I think it sounds a lot to be honest with you.
I still think you would be wise to get a Heating Engineer to spec this job for you. Boiler size, Pump size and Domestic Hot water storage, any Cold water storage that may be necessary. You would benefit from the design and the advice they will be able to give. It will cost you a few hundred pounds but I think you will save a lot more. Plus you will have the peace of mind that it will be correct, the knowledge that the system is a as efficient as possible and someone to blame if it goes wrong.
 
I used the default figure in the sizing resistance in copper tube. It was tiny. 3.5M is much bigger. Yes looking at 40CDi regular, but with Robo kit. I thought 35CDi system was just too tight. In that case I would need 8.3M head.
By "default figure" do you mean 11 deg C as on page 2 (46 in the formula for flow rate on same page)? If so, that is incorrect for your boiler which is designed for a 20 deg C differential. 46 then becomes 84. If you redo your flow rates and resistance using 84, you will find that the head is about 30% of what you originally calculated. That's because resistance varies with flow rate squared.

What was "tiny"? Don't understand your reference to 3.5M and 8.3M.

You also need to take the 20C differential and lower operating temperatures (needed to ensure condensing) when selecting your rads, as rad output will be reduced.

It would have been helpful if you had mentioned HMO in your opening post.

Have you thought about having two boilers, a 17kW for the heating and a 20kW for the cylinder? A smaller heating boiler will modulate much lower and will be condensing more often - if the system is correctly designed. You could also include weather compensation.

The HW boiler needs to run with a flow temp of 70-75C and a 10 deg differential, otherwise the cylinder will not heat up to 60C quickly enough. This means the boiler will not condense.
 
You make some very valid points, I think I need to wind this back to make sure I'm getting correct results.
Calculating head is complicated, I'm now thinking about a single boiler using W-Plan. If I also have a 400L cylinder the heat exchanger is 17kW. This way I can use a single 18kW boiler to run both.
Worst scenario if the boiler can't cope I could buy a second 18kW boiler further down the road and have a dedicated boiler for each.
I recall being told by Worchester a while back you want your boiler running at 100% for best efficiency?

Thoughts?
 
Seems to be various heat exchangers, Gledhill 300L has 30kW heat exchanger !!!, I'm looking at Grahams Therma.

I'll just go for a single cylinder.
 
W Plan is either heating or hot water; you can't have both at the same time. If it's a HMO, you won't have any control over when anyone wants to wash, bath or shower. So there may be up to eight people showering early in the morning when the heating needs to be on. With W plan hot water takes priority; everyone freezes as the heating is not on. You can time the hot water to recover when heating is not required, i.e. overnight or when most of the inhabitants are at work; but this can't be guaranteed to work all the time.

Have you had the water pressure and flow rate checked to make sure it is sufficient for eight simultaneous showers?

You haven't answered my earlier questions, so here they are again:
  1. Where did you get the idea from that the CDi 40 heat exchanger was low resistance (tiny?)?
  2. Where does the 3.5m head come from?
  3. Where does the 8.3m head come from?
 
Water Pressure is very good in the property, they'll be no problem.
Agreed it's one or the other with W-Plan, it'll take some tweaking to get it right. But remember with HMO, they're not all rushing out the door to get to work, showers are spread throughout the day. For those that wash anyway!
1. I used a default figure from calculating copper pipe resistance for average boiler, this was proven to be inaccurate. My bad.
2. You said from Technical Bulletin 48 it was 3.5M ?
3. I calculated 4.8M using calculations supplied previously. I simply added your 3.5M and got 8.3M
 
Just been reading modern boilers prefer a W or S-Plan where each circuit gets 100% of boiler. Most 300 & 400 cylinders have a reheat time of 38-45 minutes. Therefore giving Hot Water 100% for 45 minutes every few hours should not affect Central heating that much.
I was also reading if you give hot water preference, you can reheat as soon as it drops, so maybe only need 15 minutes whenever someone takes a shower, so central heating should not be affected unless you get several showers in a row on a cold night.
They were also saying you want the biggest heat loss to stop boiler cycling, so again W or S-Plan so boiler always running at max.
 
1. I used a default figure from calculating copper pipe resistance for average boiler, this was proven to be inaccurate. My bad.
2. You said from Technical Bulletin 48 it was 3.5M ?
3. I calculated 4.8M using calculations supplied previously. I simply added your 3.5M and got 8.3M
  1. Modern heat exchangers have very narrow passageways for the water to pass through, so the resistance is very high. Also, the resistance is not fixed, it varies with the flow rate.
  2. The figure of 3.5m only applies when the heat exchanger is running at max output with a flow-return differential of 20C. The same hex running at 20kW, with the same differential, has a resistance of approx 0.8m. This is because the flow rate is halved. See attached chart for the CDi hex.
  3. The resistance of 4.8m assumed a differential of 11C. Resistance is proportional to flow². The flow rate for a 20C drop will be 55% if the flow for a 11C drop (11/20) so the resistance will be 0.55² = 0.30 x 4.8 = 1.45m.
  4. The available head on WB system boilers is 2m, which gives a margin of 0.55 metres.

Groves.png
 
  • Like
Reactions: fezster
Just been reading modern boilers prefer a W or S-Plan where each circuit gets 100% of boiler. Most 300 & 400 cylinders have a reheat time of 38-45 minutes. Therefore giving Hot Water 100% for 45 minutes every few hours should not affect Central heating that much.
Only W Plan can guarantee HW priority. That's because it uses a diverter valve (similar to Y plan but without a mid-position).

