Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Beware the misread label!

View the thread, titled "Beware the misread label!" which is posted in Central Heating Forum on UK Plumbers Forums.

Sparkgap

Esteemed
Plumber
Subscribed
We are currently having issues with ionisation probes (supposedly) on a pair of large commercial boilers at a site. While discussing possible causes (not that we are too concerned as this issue has been dropped back in the lap of the manufacturers who commissioned them) I got to thinking of flame probe problems I had on another site many years ago.
The site had 3 floor standing gas boilers feeding a common header. When it came to commission them one boiler would happily cycle through and start up. The other two would cycle through then lock out. gas pressure okay, flame probes okay etc. While looking at the backs of the boilers and scratching my head I noticed that the electrical connection labels on the two faulty boilers were the opposite way round to the one on the working boiler (NEL, not LEN). Could it be something so simple as swapped mains connections? Changed over live and neutral on the two boilers and all working perfectly. Boilers commissioned and everybody happy.
I suppose the lesson learned from this is even when everybody does their job correctly you are still at the mercy of some numpty in the factory slapping the label on the wrong way!
 
We are currently having issues with ionisation probes (supposedly) on a pair of large commercial boilers at a site. While discussing possible causes (not that we are too concerned as this issue has been dropped back in the lap of the manufacturers who commissioned them) I got to thinking of flame probe problems I had on another site many years ago.
The site had 3 floor standing gas boilers feeding a common header. When it came to commission them one boiler would happily cycle through and start up. The other two would cycle through then lock out. gas pressure okay, flame probes okay etc. While looking at the backs of the boilers and scratching my head I noticed that the electrical connection labels on the two faulty boilers were the opposite way round to the one on the working boiler (NEL, not LEN). Could it be something so simple as swapped mains connections? Changed over live and neutral on the two boilers and all working perfectly. Boilers commissioned and everybody happy.
I suppose the lesson learned from this is even when everybody does their job correctly you are still at the mercy of some numpty in the factory slapping the label on the wrong way!
Yes it can be. The reverse polarity can allow everything to work except in some cases, flame recognition. It depends on the set up/how the current flows.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Beware the misread label!" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Sparkgap,
Last reply from
Last Plumber,
Replies
1
Views
17
Back
Top