I have a vokera compact he35 combi and would like to check a few things:
1. Is the DHW thermostat “dry” or does the boiler need to be drained to replace this?
I ask the above as I am experiencing a few issues with the boiler and thought of trying the above first.
Hot water is...
Shaun, now I'm confused. He has linked the 4th port on the FLOW pipe to the 4th port on the RETURN pipe. The other three ports on both flow and return serve 3 radiators. The system has 16 rads in total served by a number of manifolds.
You appear to suggest what he has done is wrong, May I ask why?
Just spotted one of the 4 ports on the above FLOW unit is plumbed directly into the RETURN unit. Should plumber not have blanked off the unused port on FLOW and RETURN instead of plumbing them together? Manifold is feeding 3 rads.
Just checked and flow and returns are correctly plumbed at manifold. Measured length again and closer to 10m each way! Also noted none of the microbire pipework is insulated, so yet another to do job or is the heat loss through 10mm microbore not worth worrying about? Will be draining the...
Thought I would provide an update on this one, as only fair given all the advise given to date. Currently running system with x400 sentinel in it before giving it a manual flush using mains pressure in a couple of weeks time.
What we found to date - 2 problem rads (slow to heat and not heating...
took a break from this problem as a- we had a temp swing of +15 degree here in Glasgow in the last week and so not so urgent as before and b- head was spinning fault finding. Consensus appeared to be that there was a blockage in the return leg from 3yr olds radiator. Whilst I have yet to...
brainwave.........perhaps, just seen brothers hot rad - 65 top, 67inlet, 55 outlet (ideal 12 degrees temp drop) with lockshield at 2 turns from open. Problem rad is wide open on lockshield with inlet of 63 and outlet of 58 (5 degree drop) and top of rad at 58. Surley if I throttle down...
well. after a couple of days tapping the TRV in 3yr olds room, finally bot the bullet and replaced the TRV body completely with new unit. Pump speed 3. with the result .....................NO CHANGE! 55degree radiator temp at top compared with brother room at 65 degrees. Radiator no cold zones...
7:30am - 52 lounge, 55 bedrom, coming up but slowly as other rads in system start shutting down on thier TRVs as rooms reach temps...........downside of all this is I now have a boiler pressure of 2.7bar!!!!!!!!!1 up from 1bar cold. Clearly increasing pump speed to 3 with current lockshiled...
7am update, heating on for 1hr, 1-degree outside..............no improvement. rads 65-degree throughout house, problem 2 still at 50. Going to kick out theem with a mallet when I get back from work tonight
Can I just ask one more favour - Im seeing 1.25 bar pressure rise from cold to hot and have a cold pressure of 1bar, hot goes just over 2bar after 3 1/2 hours tonight. Does this indicate I should check/re-pressurise the expansion vessel or is +1bar from heating acceptable? The vokera 35h EV...