Hi, I’m newly qualified and just need to clear things up. I shadow a few gas engineers still as I want to be 100% certain on what I am doing. I was at a landlord safety check yesterday and he was unable to do the operating pressure as it was a zero governor gas valve. So we done a gas rate instead, but my question is; can you always just do a Gas rate instead of operating pressure? Or should you preferably do the operating pressure when you can?
I’m not sure whether working with 3/4 different engineers is making it more confusing for me as they have so many different theories!
Thanks in advance.
 
You can still check the inlet pressure to see if the gas supply is correct or undersized
 
You are getting confused mate. Your gas rate dependant on size of boiler will come out at around 3.0kw but everyone calls the output rating a gas rate?
 
You can still check the inlet pressure to see if the gas supply is correct or undersized

We checked the inlet pressure and there was no drop from the meter which means it was all good in that sense. Just a bit confused on the bit that you fill out on the actual certificate.
 
You are getting confused mate. Your gas rate dependant on size of boiler will come out at around 3.0kw but everyone calls the output rating a gas rate?

So where it says operating pressure or heat output what can you do there? On that specific boiler I mentioned? We left it by doing just your normal gas rate as in time taken to do one revolution with the appliance on full rate.
 
Premix fan boilers (all modern condensing boilers) you can not take a ‘Burner Pressure’.
However you can take a ‘working inlet pressure’. This should be done with all other appliances burning on full. This test tells us if the gas pipes are sized correctly and if the regulator on meter is opporating correctly.
You can Gas Rate Any gas appliance and this makes our lives easier because it means you don’t need to take cover off the boiler!
However I do recommend that you do take cover off and visually inspect boiler inside. This is because if you sign a boiler off that is defective inside then it’s your head on the block
 
Premix fan boilers (all modern condensing boilers) you can not take a ‘Burner Pressure’.
However you can take a ‘working inlet pressure’. This should be done with all other appliances burning on full. This test tells us if the gas pipes are sized correctly and if the regulator on meter is opporating correctly.
You can Gas Rate Any gas appliance and this makes our lives easier because it means you don’t need to take cover off the boiler!
However I do recommend that you do take cover off and visually inspect boiler inside. This is because if you sign a boiler off that is defective inside then it’s your head on the block

Thanks for your reply, everything has been taken on board. I appreciate your guidance, cheers!
 