Hiya guys
I'am in a bit of a stick
Small bungalow with a heating requirement of about 12.5 KW that includes an additional 10% heat loss on pipework.
One bathroom & one kitchen, customer has a bee in their bonnet about HW performance
Dynamic CW pressure of 1.2
CW flow rate of 18 litres per min
I know a heatslave 12/18 is going to do the job CH wise; It requires 1.5bar dynamic cw to provide 15/trs per min on the HW
But part of me wants to spec a 18/25 & put it on a low range 18KW nozzle just because it provides more HW flow rate & requires slightly less dynamic CW pressure to attain 18ltr per min on HW.
But if I choose the larger boiler its going to be approx 5.5KW bigger than needed & Iam just wondering if thats going to stop the boiler condensing as well as it should as oil boilers don't modulate.
Thanks for reading anyway