This is my first post and need help with underfloor heating.

I have just had an extension built with the floor area for this room now circa 24m2. This room is going to run underfloor heating on its own zone. Rest of the house is rads.

System has been installed and just waiting for room stats to arrive so insulation can be completed.

After the plumber left I had a look at the manifold and noticed that the pump hasn't been fitted. He informed me that he did this as he didn't want to cause pressure issues on my existing combI. 28I junior. I sort of understand this and wasnt worried. But having had another look I have noticed he hasn't fitted the mixer value which I assume is a big issue.

Any advice on how to proceed? I don't want to damage the boiler but I also don't want to be over heating my floor and damaging screed and tiles.

Many thanks in advance
 
Thank you for the quick response.

Is there any chance that the additional pump will cause a problem with my boiler. Plumbers says he has had experience of this in the past and that my boiler is powerful enough with out additional pump being installed
 
Last edited by a moderator:
I don't think he is planning on fitting later. Pipework and zone valves all fitted all the way back to the boiler. UFH is not running yet. I assume the zone valve is closed.
 
1449959304610-1484313303.jpg

As you will see its also leaking
 
Without a mixing valve and seperate pump. Your floor is going to get very hot! The only way this could work ( sort of) is if this was the only heating needed from the boiler. Then the boiler thermostat could be set at a lower temp.
But as you have existing radiators, you will need them to be higher temp.
It's a shame in our trade when the customer has to correct the plumber! In this case I do wonder if he is one.

Get him back and sort those leaks.
 
Have seen this a few times , people do not understand how underfloor heating works . Worst one we saw 2 manifolds 12 zones on one and 10 on the other all from a Baxi 100 combi . Took the customer 12 months to realise something wasn't right
 