Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Balancing radiators or not.

View the thread, titled "Balancing radiators or not." which is posted in UK Plumbers Forums on UK Plumbers Forums.

Hi all. I have a Combi green star 30i gas boiler and Was installed by helplink a few years ago to my existing system which was installed by servo warm. I have had 2 new extra radiators installed bringing the total to 8. All the radiators except the one in the hall have trv valves. As far as I know all the lockshield valves were fully open but I have been trying different ways of trying to balance the system to get the best. I have gone around and opened the lockshields 1/4 of a turn in order but the radiators are hissing. Would it be ok to open all the lock shields to fully open and see what happens? I have no issues with any cold radiators or cold spots anywhere.
welcome the advice please.
 
The idea of balancing the system is to ensure even and suitable flow to each radiator. If you open all the lock shields up you may find the rads at the furthest destination don’t receive much flow and then you’ll need to balance again.

When balancing its best to but rarely possible to do on design outside temperature days and with the flow temperature at design flow temperature. It’s a bit warmer at the moment so if you have to balance again open all windows and doors to try and mimic full load conditions. Shuttle adjustments can be made if needed afterwards.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Balancing radiators or not." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Njh11,
Last reply from
SJB060685,
Replies
2
Views
1,666
Back
Top