hot water to be run at the same time under full load. Remember, the heat loss calculated will be at -1,-3 or whatever ie 1-2 weeks a year.

The rating of the coil is irrelevant really as long as heat up time complies with part L. In reality who's checking? How often will you need to heat the entire cylinder from cold?

if you are adding the coil size to the heat loss then your massively over sizing boilers.

Sounds like this boiler was sized perfectly which makes a change.

Also, who's to say the radiators aren't over sized? Sizing a boiler should be done by heat loss of the building not radiator sizes.

if they are running out of water, the cylinder is undersized not the boiler.
 
Suppose its like everything, make do and change settings or get it changed..also being there and knowing if their bath people or shower, and when through the day are people using hw....
 
im assuming its balanced. i still believe it to be undersized but hay ho.
 
Last edited by a moderator:
My parents house needs 29kw heat, it has two unventeds, a 250 and 300 litre.

boiler is 32kw output. Coils are balanced as is the system and it runs it more than fine.

it has solar but thats usually pretty irrelevant when the heating is needed.

if you cant see a lockshield valve on the coil then its the path of least resistance for the system to pump to.

simple valve and extend hot water periods.

all it needs
 
adjust the clock so the hot water comes on at a time the heating is not required.

Explain to the customer that that system is not designed to work with the Randal-style clock. Use the heating system in the Canada mode, not in the Cornwall 2hours day mode.
Remove the clock on the cylinder and put a thermostat instead the clock on the heating in the coldest room.
Make sure that the heating IS ON FOR 24/7 in THERMOSTAT-controlled mode.
Water should be in 24/7 on cyl thermostat.
Buy some programmed valves, to cut out unused rooms. Get the house PROPERLY insulated.

I remeber heating the 4room semi house with 32KW ex-combi boiler modulated down to ~8KW when the outside was -7 C. inside was 19 C. Solid uninsulated walls + loft insulation.

PS: You are not going to save much with well insulated unvented cyllinder kept on the timer. So ditch it for the cyl.

PPS: Do check the condition of the boiler's heatex (esp if the boiler is older than 5-20 years, and was serviced last time 5-10 years ago), Make sure it is clean. Use a spatula/stiff brush/stick for clening the crud out of it.
 
Lockshield valve on the coil, balance it and job done?

I was told that under part L we should no longer fit balancing valves to cylinders. The reason being all systems should be fitted with a programmer capable of separate times for heating and hot water and this enables the full load of the boiler to be sent to the cylinder before the heating comes on. Doing this means that the boiler can be accurately sized for the heat requirements of the property and it will remain in condensing mode for longer.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "under sized boiler ???" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
sheff paul,
Last reply from
happyflyer,
Replies
111
Views
13,006
Back
Top