Final update - I've now run the CH on 3 seperate occassions for a total of 9hrs without a problem, same time as using DHW.
Conclusion
Water in the gas main external to my property caused some contamination of the gas valve filter. This in turn caused a reduction in flow/pressure supplied to the gas valve which led to a drop in supply pressure of 1mb. Whilst not a problem to the maximum pressure it was a problem to the minimum required pressure of 2.5mb, pressure actually measured at 1.5mb. I estimate that 4% loss of flow through the gas valve filter would lead to a 1mb drop in pressure.
Suggestion
Baxi should make the filter a servicable, replacable part so it can be checked and/or replaced during annual service.
Baxi should enhance their troubleshooting guide to indicate checking min pressure when any flame/burner issues are being considered.
Thanks again to all who helped me think this issue through.