SlimD

Gas Engineer
Sep 6, 2016
67
14
8
Dartford
Member Type
Heating Engineer (Has GSR)
When it starts up the fan comes on for half a second then off, then on, off, on, etc...
Air pressure switch seems to be making. Both overheat & thermostat ok
Potentiometer?
 
Is the termistor connected and working fine?
Yes. Seems it was a loose connection somewhere on either the board or the potentiometer. I had it all out to check it and when I put it all back it all started working normally. Bloody electrics!
 
That’ll be the board , it’s usually the relay that controls the fan kicking in and out because of a dry joint - if you pull out the board and turn it upside down you can see it sparking in sympathy . Resolder the joint or if it’s badly burnt replace.
 
That’ll be the board , it’s usually the relay that controls the fan kicking in and out because of a dry joint - if you pull out the board and turn it upside down you can see it sparking in sympathy . Resolder the joint or if it’s badly burnt replace.
Thanks I’ll remember that if I get called back to it
 