Most cylinder thermostats have a differential of about 10C. If the hot water is stored at 60C and incoming cold is at 20C, the cylinder temperature will drop to 50C when 25% of the hot water has been used. That's equivalent to two ten-minute showers for a 400 litre cylinder.

They were also saying you want the biggest heat loss to stop boiler cycling, so again W or S-Plan so boiler always running at max.
That doesn't make sense. Can you post a link to this?
 
Most cylinder thermostats have a differential of about 10C.

3°C is typical for a domestic mechanical cylinder thermostat.

If the hot water is stored at 60C and incoming cold is at 20C, the cylinder temperature will drop to 50C when 25% of the hot water has been used.

This would only be true if the incoming cold mixed completely with the hot water. It doesn't; cylinders are designed to prevent incoming cold disrupting the stratification so the transition between hot and cold as the tank runs out is fairly abrupt.

That's equivalent to two ten-minute showers for a 400 litre cylinder.

A 400 litre (nominal capacity) cylinder at 60°C will be able to supply about 440 litres of mixed water at 50°C, which is a painfully hot shower. A ten minute shower uses between 60 (eco head) and 150 (power shower) litres of mixed water so you should get between 3 and 8 showers out of a tank depending on personal preferences.
 
3°C is typical for a domestic mechanical cylinder thermostat.
Honeywell L641A = approx 10C
Drayton HTS3 = approx 8C
Danfoss ATC = 6-10C

Only mechanical thermostats with a working anticipator have a differential around 3C; and cylinder thermostats do not have anticipators

How do you design a straight sided cylinder to prevent incoming cold disrupting the stratification?

I wasn't suggesting that showers were normally taken at 50C. The two 10 minute showers assumed that the shower temperature was 40C; i.e. 50% cold @20C and 50% hot at 60C.
 
Apparently modern condensing boilers are able to carry a higher temperature than older boilers, so a 15mm pipe is able to carry 9kw, a 22mm pipe 24kW and 28mm pipe 70kW.
On that bases if my heat load is only 17kW I only need run 22mm pipe, I don’t need to run any 28mm?
 
Grundfos advised 1st pump should be configured with autoAdapt, with second pump fixed rate. This way AutoAdapt will adjust accordingly.
But Grundfos said 2nd pump would always be running at 100% which would reduce life and ties in with your comment.

I've got some more realistic prices, difference is about £200

I'm still leaning towards 2 in series.

Interesting discussion about 2 pumps in series. All the literature I've read says that 2 in series increases the head and 2 in parallel increases the flow. What I couldn't quite understand is how 2 pumps in series with different specs work in tandem? Eg. I have a 25-80 with a 15-60 in series - what exactly happens in that scenario, does anyone know?
 
Interesting discussion about 2 pumps in series. All the literature I've read says that 2 in series increases the head and 2 in parallel increases the flow. What I couldn't quite understand is how 2 pumps in series with different specs work in tandem? Eg. I have a 25-80 with a 15-60 in series - what exactly happens in that scenario, does anyone know?

How far apart are they?
 
Approximately 4-5m of 28mm pipework. There is also a zone valve in between the 2.

One pump is serving the entire system, the other only a single zone. This zone has the index rad on it and the pump in series is legacy before the 25-80 was fitted. The plan was to remove it but given it was working, it was left in.
 
Oh I see.
In all honesty, I have only ever sized pumps correctly and fitted the right one. I can't say I have ever experimented with pumps in tandem. I have seen it done but only in a situation where the pump was undersized and someone added another to the circuit further along at the point where the pressure and flow from the original was exhausted. I can see how this may work but it is not something I personally would do.

There is no reason why pipes and pumps cannot be correctly sized for the job they are intended to do.
 
Apparently modern condensing boilers are able to carry a higher temperature than older boilers
It's nothing to do with higher temperature, e.g. 80C compared to 70C, but with the greater difference between flow and return temperatures, i.e 20C compared to 11C. The larger difference is achieved by a lower flow rate - 14.35 litres/min @ 20C compared to 26.1 lpm @ 11C for a 20kW boiler.

The lower flow rate (lmp) means that the water velocity (metres/sec) is reduced proportionally. Experiments have shown that the water velocity needs to be above 0.3 metres/sec (to reduce the chance of sludge settling in horizontal pipes) and below 1.5 metres/sec (to reduce the noise caused by the water passing through the pipe.

The pdf "Small bore heating systems", which I attached earlier, has more information.
 
Oh I see.
In all honesty, I have only ever sized pumps correctly and fitted the right one. I can't say I have ever experimented with pumps in tandem. I have seen it done but only in a situation where the pump was undersized and someone added another to the circuit further along at the point where the pressure and flow from the original was exhausted. I can see how this may work but it is not something I personally would do.

There is no reason why pipes and pumps cannot be correctly sized for the job they are intended to do.

It's a bit of a mish mash to be honest. The 25-80 should be more than sufficient for that zone so the second circulator needs to come out at some point. Probably when the Low Loss Header goes in 🙂

I was just intrigued as to how it worked as logically it doesnt make sense to me that a second slower pump can work in tandem with one which is capable of much higher flow rates. But it does work, so not sure.
 

Official Sponsors of Plumbers Talk