Hello all,
My heating system is as follows: Y plan configuration controlled by a Landis & Gyr timer (hot water or heating & hot water selection)

This weekend I have changed the timer to a Drayton Mi-genie wish 2.When I changed the timer over it would only allow water to be heated.
I drew out the circuit to find the HW OFF signal to the grey cable on the 3 port valve was missing. This has now been installed and electrically works fine.
My problem is that the radiators are not getting as hot as before, taking all day to get up to 19 deg! even when only heating is selected (hot water off).
Do I have a problem with my 3 port valve now that the grey is being used?

Any my advice would be gratefully appreciated.
 
The correct wiring is inscribed on the head of the valve. Make sure grey wire becomes live when hot water call is satisfied. This, together with white live, fully opens valve to heat
. If head fitted correctly, cable exits next port A. Manual lever on side of port B.
 
Last edited:
Took off the 3 port valve head and selected each of the 3 settings. 'Water' didn't move. 'Heating and hot water' turned half way & 'heating only' turned all the way over so I eliminated the valve. Checked voltage at pump and that was ok. Turned mechanism in valve and found resistance. Kept turning to release and is now free. Tested heating and all rads are getting hot. Will test over the next few days and if it sticks again will replace the valve.
Thanks for the advice.
 