We are about to install a central heating system with a max run of 30m from the boiler and I was wondering if it would be a good idea to install the ABV (automatic bypass valve) at the end of the circuit to keep the circuit as warm as possible. There are 20 rads (19 TRV) and 3 towel holders (always open)
Thanks in advance for any input.
the further away fm the boiler it is the better, most mis state a min distance away.
No, there's no need to keep the circuit as warm as possible.
Hi Alex, could you pls elaborate?
The ABV will open and 'short' the circuit when a significant proportion of the 20+ radiators with TRV stop taking water from the main distribution loop (32 and 25mm MLCP) Placing it a the end of the 30m circuit would mean hot water leaving the boiler would at least "go round the circuit" before returning, thus sinking some of the heat energy and keep all the branch circuits in contact with hot water.
An ABV closer to the boiler is only dealing with the pressure issue, further away if can also return cooler water to help with boiler cycling??
Don't think you quite understand the purpose of an ABV, what type of boiler are you installing ? What are the manufacturers minimum flow rate requirements through it ?
Its quite possible I dont understand something! That why I am here..
Ferroli ECONCEPT-TECH-MICRO 35kW combi condensing with accumulator. There is no min specified but I calculate 300L/hr to "sink" the min power of 7kW.
As you say - you've got 3 towel holders (always open). Why do you need ABV?
System has a 20 deg drop across each element (rad or towel hoder). Not sure I can sink the min power output of 7kW with the 3 towel holders (and the ref rad near the thermostat in the hall way)
ABV not expensive, dont see any downside to installing one to guarantee system will always work well.
building regs require an abv, as there is a risk of towel rail being used as a bypass,being isolated and pump pushiung against a dead circuit and all the problems that will cause. so for £20 put one in
The above boiler has built-in HYDRAULIC BYPASS - speeds up installation and ensures the minimum flow rate through the heat exchanger at all times.
Nothing to worry about!
As Alex suggests if boiler has by-pass built-in then no requirement for additional one to guarantee min flow rate, if a boiler does not have one then using ABV it should to set to open as pressure in system builds which would equate to a flow rate of 0.0833 kg/s (your 7kW @ 20 C diff) this would send flow water straight back to the boiler which would shut down on it's thermostat as we would want as system / house is up to temperature. Therefore best place for ABV is as close to boiler as poss but after pump.
Hope this helps.