Hi guys... just a heads up first I've popped over from the electrical Forum where I Mod' for a little advice, yep I know, a Sparky asking a Plumber for advice, must be a sign of the end of the world :O
What my issue is my own boiler has been playing up, I'm a Electrical Engineer by trade and build control systems so actually identifying the problem wasn't a issue, burner flame cutout, refusal to ignite etc etc all traced down to the fan that had slowly but surely bit the dust and seized up, anyway after replacing said part it cured all the problems in one swift swoop but a new issue has risen it ugly head - the flame will only work in low thus I get luke warm water and C/H the same..
My query is what the Modulator voltages should be for High and Low as at present I'm only seeing 12v dc with a low flame.. now the way I see this is it thinks its already at temperature with the onboard stat which both are set to full, I'm aware it should start off high flame but it doesn't so suspect the fault on the pcb... any input would be great and please be kind or I'll set Dan on you 😀
PS - I am not interfering with the Gas side and nothing has been changed other than the fan which before its failure the boiler was all working fine.
What my issue is my own boiler has been playing up, I'm a Electrical Engineer by trade and build control systems so actually identifying the problem wasn't a issue, burner flame cutout, refusal to ignite etc etc all traced down to the fan that had slowly but surely bit the dust and seized up, anyway after replacing said part it cured all the problems in one swift swoop but a new issue has risen it ugly head - the flame will only work in low thus I get luke warm water and C/H the same..
My query is what the Modulator voltages should be for High and Low as at present I'm only seeing 12v dc with a low flame.. now the way I see this is it thinks its already at temperature with the onboard stat which both are set to full, I'm aware it should start off high flame but it doesn't so suspect the fault on the pcb... any input would be great and please be kind or I'll set Dan on you 😀
PS - I am not interfering with the Gas side and nothing has been changed other than the fan which before its failure the boiler was all working fine.
Last edited: