Hi all – would appreciate some advice please
I have a three year old Viessmann 26 kw system boiler – a Vitodens 100-W WB1B. As far as I know (and I have no reason to doubt it) it was installed properly by local tradesperson (Gassafe reg and all that sort of thing) to replace knackered old boiler. In process of installation the boiler was relocated to an attached garage. As far as I know and as far as I am concerned the job was done well, no hassles and no complaints – all the work is neat, tidy and as a lay person it looks like a proper job..
However, ever since install the pressure has been problematic. There are two pressure gauges,. one as part of boiler and one near the filling loop. Filling loop is in first floor HW Cupboard by HW Cylinder. As far as I know the filling loop uses some components from the old install and is a braided hose approx 12 inches long with a black plastic handle at one end to allow water to fill the system.
There are 13 radiators (approx ½ on the ground and ½ on first floor)
System pressure at new was 1.2 bar dead cold. Over a few weeks it rose to be 3 bar and I was advised to bleed rads and release air from HW circuit vent. Did so and very little air came out. Pressure down to about 1.5 bar. Was told it should be okay.
Noted that when we left went on holidays in July this year that pressure on leaving was approx 1.5 bar if cold and approx 2.2 bar hot. Boiler left in holiday setting for three weeks (i.e. Off). On return pressure was 3.2 bar stone cold. Fire up boiler and pressure rises and prv releases water – all settles down to about 2.8 -3.0 bar after a few hours.
Decided to get installer to do service and look into pressure issues. Told expansion vessel knackered which explains odd pressure issues and so the rest of Service done – Fermox filter cleaned etc, new chems added in service and new exp vessel ordered and fitted a few days later. Boiler fired up – checked and installer all okay with various readings (efficiency, temperatures, pressure etc). Pressure set on completion of everything was 1.5 bar at 47 C.
First question, does blown expansion vessel explain away pressure problems?
Within 24 hours pressure was up to 3.2 bar at 65.4 C and 2.6 bar at 29.8 C. Boiler is on program and so figures reflect the max and min values throughout the 24 hour cycle
This has pretty much been the case for last three weeks up to a couple of days ago when boiler threw a fault code F4 (see later on – I will get to this). Contacted installer – he is very busy so gave me some advice on going through and eliminating all air related issues that I can deal with and also on resetting boiler.
Started today at pressure of 2.8 bar stone cold (i.e. am pretty sure water temp was less than 20 C as boiler been off for over 24 hours. So today, bled every rad twice – started at lowest and furtherest from boiler and finished at highest and closest. TRV on every radiator fully open. All rads immediately discharged water so as far as I know that means no air in rads. Bled HW Circuit and tiny amount of air came out (really tiny amount). Pressure on completion 1.0 bar and topped up via a short fill from filling loop to 1.5 bar. That was around midday.
Tried to Restart boiler – went through 4 cycles attempting to start and then returned the F4 error. Noticed that when attempting to start that pressure rose about 0.2 bar (presumably as pump kicks in and cycles water around) and then drops by same amount when boiler finishes its failed start attempts.
So, boiler off – not working, everything stone cold and pressure now at 17.00 is 3.4 bar and PRV is releasing pressure!
I have been assured the filling loop is not passing water BUT i have no idea if I have any way of proving that for myself.
Second question, is there some method or trick that I can use to confirm the filling loop when closed is in fact closed and no additional water is entering system? As far as I know, the filling loop is fed from the rising main and I am pretty sure I was told our mains pressure was over 3 bar.
Third question, is it likely that the new expansion vessel has split or whatever and if so what causes these things to split / rupture / leak or whatever it is that they do?
The F4 issue – according to Viessmann literature this is “Burner in Fault State, No Flame Signal is Present and says under the measures column - Check the ignition/ionisation electrode and cables, check the gas pressure, check the gas train, ignition, ignition module and condensate drain.Press "Reset"”
Now – I know nothing about Boilers but was an aircraft engineer and logic says to me that message has nothing to do with system water pressure. However, I am prepared to accept that the fault code could be a “bad message” that is arising due to the water pressure issues.
I have discussed all this with my installer and he agrees that the pressure shouldnt be rising like this and that I should not be needing to bleed rads to keep the pressure under control. He is exceptionally busy and cant get to me for a few days but we do have a service request logged with Viessmann to come and deal with it.
I would like to decrease my state of ignorance in advance of that visit – so can anyone offer advice please? As I said earlier, I have no issue with the install or installer and he has been nothing but helpful and free with advice. But I am not understanding whats happening here and just want to get other views on what might be going wrong.
