Yeah this makes sense but is it something that needs to be done on an old existing system. I would say yes but customer will say show me where it says that and this document is ambiguous as ever. Not criticising what you've put as it is right however it does seem to imply new buildHad to quote customer the regs as they didnt like the idea of an aecv
8.17.1 An additional emergency control valve (AECV) shall be fitted:
a) to the installation pipe where it enters the building if the meter is sited 6 m or more away from the
building; or
b) inside individual flats served by a large single or multiple meter installation located in a remote or
communal area (see Figure 7).
Here is the rest of it
8.17.2 Every AECV shall:
a) be labelled or marked to show its open and closed position;
b) be fitted in an accessible position;
c) be easy to operate;
d) be fitted with a suitable handle which is securely attached, or other permanent means of operation;
e) where the lever moves in the vertical plane, move to the “off” position in a downward direction.
There shall be a permanent notice attached to the valve giving the following information:
a) the valve is an “emergency control for customers’ use”;
b) details of the parts of the installation isolated by the valve;
c) the telephone number of the Gas Emergency Service; and
d) advice to the customer on actions to be taken if they think they can smell gas.
8.17.3 A pressure test point shall be installed no more than 300 mm downstream of the AECV.
Had to quote customer the regs as they didnt like the idea of an aecv
8.17.1 An additional emergency control valve (AECV) shall be fitted:
a) to the installation pipe where it enters the building if the meter is sited 6 m or more away from the
building; or
b) inside individual flats served by a large single or multiple meter installation located in a remote or
communal area (see Figure 7).
Here is the rest of it
8.17.2 Every AECV shall:
a) be labelled or marked to show its open and closed position;
b) be fitted in an accessible position;
c) be easy to operate;
d) be fitted with a suitable handle which is securely attached, or other permanent means of operation;
e) where the lever moves in the vertical plane, move to the “off” position in a downward direction.
There shall be a permanent notice attached to the valve giving the following information:
a) the valve is an “emergency control for customers’ use”;
b) details of the parts of the installation isolated by the valve;
c) the telephone number of the Gas Emergency Service; and
d) advice to the customer on actions to be taken if they think they can smell gas.
8.17.3 A pressure test point shall be installed no more than 300 mm downstream of the AECV.