I would love to be able to get my teeth into this job/headache!
shame tbh
not when its a system boiler.You size boilers for the hot water demand, not heating. I would get this system balanced properly using the two thermometer method, getting the correct temps on the flow and return and sorting out the bypass in the process. I would put money on this sorting it.
... have you been in touch with Intergas...
Here goes! Why do you need a bypass on a "y" plan? There's always a port open to either the cylinder or a bypass radiator! Both long enough runs and usually longer than where the bypass would be fitted.
not when its a system boiler.
so the boiler is short cycling, turning itself off because it is up to temperature, so what temperature is the return pipe??
is there one or two radiators that get piping hot quickly? = balancing issue.
have the parameters been properly set?
ch power to max 85 percent??
is installation type set to position 3- heat only!??
Why do you say that? The 18SB (OP's boiler) drop is only 0.75m at full output, which leaves 3.5m for the heating circuit.the pressure drop on the Intergas alone is rather high to start with.