Jones82
221
85
28
Heating Engineer (Has GSR)
Hi
I'm Gsr by the way and should get around to sending in my card details.
I'm working on a system boiler and central heating system and the prv/vessel has recently failed, I'm finding it difficult to source the prv short notice, I'm thinking of capping the Prv inside the boiler or the existing discharge pipe work then fitting a new one on the return pipe work close to the boiler, I'm already fitting a replacement external expansion vessel and filling loop so perfect time to do it.
The existing internal vessel has split and is undersized.
If it was a combi then I wouldn’t even think about it, as someone could isolate the heating and run hot water but it’s a system boiler, if you isolate the heating then the boiler wouldn’t work at all. The by pass and vessel are external, why not the prv? Its common practice on heat only boilers?
  • Optimistic
Reactions: Dave54
Remeha advanta plus and it has the usual isolators on the flow return and Gas as they enter the boiler. But if you shut these on a system boiler or even a modern heat only boiler then the flow switch won’t allow the boiler to fire ?
Still doesn't matter what happens if the flow switch sticks etc if it has valves you can prv needs to be in the same place
And no you can't put one / a new one after the old prv
Yes I guess your right it would also be against the manufacturers instructions.
I thought some manus allowed remote prv as long as you tee the boiler PRV into the return after the iso's.
No idea if remeha allow this though
Can't do link Adobe mobile. But I fitted a Baci system on my own home and was awkward for PRV. Followed their instructions but did not buy their kit. Plumb BLR PRV into return (?) . Fit remote PRV but had to be the highest point IIRC. Can't remember but the instructions are available online
If it has isolation valves beneath the Boiler I would say no. You do not want a situation where the boiler can be isolated without any form of relief.
If you permanently removed the isolation valves then it would be safe.
Another problem with h doing it that way, is that the valve would be open and the valves are not designed to hold pressure on the outlet side of the valve.
Ive never come accross a heat only with isos underneath or on top?
Heat onlys don't have prvs
I know, read the message i quoted bud. He wrote about closing iso's on heat onlys...thats why i said ive never come accross a heat only with iso's. Incase it goes kaboom with no prv.