Replying to a slightly old post, but this is exactly what I did recently and it works fine. I used a 2NC contactor (as I have 2 CH zones) and a 3 module wylex enclosure, as the 2 module one linked to in this thread doesnt have the required depth to house the contactor.
When DHW fires, it shuts...
From the FAQ sheet: https://heatingcontrols.honeywellhome.com/documents/All/pdf/975.pdf
"When this Heating demand is satisfied, during a Heating ON period, 50V to 150V (voltage can vary according to the supply) will remain on the orange wire and the valve will continue to be energised and warm...
From my experience, a honeywell ABV is very easily damaged (Im sure other brands are similar) if you try to set it incorrectly. So worth checking if it is constantly bypassing (assuming you have a bypass!).
I had that exact problem with my Vaillant 438 many years ago John. Despite d.0 range rating, the boiler would first fire at X% of it's total output. A later revision of the PCB improved on this (although, it continued to be a problem to an extent).
The return temperature will dictate the amount of condensing which occurs. The lower the return temp, the more it condenses (45 degrees for 90%+ condensing, 55 degrees will be less than that). However, even if the boiler is setup for 80 degrees flow temps, and assuming the system has been setup...
Have they measured your incoming flow rate and dynamic pressure to ensure an unvented cylinder is suitable? It should be a minimum of around 20 litres / min with 2 bar working pressure. You will also need to ensure your internal pipework is upgraded, especially to showers which should be in...
The 2 port valve won't stop the reverse circulation (as the water doesnt flow through it when this occurs).
The return water from the HW cylinder may go back up the return pipe for the CH (as it is the last tee). It will then flow in reverse through the radiator flow pipe to the next radiator...
Would you mind elaborating on this?
If your EV is charged to 1 bar and you top up the system to 1.5 bar, you are utilising the expansion capacity of the vessel when cold, reducing the amount of expansion available when hot. Is there some advantage in doing this (which is what I think you were...
Yes, if it's not drop tight, the static pressure could rise under no flow conditions.
Does the pressure only rise when the unvented cylinder is being heated? If so the EV needs charging (as said above).
You should also have a NRV between the cylinder and the balanced cold, to stop hot water...
Does anyone have experience of either of these?
Reliance – Aquasystem 500 Litre Potable Expansion Vessel XVES050150
£660
GWS Challenger 450L Accumulator Tank
(same as Stuart Turner Mainsboost 450SV?)
£690
Both are similarly priced.
The reliance has a replaceable membrane.
The GWS has a 5...
Boiler is a Vaillant 438.
I'm not sure about in Summer, but I guess will find out soon enough. The kids are only just now using the shower more excessively. I will have to educate them on how HW can run out and not to spend unnecessarily long in there.
I'm toying with the HW priority and...