Hi All
I'm new to this forum thing and I don't really knew w what I'm doing , so go easy please
Right info
Biazi riva plus he plus 28 kw
Heating but no hot water . Initially I thought flow switch .no fault showing on boiler just green light flashing waiting for a command .
Changes magnetic flow switch , no joy . Actuater on diverter valve working(motor runs pin moves . Diverter valve pin operates when pushed manually so not ceased . Checked dhw thermistor gets 15 ohms . Rings biazi .should he getting around 12 ohms on sensor so no issue there . Run a magnet over sensor I was advised by biazi. Does this still nowt. So then he says pcb . Ok I says , changes pcb . Sets up the board with the instructions . Now nothing works not even heating and I'm getting an air pressure switch fault code . I haven't gone any where near aps . Rings biazi again . He runs me through board setup , still same.
Still no hot water . Now he says oh may be the turbine in the flow switch has jammed , there's a filter in there that could be blocked . Why would he advise a pcb first ??
I'm st a loss now . How can I have heating , swap a board and now have an aps fault . Checked all connections etc biazi guy says could be condensate unit ?? Or aps . I know coincidences happen but I refuse to believe that after swapping the board the aps has decided to go or the condensate unit has suddenly blocked in the space of an hour .
Only been an engineer for a few two year and I don't do many breakdowns so any knowledge from you wiser guys would be greatly appreciated, before I end up ragging the boiler off the wall and throwing it in a skip
Cheers guys
I'm new to this forum thing and I don't really knew w what I'm doing , so go easy please
Right info
Biazi riva plus he plus 28 kw
Heating but no hot water . Initially I thought flow switch .no fault showing on boiler just green light flashing waiting for a command .
Changes magnetic flow switch , no joy . Actuater on diverter valve working(motor runs pin moves . Diverter valve pin operates when pushed manually so not ceased . Checked dhw thermistor gets 15 ohms . Rings biazi .should he getting around 12 ohms on sensor so no issue there . Run a magnet over sensor I was advised by biazi. Does this still nowt. So then he says pcb . Ok I says , changes pcb . Sets up the board with the instructions . Now nothing works not even heating and I'm getting an air pressure switch fault code . I haven't gone any where near aps . Rings biazi again . He runs me through board setup , still same.
Still no hot water . Now he says oh may be the turbine in the flow switch has jammed , there's a filter in there that could be blocked . Why would he advise a pcb first ??
I'm st a loss now . How can I have heating , swap a board and now have an aps fault . Checked all connections etc biazi guy says could be condensate unit ?? Or aps . I know coincidences happen but I refuse to believe that after swapping the board the aps has decided to go or the condensate unit has suddenly blocked in the space of an hour .
Only been an engineer for a few two year and I don't do many breakdowns so any knowledge from you wiser guys would be greatly appreciated, before I end up ragging the boiler off the wall and throwing it in a skip
Cheers guys