As I've never had the opportunity to help install (or see designed) a traditional system boiler/cylinder plumbing set-up, some airing cupboards leave me scratching my head.

1. When the boiler is housed next to cylinder and the return rises up from ground level and T's into the cylinder coil tapping as it passes, wouldn't that unintentionally heat the cylinder even when hot water wasn't being called for?

2. When you see a pipe T'd off the flow from the boiler before it passes through the pump and divertor valve, what is this likely to be for? Since it would get hot no matter what you were calling for....I'm guessing often a bathroom rad? Or could it be something else?

3. If the flow has a bleed valve at it's highest point which has been replaced with a cap is this simply because the lazy plumber didn't want to get a replacement valve and all he had was a cap? Or could there be a good reason?

4. Do even experienced guys like some of you sometimes look in an airing cupboard and think...I have no idea what half of this is doing or where it's going...?
 
1. Depends on valve arrangement , but if divertor valve is on heating only there will be no flow through the coil
2. Combined feed and vent
3. We sometimes use a cap , easy to bleed and usefull for chemical additions
4.No LOL its usually easy to sort, trace the pipes
 
As I've never had the opportunity to help install (or see designed) a traditional system boiler/cylinder plumbing set-up, some airing cupboards leave me scratching my head.

lIt all comes with experience

1. When the boiler is housed next to cylinder and the return rises up from ground level and T's into the cylinder coil tapping as it passes, wouldn't that unintentionally heat the cylinder even when hot water wasn't being called for?

Yes a gravity system, however you may see a valve fitted to this with a thermostatic head to provide an interlock

2. When you see a pipe T'd off the flow from the boiler before it passes through the pump and divertor valve, what is this likely to be for? Since it would get hot no matter what you were calling for....I'm guessing often a bathroom rad?Or could it be something else?

One or two pipes between boiler and pump on the flow are feed and expansion pipes or single pipe combinded feed and expansion.



3. If the flow has a bleed valve at it's highest point which has been replaced with a cap is this simply because the lazy plumber didn't want to get a replacement valve and all he had was a cap? Or could there be a good reason?

If a compression cap fitted it can still be vented just loosen and retighten


4. Do even experienced guys like some of you sometimes look in an airing cupboard and think...I have no idea what half of this is doing or where it's going...?

Not very often
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Airiing Cupboard Blues" which is posted in Air Sourced Heat Pumps Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
WaterTight,
Last reply from
ecowarm,
Replies
4
Views
1,438
Back
Top