Any help would be greatly appreciated.
I have an indirect C/H system with two 2way valves, one for water an one for the C/H with a Wilo pump. The water is heated by a Firebird Olympic S50/70 oil boiler. My issues are as follows:
1: We are unable to heat the hot water tank using the boiler (we are currently using the immersion), when H/W is selected the valve opens fine and the inlet pipe to the coil gets nice and hot. However, the water in the tank never gets hot enough to trip the tank thermostat (even when set low) , the boiler trips on its overheating stat first. The return pipe from the coil also never gets hot and when held doesn't feel like there is flow.
My initial thoughts were that there is a blockage in the coil???
2: The boiler trips on its thermostat sometimes when we have the heating on. The room stat works fine and turns the boiler off when it's at the required temp, but on occasion the boiler trips before the room stat. We have to manually reset the stat each time and upon removing the cover it is apparent that the boiler is hot.
Our boiler service man says the boiler stat is faulty and this will fix the tripping issue, however I am concerned that the two problems above are linked? If there is less flow due to a blocked coil would this cause the boiler to run hotter?
I have checked for air locks blending everything I can and have been up to the attic to check there is water in both tanks.
Should the blockage be cleared first? Wouldn't replacing the boiler stat, assuming it isn't cutting out soon enough (that's why it's overheating), cause the boiler to cut out potentially before the room stat?
I hope all this is clear I would be very greatful of any help.
Thank you in advance.
Connor
I have an indirect C/H system with two 2way valves, one for water an one for the C/H with a Wilo pump. The water is heated by a Firebird Olympic S50/70 oil boiler. My issues are as follows:
1: We are unable to heat the hot water tank using the boiler (we are currently using the immersion), when H/W is selected the valve opens fine and the inlet pipe to the coil gets nice and hot. However, the water in the tank never gets hot enough to trip the tank thermostat (even when set low) , the boiler trips on its overheating stat first. The return pipe from the coil also never gets hot and when held doesn't feel like there is flow.
My initial thoughts were that there is a blockage in the coil???
2: The boiler trips on its thermostat sometimes when we have the heating on. The room stat works fine and turns the boiler off when it's at the required temp, but on occasion the boiler trips before the room stat. We have to manually reset the stat each time and upon removing the cover it is apparent that the boiler is hot.
Our boiler service man says the boiler stat is faulty and this will fix the tripping issue, however I am concerned that the two problems above are linked? If there is less flow due to a blocked coil would this cause the boiler to run hotter?
I have checked for air locks blending everything I can and have been up to the attic to check there is water in both tanks.
Should the blockage be cleared first? Wouldn't replacing the boiler stat, assuming it isn't cutting out soon enough (that's why it's overheating), cause the boiler to cut out potentially before the room stat?
I hope all this is clear I would be very greatful of any help.
Thank you in advance.
Connor