Called out to fault on Alpha HE 33. New Fan Installed.

View the thread, titled "Called out to fault on Alpha HE 33. New Fan Installed." which is posted in Gas Engineers Forum on UK Plumbers Forums.

Hi guys. First post on here. Called out to fault on Alpha HE 33. Fast blow fuse found to have blown. Faulty fan found to be problem. New fan installed and tested. Four days later and a call from customer to say boiler not working again. fast blow fuse found to have gone again. Replaced and gone again three days later. Anyone come across this before. Any pointers would be welcome. Starting to think wiring loom maybe
 
Could be pcb fault, water leak, pump, how do you know it was the fan.
Are you qualified to be tinkering in there?
 
Could be pcb fault, water leak, pump, how do you know it was the fan.
Are you qualified to be tinkering in there?
Stu
am qualified GSR engineer. Fan was replaced after a process of deduction by disconnecting mechanical parts, fan, pump, gas valve, diverter motor etc. Everything worked ok with fan disconnected and fuse didn’t blow. PCB ok and no water
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Called out to fault on Alpha HE 33. New Fan Installed." which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Hilton owl,
Last reply from
townfanjon,
Replies
5
Views
2,168
Back
Top