It's a big system commerical 35 rads. Plan on running the system at 1 bar cold. I know most expansion vessels in combis are pre charged to 0.75 bar.Normally, a E.vessel would be installed pre charged to 1.0 bar and then filled to 1.5 bar, it will then rise to ~ 2 bar with a hot system, no problem. If its pre charged to 1.5 bar and its only filled to 1.5 bar then the final pressure will be practically the same but will have to be topped up more frequently after any air venting etc as there is no reserve. If pre charged to 1.5 bar and filled to 2 bar then the final pressure will be ~ 2.6 bar, still OK but getting a bit near the boiler PRV (safety valve) lifting pressure of 3.0 bar.
Why have you a 35 litre E.vessel for a CH system??, it's normally around 10 to 12 Litre, are you sure its not attached to your unvented HW cylinder? If it is attached to your CH system then the pressure will only rise ~ 0.25bar even with precharge/filling pressures of 1.5/2.0 bar
Thanks its yet to be fit so if I'm going to depressurise now is the time. I want to run to system at no more then one bar cold. Boiler manufactor specifics this. Also is a convert from open vented to sealed so want to keep the pressure as low as I can. Thanks.You will have to fully de pressurize on the water side before reducing the air side pre charge pressure.
If you have no special concerns re pipework/rads why not leave it at 1.5 bar and initially fill to 1.5 bar, I wouldn't expect the hot pressure to be >2.2 bar and try that, if you fill to say 1.7 bar would expect ~ 2.3 bar, you may well find those final pressures are lower as I calculated them on a system vol of 400 litres which may be lower.
If you do the above and post the findings I can probably calculate the air side reduction required without draining down the system, just ensure all the system up to normal temperature.
Can I also ask what would happen if the system was filled to 1 bar cold. And the expansion vessel was left at the pre-charge of 1.5bar? Guessing it wouldn't start using the expansion till it gets to 1.5 bar. So the pressure would rise quiet alot?If you want to run at 1 bar cold then reduce the pre charge to 1 bar and fill to 1 bar or preferably reduce pre charge to 0.75 bar and fill to 1 bar, even with a system capacity of 500 litres then the hot pressure at 1bar/1bar will only be 1.71 bar and at 0.75bar/1bar, 1.85 bar.
No, since water is virtually non compressible it would almost immediately rise to 1.5 bar (after heating up a few degrees) and would behave exactly the same as if the pre charge and filling pressures are the same ie 1.5 bar.Can I also ask what would happen if the system was filled to 1 bar cold. And the expansion vessel was left at the pre-charge of 1.5bar? Guessing it wouldn't start using the expansion till it gets to 1.5 bar. So the pressure would rise quiet alot?
Thanks I was going to go with one bar system pressure cold. And a pre charge of 1 bar. This should go up to around 1.75bar did you say?No, since water is virtually non compressible it would almost immediately rise to 1.5 bar (after heating up a few degrees) and would behave exactly the same as if the pre charge and filling pressures are the same ie 1.5 bar.
If the system capacity/precharge/filling are 400ltrs/1.5bar/1.5 bar the final pressure will be ~ 2.16 bar with a 35 litre EV.
If the system capacity/precharge/filling are 400ltrs/1.5bar/1.75 bar the final pressure will be ~ 2.57 bar with a 35 litre EV.
If the system capacity/precharge/filling are 400ltrs/0.75bar/1.0 bar the final pressure will be ~ 1.63 bar with a 35 litre EV.
Ah so I should drop the pre charge to around 0.8. But then the expansion vessel will use some of its storage even when the systems cold? Interesting thread. Didn't no the ins and out of pre charge pressures etc. Just thought was abit high at 1.5 bar on the vessel bought.Normally 0.2 bar below operating pressure matt
I think that answers my above question.Yes, the advantage is that you have a reserve volume of water to make up for any air venting, micro bubbles collapsing or any tiny leaks without the system pressure falling below your minimum requirement of 1.0 bar before top up is required, you can also monitor for any leakage as the pressure will fall from 1.5 bar cold to 1.0 bar before exhausting this reserve.
If you take a fairly standard CH system of 75 litres with a 12 litre EV pre charged to 1.0 bar and filled to 1.5 bar then you will have a reserve volume of 2.4 litres and a final hot pressure of 1.92 bar, if both pre charge and filling pressure are 1 bar then no reserve and if any slight leakage/venting etc the cold pressure will start falling immediately, but yes, the reserve does reduce the amount of expansion available as the final pressure with no reserve will be 1.26bar (vs 1.92bar), any pressure up to 2.25/2.5 bar is not a problem for any system, one can always install a slightly bigger EV if any worries re final pressure.
System or HWC capacity | 7.00 | Litres |
Vessel Capacity | 2.00 | Litres |
Pre Charge Pressure | 3.30 | Bar.G |
Pre Charge Pressure | 4.30 | Bar.A |
Filling/supply Pressure | 3.50 | Bar.G |
Filling Pressure | 4.50 | Bar.A |
Air Space Vol | 1.91 | Litres |
Reserve Water Vol | 0.09 | Litres |
Expansion % | 1.83 | % |
Expansion | 0.13 | Litres |
Water Space Vol | 0.22 | Litres |
Air Space Vol | 1.78 | Litres |
Final Pressure | 4.82 | Bar.A |
Final Pressure | 3.82 | Bar.G |
Thats what's happened yes. So a pressure relief and expansion valve under the sink won't work on this heater?That’s the thing it’s not unvented it’s gravity / equal pressure
the heater isn’t under pressure it’s always open to atmosphere hence when it’s heating the tap will drip most people try and tighten it down more which just breaks them
Any calcs with air (or any gas) pressures involved must be done in absolute (a) units, absolute pressure is Gauge Pressure (g) + 1 (bar) you then subtract the 1 to return to gauge pressure. Atmospheric pressure is 0 Bar.g or 1 bar.aCan I ask what is ment by bar A/ bar G pre-charge?
Same, hence why this forum is great for building up knowledge.I thought a vented tap was for use with a unvented HW heater and should only leak/drip while the water is heating up and could be used in lieu of a expansion vessel but obviously not.
Reply to the thread, titled "Expansion vessel pre charge" which is posted in UK Plumbers Forums on Plumbers Forums.