It's at the top..so how long should I press it for?Only if the Schrader valve is at the bottom.
I got same problem!Normally the air will have droplets of water with it if the vessel has gone. Just try to recharge it and go from there. Dont forget to dump the water pressure first before pumping up the vessel.
Keep draining while you pump up and wait until the water stops then pump some more until you have no water coming out and the shrader gauge says 1 barI got same problem!
I drained water till zero on water guage, then inflated the EV, The water guage went up, shud that happen?
If that happens dump the pressure again, until the water gauge doesn't increase whilst pumping up the vessel.I got same problem!
I drained water till zero on water guage, then inflated the EV, The water guage went up, shud that happen?
many thanx for that, will try that tomorrow, I thought the EV had punctured and the air was leaking into the water?If that happens dump the pressure again, until the water gauge doesn't increase whilst pumping up the vessel.
No, as you pump up the ev the water inside it is pushed back into the system and can make the water gauge increase.many thanx for that, will try that tomorrow, I thought the EV had punctured and the air was leaking into the water?
only have one guage, water, let me get this clear, if I pump up EV and leave open the water drain tap that will drain water to zero..the close water tap and repressurise, is that about right?Keep draining while you pump up and wait until the water stops then pump some more until you have no water coming out and the shrader gauge says 1 bar
no got it wrong u mean one bar on footpump, and zero on water guage, then add water to one bar on water guage?only have one guage, water, let me get this clear, if I pump up EV and leave open the water drain tap that will drain water to zero..the close water tap and repressurise, is that about right?
no got it wrong u mean one bar on footpump, and zero on water guage, then add water to one bar on water guage?
thanx for that I will let uknow if it works, if not take it, I fit another EV??Correct once one bar or foot and no water is draining via drain tap
Remove foot pump close drain tap and re pressurise boiler as you normally would do if pressure is low
a bit late tonite but on my mind?...under the boiler theres two warer controls close together I use to top the water up. The big white key is thag suposed to cut the water off, cus on or off, I can still get water tgru the small white valve. Am thinking cud the water be passing thru into system and spurting out safetg valvd cus I have heard the hiss of water a few times being ejected outside?..try to attach pic of the two valves which are side by side!Correct once one bar or foot and no water is draining via drain tap
Remove foot pump close drain tap and re pressurise boiler as you normally would do if pressure is low