Dec 16, 2016
28
Help appreciated to help me think this one through.. 🙂
Have changed the synchro motor
Gears are fine.. micro switch fully engages when hot water is switched on from timer.. you can see and hear the click from the microswitch
the switch is calling for the boiler to burn.. hot water no problem
Surely the microswitch, when off, closes the pipe to the cylinder and just directs the heated water into the central heating SO what triggers the call for central heating..maybe an open microswitch at the 2 port and a call from the room stat.
room stat is turned up
SO.. the room stat is faulty as the 2 port seems fine?
The heating sometimes works but sometimes doesn't.. an intermittent room stat fault?
It's an unvented system with solar water heating.. so two 2ports to the cylinder.
You must have another two port for your heating circuit.
Programmer-Room stat-MV- Boiler on !
you need to check the heating MV Surely.
MV = Motorised Valve.
There are two or three port types in most domestic installations like yours.
You normally would have an 'S' plan ( zone valves or two port valves, one for each zone e.g Hot water, Heating upstairs, Heating downstairs, Underfloor heating etc).
Or a 'Y' plan which is a three port valve ( one port to Heating and one port to Hot water)
What set up have you got?
The thing you mention about open microswitch and signal/voltage from room stat is not correct by the way
there is no three port.. with the cylinder are two two ports..
A two port can't control two circuits separately.
Is it possible you have another one you haven't seen
Can you post photos of what you have got.
found it.. there are three two ports
so.. i guess this is the culprit? Guess Ii need to remove and check gearing, synchro motor and micro switch.
Thankyou
two are honeywell and the other is a danfoss.. pic hereView attachment 28422
Thankyou
I would check the voltages are correct (L+N) at the valve supply when there is a call for heat. Rather than pull it to bits. It could save you a lot of time and effort.
V
UK Plumbers Forums
Deleted member 120897