Colin68
Here goes! .. me and my very experienced mate are scratching our heads on this one!
set up - convention with 5 x rads and 1 x cylinder (y plan), 22mm flow and return with drop downs to all rads
Boiler is faulting on poor circulation F22 and F25 (glow worm HX 15)
What I've checked :-
1.confirmed Mid position working
2.confirmed pump working (all speeds)
3.confirmed no air lock once filled
4. mid position set to manual open and tried running the boiler and pump
5.run the boiler on heating and hot water independently (still faults)
6.power flushed the circuit
7. pushed water through the heat exchanger in the boiler (rest of circuit isolated)
8. cut the flow and return, attached a hose pipe to the flow (before the zone valve), set valve to manually open with a hose pipe to the return (into the bath), put mains water through the circuit both with the radiators isolated (just flow and return cicruit) and with radiators all on .. water flowing out of the return no problem
Boiler is 5 years old and has some leakage and limescale deposits forming around the flow at the top of the exchanger which has dripped into the bottom of the boiler casing
I am going to discount sensors causing the fault as the return temperature (after the cylinder return) is not getting up and the boiler is shutting down (flow beyond the zone valve both DHW and Heating is confirmed)
I have an 84 year old man with no heating or hot water so it's bugging me a little as you can imagine
The previous idiot has disconnected the immersion heater power (customer was told he would never need it!) and managed to fit the magnaclean on the 'FLOW'
2 x AAV's have been replaced as they were faulty
Any ideas would be welcome????? .. I am wondering is heat exchanger is partially blocked (flow and return temp difference is 40 degrees when running) confirmed via GW diagnostics
set up - convention with 5 x rads and 1 x cylinder (y plan), 22mm flow and return with drop downs to all rads
Boiler is faulting on poor circulation F22 and F25 (glow worm HX 15)
What I've checked :-
1.confirmed Mid position working
2.confirmed pump working (all speeds)
3.confirmed no air lock once filled
4. mid position set to manual open and tried running the boiler and pump
5.run the boiler on heating and hot water independently (still faults)
6.power flushed the circuit
7. pushed water through the heat exchanger in the boiler (rest of circuit isolated)
8. cut the flow and return, attached a hose pipe to the flow (before the zone valve), set valve to manually open with a hose pipe to the return (into the bath), put mains water through the circuit both with the radiators isolated (just flow and return cicruit) and with radiators all on .. water flowing out of the return no problem
Boiler is 5 years old and has some leakage and limescale deposits forming around the flow at the top of the exchanger which has dripped into the bottom of the boiler casing
I am going to discount sensors causing the fault as the return temperature (after the cylinder return) is not getting up and the boiler is shutting down (flow beyond the zone valve both DHW and Heating is confirmed)
I have an 84 year old man with no heating or hot water so it's bugging me a little as you can imagine
The previous idiot has disconnected the immersion heater power (customer was told he would never need it!) and managed to fit the magnaclean on the 'FLOW'
2 x AAV's have been replaced as they were faulty
Any ideas would be welcome????? .. I am wondering is heat exchanger is partially blocked (flow and return temp difference is 40 degrees when running) confirmed via GW diagnostics