Hi all,
Struggling to find a yes or a no answer here🤷‍♂️

BFC 30 installed... gas fired and unvented. Very very limited on where I can install the temperature and pressure relief discharge.... can I tee this into the condense on a swept tee? Provided of course it’s push fit and pvc-u

The condense is trapped at bottom at bottom of the flue Going into a rain water stack

thoughts appreciated!
 
Yes fine aslong as the run can take both loads at worse case and either polly prop or mupvc

Is the rain stack going to mains and commercial appliance

thanks Shaun, I must admit I expected an input from you...

yes stack going to mains and yes commercial. 28mm relief and 1 1/2 outlet going to rain water stack.
Client has stated a trap is required where it drops into condense line..

Bearing in mind it is literally serving condense and no other appliance nor sanitary and the condense trapped at appliance this isn’t necessary is it? Or am I completely wrong?
 
Yeah that’s I guess that’s no biggie.

Nothing worse than starting to question yourself and can’t find anything in black and white to silence the doubts!

Much appreciated Shaun👍
 