Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Alpha man

Gas Engineer
Jan 11, 2011
1,137
173
63
Charing
Member Type
Heating Engineer (Has GSR)
Guys,
could do with a little advice please, have just been to a Baxi 105e combi, nothing working and with the 30 and 50 neons flashing on off together, according to the neons
It's, failed to light, or condense blocked and fan or flue fault,

The condense trap nor pipe arent blocked, and flue and air switch and flue venturis are ok,, but no power at the fan, so with my limited knowledge on anything else except Alpha, so I presume the PCB is down,

So before I commit on buying a PCB, am I heading in the right direction?

Cheers
 
Is there any way of linking it out?
Pull the earth off the trap and if it lights do what Shauncorbs said. But I would not personally leave the lead disconnected. One of the lads did that when I was on the books at a form and the heat ex melted.🙁😱😱
 
Pull the earth off the trap and if it lights do what Shauncorbs said. But I would not personally leave the lead disconnected. One of the lads did that when I was on the books at a form and the heat ex melted.🙁😱😱

😱 How would that melt the hex sounds like it's run dry
 
Don't want to link it out as that will cut the boiler out just remove one of the leads and tape it up
We had a heat
😱 How would that melt the hex sounds like it's run dry
no idea and I thought that. But some how it did? But then again I wasn’t there so could be Bull s**t. But I have never left the cable disconnected after that story😛😛
 
Evening mate. Did you pull the lead off the trap before you put the new one in to see if it came on and stayed on? Or did you glfit the trap first? Only asking as you could take the trap back
 
Evening mate. Did you pull the lead off the trap before you put the new one in to see if it came on and stayed on? Or did you glfit the trap first? Only asking as you could take the trap back
Yep, pulled one lead off, and still didn't work, but no continuity across the condy trap, hence why I bought a new one to try, but turned out to be the PCB.

It's no bother, ill work it in to another customer who's another one of these boilers!!
 
Yep, pulled one lead off, and still didn't work, but no continuity across the condy trap, hence why I bought a new one to try, but turned out to be the PCB.

It's no bother, ill work it in to another customer who's another one of these boilers!!
you very rarely need the condy trap you just need the clean the contacts
 
Last edited:
  • Like
Reactions: Alpha man

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.