Hi everyone, i have a worcester bosch 24i junior combi non condensing which is about 3 years old. the problem is that it keeps on needing to be reset at odd times. mainly on demand though. So far i have renewed the over heat stat, the central heating stat and the pump, but so far no joy. The manual says that it could be the mainboard but im reluctant to fit one if the problem can be solved elsewhere.

I phoned worcester and they only really seem to be following the manual as i am, nothing conclusive with them tbh.

The system is only a 3 radiator system all with lockshields fully open. The system doesnt need a powerflush as its had one just under a year ago. It has an external wall mounted stat that has been renewed recently and also a new programmer.

has anyone had this problem before?? many thanks

Gas Engineer
 
oh yeah, forgot to add.....the gas valve is regulating nicely and doing everything that it should so i have ruled that out. ALso i have ruled out blockages. thanks
 
flashing once per second.

i have just had some info from an engineer who has had this problem before. he thinks that the pcb has gone.....he thinks that it is shutting off the fan. I have to check 1 thing tommorow though. I have to check the resistance at the fan, if its above 100 ohms i think the pcb is faulty. so i will check tommorow then let you know the result.
 
hi guys, update. I tested the resistance where the fan meets the pcb (st1 i think) and it has the correct resistance.... so im back to the drawing board. I did however notice that the positive pressure tube that joins the flue to the pressure switch wasnt on properly and was 'folded' on one side (which could have let the air in - or pressure out). So i have put it on test once more and am awaiting the result. hopefully its solved it but my gut tells me its a no no!!
 
long story.... but the owner also owns 40 other flats. 8 years ago he brought 15 boilers but only fitted 13. stored 2 until about 3 years ago. hence why i say the boiler is only 3 years old. technically its 8 years old but if its sat in its box then does that count?? lol
 
must be in bad condition, there is always water in the heat exchanger when i fit boilers so if thats been sitting inside the boiler for 5 years, it must be scaled up, must be overheating
 
update. checked on boiler today. Still needs resetting. flash at once per second. It looks like i have to test everything however small or large...gonna take me ages!! :66:

If i ever get it sorted i will let you know what it was :24:. Damn boiler!!! :dead:
 
update. sorry it took so long. it turns out the fault lies with the pump. the pump i fitted wasnt an original boiler pump (not strong enough) so i had to fit a brand new boiler spec pump (as the guy on worcester tech told me it has to be the correct spec). The old pump was over heating and breaking down and causing the boiler to kettle and overheat. thanks for your feedback guys.

mucho appreciated
 