I have a NEST with Viessmann system boiler with unvented cylinder.
I have a mid position and two position valve

I thought the mid position valve was faulty as it was not switching off
I got new actuator - the right one (40003916-003/U) . The manuals do make a reference to v4073a1039 so I'm sure it is the right one.
However my CH does not turn off when I switch it off in the app (when there is no HW on).
If HW and CH are on and I turn CH off it does work
I think my NEST is connected ok
App status Nest wiring status Mid posn valve wires
Both off 1245 live Grey live
Ch on 2345 White/Grey Live
HW on 1256 Neither live
Both on 2356 White live
I also notice some spurious voltages for eg after I turn Ch off 3 on nest has 55v (white wire as well)
When both CH and HW are on 4 on nest has 72v (also Grey wire)
Any clues on what is going wrong here
I have a NEST with Viessmann system boiler with unvented cylinder.
I have a mid position and two position valve

I thought the mid position valve was faulty as it was not switching off
I got new actuator - the right one (40003916-003/U) . The manuals do make a reference to v4073a1039 so I'm sure it is the right one.
However my CH does not turn off when I switch it off in the app (when there is no HW on).
If HW and CH are on and I turn CH off it does work
I think my NEST is connected ok
App status Nest wiring status Mid posn valve wires
Both off 1245 live Grey live
Ch on 2345 White/Grey Live
HW on 1256 Neither live
Both on 2356 White live
I also notice some spurious voltages for eg after I turn Ch off 3 on nest has 55v (white wire as well)
When both CH and HW are on 4 on nest has 72v (also Grey wire)
Any clues on what is going wrong here