Thanks in advance. 🙂
I have a three year old Viessmann 26 kw system boiler – a Vitodens 100-W WB1B. As far as I know (and I have no reason to doubt it) it was installed properly by local tradesperson (Gassafe reg and all that sort of thing) to replace knackered old boiler. In process of installation the boiler was relocated to an attached garage. As far as I know and as far as I am concerned the job was done well, no hassles and no complaints – all the work is neat, tidy and as a lay person it looks like a proper job..
However, ever since install the pressure has been problematic. There are two pressure gauges,. one as part of boiler and one near the filling loop. Filling loop is in first floor HW Cupboard by HW Cylinder. As far as I know the filling loop uses some components from the old install and is a braided hose approx 12 inches long with a black plastic handle at one end to allow water to fill the system.
There are 13 radiators (approx ½ on the ground and ½ on first floor)
System pressure at new was 1.2 bar dead cold. Over a few weeks it rose to be 3 bar and I was advised to bleed rads and release air from HW circuit vent. Did so and very little air came out. Pressure down to about 1.5 bar. Was told it should be okay.
Noted that when we left went on holidays in July this year that pressure on leaving was approx 1.5 bar if cold and approx 2.2 bar hot. Boiler left in holiday setting for three weeks (i.e. Off). On return pressure was 3.2 bar stone cold. Fire up boiler and pressure rises and prv releases water – all settles down to about 2.8 -3.0 bar after a few hours.
Decided to get installer to do service and look into pressure issues. Told expansion vessel knackered which explains odd pressure issues and so the rest of Service done – Fermox filter cleaned etc, new chems added in service and new exp vessel ordered and fitted a few days later. Boiler fired up – checked and installer all okay with various readings (efficiency, temperatures, pressure etc). Pressure set on completion of everything was 1.5 bar at 47 C.
First question, does blown expansion vessel explain away pressure problems?
Within 24 hours pressure was up to 3.2 bar at 65.4 C and 2.6 bar at 29.8 C. Boiler is on program and so figures reflect the max and min values throughout the 24 hour cycle
This has pretty much been the case for last three weeks up to a couple of days ago when boiler threw a fault code F4 (see later on – I will get to this). Contacted installer – he is very busy so gave me some advice on going through and eliminating all air related issues that I can deal with and also on resetting boiler.
Started today at pressure of 2.8 bar stone cold (i.e. am pretty sure water temp was less than 20 C as boiler been off for over 24 hours. So today, bled every rad twice – started at lowest and furtherest from boiler and finished at highest and closest. TRV on every radiator fully open. All rads immediately discharged water so as far as I know that means no air in rads. Bled HW Circuit and tiny amount of air came out (really tiny amount). Pressure on completion 1.0 bar and topped up via a short fill from filling loop to 1.5 bar. That was around midday.
Tried to Restart boiler – went through 4 cycles attempting to start and then returned the F4 error. Noticed that when attempting to start that pressure rose about 0.2 bar (presumably as pump kicks in and cycles water around) and then drops by same amount when boiler finishes its failed start attempts.
So, boiler off – not working, everything stone cold and pressure now at 17.00 is 3.4 bar and PRV is releasing pressure!
I have been assured the filling loop is not passing water BUT i have no idea if I have any way of proving that for myself.
Second question, is there some method or trick that I can use to confirm the filling loop when closed is in fact closed and no additional water is entering system? As far as I know, the filling loop is fed from the rising main and I am pretty sure I was told our mains pressure was over 3 bar.
Third question, is it likely that the new expansion vessel has split or whatever and if so what causes these things to split / rupture / leak or whatever it is that they do?
The F4 issue – according to Viessmann literature this is “Burner in Fault State, No Flame Signal is Present and says under the measures column - Check the ignition/ionisation electrode and cables, check the gas pressure, check the gas train, ignition, ignition module and condensate drain.Press "Reset"”
Now – I know nothing about Boilers but was an aircraft engineer and logic says to me that message has nothing to do with system water pressure. However, I am prepared to accept that the fault code could be a “bad message” that is arising due to the water pressure issues.
I have discussed all this with my installer and he agrees that the pressure shouldnt be rising like this and that I should not be needing to bleed rads to keep the pressure under control. He is exceptionally busy and cant get to me for a few days but we do have a service request logged with Viessmann to come and deal with it.
I would like to decrease my state of ignorance in advance of that visit – so can anyone offer advice please? As I said earlier, I have no issue with the install or installer and he has been nothing but helpful and free with advice. But I am not understanding whats happening here and just want to get other views on what might be going wrong.
Thanks in advance. 🙂