T
TheGasEngineer
How to test a Baxi condensate trap.
This condensate trap is used in a number of Potterton boilers as well so I understand and it can be the cause of a flame failure lockout.
Baxi will tell you to disconnect the white wire by the fan and if the boiler runs it's a damp trap....
Well it would be damp. It's a trap! So I asked how I test the trap resistance to see if it's ok? They didn't know. I asked what resistance would trigger flame failure? They didn't know... Hmmm
So I put a 250v insulation resistance test between the trap white wire and the case (and it must be disconnected from the PCB please!!) and got 7MegOhms.
Now 7MegOhms is a high figure but nevertheless this triggers flame failure. A quick clean and another reading showed >200MegOhm and this time the boiler ran. The problem is I don't know what the critical resistance is - the value where the boiler will *just* run but lets say it's 100MegOhm
The point is, during a service do the test and if the reading is 100MegOhm then it's clean enough. If it's less, dry the terminals and re-test. otherwise next week it might go critical and you get a call-back...
If the boiler suffers flame failure and the resistance is >100MegOhm then the PCB is probably US. Without this measurement there is no way of being absolutely sure which part is the problem.
This condensate trap is used in a number of Potterton boilers as well so I understand and it can be the cause of a flame failure lockout.
Baxi will tell you to disconnect the white wire by the fan and if the boiler runs it's a damp trap....
Well it would be damp. It's a trap! So I asked how I test the trap resistance to see if it's ok? They didn't know. I asked what resistance would trigger flame failure? They didn't know... Hmmm
So I put a 250v insulation resistance test between the trap white wire and the case (and it must be disconnected from the PCB please!!) and got 7MegOhms.
Now 7MegOhms is a high figure but nevertheless this triggers flame failure. A quick clean and another reading showed >200MegOhm and this time the boiler ran. The problem is I don't know what the critical resistance is - the value where the boiler will *just* run but lets say it's 100MegOhm
The point is, during a service do the test and if the reading is 100MegOhm then it's clean enough. If it's less, dry the terminals and re-test. otherwise next week it might go critical and you get a call-back...
If the boiler suffers flame failure and the resistance is >100MegOhm then the PCB is probably US. Without this measurement there is no way of being absolutely sure which part is the problem.