Just done a boiler swap and this is killing me. Sealed system was a greenstar ri have put in Glowworm R so no diffference. New pump. Can get all rads hot individually but not all together so no blockage. Out of ideas here any thoughts. Boiler cycling on n off but heat going nowhere else
 
No drain off but AAV above. I’m 99.9% sure pump is right way round as I goes down and under and into centre of three port
 
A few more thoughts.....maybe stick a pressure gauge in one rad's blank vent to ensure static head is same as filling pressure of 1.5 bar or whatever, allowing for difference in pressure gauge elevations. If OK increase the filling pressure to 2.5 bar temporarily which might collapse/shift any entrained air.
It does point to a head/circulation problem for whatever reason as one rad at the time only circulating, suggest re installing the UPS3 and beg/borrow a energy monitor, put the pump to full speed 3 and measure the power.
27W = 0 circulation, 36W = 0.3 m3/hr, 5 LPM (one rad maybe circulation). 43W = 0.6m3/hr, 10 LPM (minimum, "normal" expected) and 60W = or > 1.1 m3/hr, 18.33 LPM.
 
That sucks, well done finding it.
I did a boiler the other week and didn't realise until commissioning that all 5 rads in extension had massive highspots (when I saw the pipes behind the rads I assumed it ran down the wall, not up from the floor and back down to tails!), combined with vented system it was a massive PITA!
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Air or not" which is posted in Air Sourced Heat Pumps Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Riley

Plumber
Gas Engineer
Subscribed
Plumbers Arms member
Joined
Location
Sarf Coast

Thread Information

Title
Air or not
Prefix
N/A
Forum
Air Sourced Heat Pumps Advice Forum
Start date
Last reply date
Replies
18
Unsolved
--

Thread Tags

Tags Tags
None

Thread statistics

Created
Riley,
Last reply from
John.g,
Replies
18
Views
2,150

Weekly or Monthly Email Digest

Back
Top